Question

Problem 3. Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW at

0 0
Add a comment Improve this question Transcribed image text
Request Professional Answer

Request Answer!

We need at least 10 more requests to produce the answer.

0 / 10 have requested this problem solution

The more requests, the faster the answer.

Request! (Login Required)


All students who have requested the answer will be notified once they are available.
Know the answer?
Add Answer to:
Problem 3. Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Similar Homework Help Questions
  • Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW...

    Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW at 0.8 power factor lagging. The line impedance is (1.4 +J1.6) Ω per phase between generator G1 and the load, and (0.8 +jl ) Ω per phase between generator G2 and the load. If generator Gl supplies 15 kW at 0.8 power factor lagging, with a terminal voltage of 460 V line- to-line, determine 1. The voltage at the load terminals. 2. The voltage...

  • EXPLAIN THESE QUESTIONS WITH THE HELP OF DIAGRAMS AND LABEL DIAGRAMS IN SUCH A WAY THAT...

    EXPLAIN THESE QUESTIONS WITH THE HELP OF DIAGRAMS AND LABEL DIAGRAMS IN SUCH A WAY THAT I CAN EASILY UNDERSTAND WHAT WE ARE FINDING AND HOW WE ARE FINDING THE REQUIRED THINGS .I AM POSTING MY QUESTION 4TH TIME PLEASE DONOT WASTE IT AND PLEASE DO ALL STEPS I NEED MY ANSWER STEP BY STEP by the line Two balanced Y-connected loads, one drawing 10 kW at 0.8 power factor lagging and the other 15 kW at 0.9 power factor...

  • UISIZULU Problem 4 A three phase, 5 kW, wye-connected load operate onnected load operates at 0.8...

    UISIZULU Problem 4 A three phase, 5 kW, wye-connected load operate onnected load operates at 0.8 power factor lagging with a terminal voltage of 100 V (line to line). The cables connecting e bles connecting each phase of the load to the wye-connected supply has an impedance of (0.25 +0.25) 12. Compute the following: a) Reactive power drawn by the load. b) Real and reactive power losses in the system. me current and line voltage at the source terminals and...

  • A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel...

    A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel connected loads: • Load 1 absorbs a total of 125 kW and 100 KVAR • Load 2 is a delta-connected impedance load with (125+j 40)ohms/phase • Load 3 absorbs 120 kVA at 0.8 power factor (lagging) Given that the line-neutral voltage at the load end of the line is 2400 V, determine the magnitude of the line-to- line voltage at the source end of...

  • The impedance of a three-phase line is 0.3 + j 2.4 per phase. The line feeds...

    The impedance of a three-phase line is 0.3 + j 2.4 per phase. The line feeds two balanced three- phase loads connected in parallel. The first load takes 600 kVA at 0.7 p.f. lagging. The second takes 150 kW at unity power factor. The line to line voltage at the load end of the line is 3810.5 V. Find a) The magnitude of the line voltage at the source end of the line. b) The total active and reactive power...

  • 12. For a three-phase balanced system, a generator serves a remote load through two parallel tran...

    12. For a three-phase balanced system, a generator serves a remote load through two parallel transmission lines with 4 transformers. The system parameters are as follows: Generator: T1: (A-Y, with Y side voltage leading) T2: (A-Y, with Y side voltage leading) T3: (A-Y, with Y side voltage leading) T4: (A-Y, with Y side voltage leading) Line-1 Line-2 Load 100MVA, 21kV, x-0.15pu 120MVA, 20Д/165Y kV, x-O.12pu 80MVA, 20A/1 10Y kV, x-O.1pu 120MVA, 165A/33Y kV, x-0.12pu 80MVA, 11ОД/33Y kV, x-O.1pu 30+j100 O...

  • 3. A 345-KV, three-phase transmission line delivers 500MVA, 0.866 power factor lagging, to a three phase...

    3. A 345-KV, three-phase transmission line delivers 500MVA, 0.866 power factor lagging, to a three phase wve-connected load connected to its receiving-end terminals, the voltage at the receiving end is 345kV. a) Find the complex load impedance per phase. b) Find the real and reactive power per phase. 15 pts.

  • Rework problem 3.4 if the load connected to the 240-V secondary winding absorbs 110 kVA under...

    Rework problem 3.4 if the load connected to the 240-V secondary winding absorbs 110 kVA under short-term overload conditions at an 0.8 power factor leading and at 230 volts. Reference of problem 3.4 A single phase 100-kVA 2400/240-volt 60 Hz distribution transformer is used as a step down transformer. The load, which is connected to the 240-volt secondary winding, absorbs 60kVA at 0.8 power factor lagging and is at 230 volts. Assuming an ideal transformer, calculate the following: a) primary...

  • Problem 1: A single-phase load with a nameplate rating of 4.16kV, 2.5MW, 0.8 pf (lag) is...

    Problem 1: A single-phase load with a nameplate rating of 4.16kV, 2.5MW, 0.8 pf (lag) is being supplied from a 4.16kV singe-phase generator. There is a 5km transmission line between the generator and the load. The transmission line has an impedance of 0.5 / 60◦ ohms per 1000m. What is the ratio of the voltage at the load to the voltage at the generator terminals? What is the power loss in the transmission line? What is the actual load power?...

  • A three-phase feeder has line voltage of 13.8 kV and supplies load of 7000 kVA at...

    A three-phase feeder has line voltage of 13.8 kV and supplies load of 7000 kVA at power factor of 0.8 lagging. Find: The feeder current in A, real power in kW and Reactive power in kVAr. The capacitor size in kVAr to improve the power factor to 0.98. The feeder power in kW and kVA and current in A, after installing the capacitor bank.