Question

by the line Two balanced Y-connected loads, one drawing 10 kW at 0.8 power factor lagging and the other 15 kW at 0.9 power fa

EXPLAIN THESE QUESTIONS WITH THE HELP OF DIAGRAMS AND LABEL DIAGRAMS IN SUCH A WAY THAT I CAN EASILY UNDERSTAND WHAT WE ARE FINDING AND HOW WE ARE FINDING THE REQUIRED THINGS .I AM POSTING MY QUESTION 4TH TIME PLEASE DONOT WASTE IT AND PLEASE DO ALL STEPS I NEED MY ANSWER STEP BY STEP

0 0
Add a comment Improve this question Transcribed image text
Answer #1

For the Question 2.45

a) Source current = 30.08 A with 0.9999 pf lagging

b) Ammeter reading connected in neutral wire is = 0 A

© 2-45 By Given information about circuit Gannected in parallel loads are - - - - - - 1,Ibr // - sc saat Load 1 Loada as givelire voltage of source = 480 line voltage of loads = 4804 c Parallel connection] Load I active lower Piz loko at of power facNow apply RCL at node m. Ja = Jar tāds = 15.04 1-36.87° +20.05 125.84° Ila Ia - 30.08 (-0.540A So source carrent= I= 30.08 AAs given in question all the loads are balanced and for a balanced 3-6 network theme taral all the phare currents will adds u

Add a comment
Know the answer?
Add Answer to:
EXPLAIN THESE QUESTIONS WITH THE HELP OF DIAGRAMS AND LABEL DIAGRAMS IN SUCH A WAY THAT...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Problem 3. Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs...

    Problem 3. Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW at 0.8 power factor lagging. The line impedance is (1.4 + j1.6) 12 per phase between generator G1 and the load, and (0.8 + jl) 2 per phase between generator G2 and the load. If generator G1 supplies 15 kW at 0.8 power factor lagging, with a terminal voltage of 460 V line-to-line, determine: 1. The voltage at the load terminals. 2....

  • Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW...

    Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW at 0.8 power factor lagging. The line impedance is (1.4 +J1.6) Ω per phase between generator G1 and the load, and (0.8 +jl ) Ω per phase between generator G2 and the load. If generator Gl supplies 15 kW at 0.8 power factor lagging, with a terminal voltage of 460 V line- to-line, determine 1. The voltage at the load terminals. 2. The voltage...

  • A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel...

    A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel connected loads: • Load 1 absorbs a total of 125 kW and 100 KVAR • Load 2 is a delta-connected impedance load with (125+j 40)ohms/phase • Load 3 absorbs 120 kVA at 0.8 power factor (lagging) Given that the line-neutral voltage at the load end of the line is 2400 V, determine the magnitude of the line-to- line voltage at the source end of...

  • UISIZULU Problem 4 A three phase, 5 kW, wye-connected load operate onnected load operates at 0.8...

    UISIZULU Problem 4 A three phase, 5 kW, wye-connected load operate onnected load operates at 0.8 power factor lagging with a terminal voltage of 100 V (line to line). The cables connecting e bles connecting each phase of the load to the wye-connected supply has an impedance of (0.25 +0.25) 12. Compute the following: a) Reactive power drawn by the load. b) Real and reactive power losses in the system. me current and line voltage at the source terminals and...

  • The impedance of a three-phase line is 0.3 + j 2.4 per phase. The line feeds...

    The impedance of a three-phase line is 0.3 + j 2.4 per phase. The line feeds two balanced three- phase loads connected in parallel. The first load takes 600 kVA at 0.7 p.f. lagging. The second takes 150 kW at unity power factor. The line to line voltage at the load end of the line is 3810.5 V. Find a) The magnitude of the line voltage at the source end of the line. b) The total active and reactive power...

  • 10. Two loads connected in parallel draw a total of 2.4 kW at 0.8 pflagging from...

    10. Two loads connected in parallel draw a total of 2.4 kW at 0.8 pflagging from a 120-V rms, 60- Hz line. One load absorbs 1.5 kW at a 0.707 pf lagging. Determine: (a) the pf of the second load, INV 11. Calculate the line currents for the system shown in figure. Calculate also the total power and reactive power consumed by the load. w 12. For the balanced three-phase circuit in Fig.. Calculate the line currents, the phase voltage...

  • 508 CHAPTER 11 . POLYPHASE CIRCUITS 11.40 In a balanced three-phase system, the source has an...

    508 CHAPTER 11 . POLYPHASE CIRCUITS 11.40 In a balanced three-phase system, the source has an aboc phase-sequence and is connected in delta. There are two rallel wye-connected loads. The phase impedance of load i and load 2 is 4 The line impedance connecting the source to the loads is 0.3 + j0.2 2. If the curre IAN! = 10/20-Arms, find the delta currents in the source 4 Ω and 10 +/4 Ω, respectively. nt in the a phase of...

  • solve no: 3.14 , 3.16, 3.19 please show each step and solve for beginners 120 Power...

    solve no: 3.14 , 3.16, 3.19 please show each step and solve for beginners 120 Power System Analysis 3.12. A single-phase system similar to that shown in Figure 3.11 has two transformers A-B a B-C connected by a line B feeding a load at the receiving end C. The ratings and parame ter values of the components are 500 V/1.5 kV, 9.6 kVA. leakage reactance 5 % 1.2 kV/120 V, 7.2 kVA, leakage reactance 4 % series impedance (0.5 +...

  • Sketch the 3-phase systems, and show your calculations: Problem (a): A positive-sequence balanced thrcc-phase wyc-connected source...

    Sketch the 3-phase systems, and show your calculations: Problem (a): A positive-sequence balanced thrcc-phase wyc-connected source supplics powcr to a balanced wyc-connected load. The line voltage is 100 V. The line impedance is 2 ? per phase, and the load impedance is 50 +j30 ? per phase. Determine the load voltages if V an-00. Problem (b): A positive-sequence balanced three-phase wye-connected source supplies power to a balanced wye-connected load. The magnitude of the line voltages is 208 V rms. If...

  • 9. A three phase balanced Y connected source is supplying three, three phase loads that are...

    9. A three phase balanced Y connected source is supplying three, three phase loads that are connected in parallel. First load is a y connected and has an impedance of 30+j40 ohms. The second load is absorbing a total of 150kVA at 0.5 power factor lagging. The third load is absorbing 150kVA at 0.5 power factor leading. The line to line source rms voltage is 2500V. i Find the load current in each load i) Find the total real and...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT