Question

A three-phase feeder has line voltage of 13.8 kV and supplies load of 7000 kVA at...

A three-phase feeder has line voltage of 13.8 kV and supplies load of 7000 kVA at power factor of 0.8 lagging.

Find:

  1. The feeder current in A, real power in kW and Reactive power in kVAr.
  2. The capacitor size in kVAr to improve the power factor to 0.98.
  3. The feeder power in kW and kVA and current in A, after installing the capacitor bank.
0 0
Add a comment Improve this question Transcribed image text
Know the answer?
Add Answer to:
A three-phase feeder has line voltage of 13.8 kV and supplies load of 7000 kVA at...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 3. Figure 2 shows a single line diagram of a 13.8 kV primary feeder supplying power...

    3. Figure 2 shows a single line diagram of a 13.8 kV primary feeder supplying power to a load at the end of the feeder. A shunt capacitor bank is located at the load bus. The capacitor bank is Y-connected with a reactance Xc = 400/phase. Assume that the voltage at the sending end of the feeder is 5% above rated and theat the load is Y- connected with Ruoad = 200/phase in parallel with load Xload = 400/phase. Determine:...

  • A 240V three phase power system supplies two loads in parallel: Load 1: measured line current...

    A 240V three phase power system supplies two loads in parallel: Load 1: measured line current 30A, power factor 0.85 lagging, and Load 2: measured power 10kW, reactive power -7.5kVar A. Determine the power factor of load 2. B. Determine the total real power (in kW), reactive power (in kVAR), apparent power (in kVA), power factor and line current (in A) of the two loads.

  • A three-phase load of 15 kVA with a PF of 0.8 lagging is connected in parallel...

    A three-phase load of 15 kVA with a PF of 0.8 lagging is connected in parallel with a three-phase load of 36 kW at 0.6 PF leading. The line-line voltage is 2000V. a) Find the total complex power and power factor. Is it inductive or capacitive? b) How much kVAR is needed to make the PF unity? c) What is the magnitude of the current going into the total load?

  • A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel...

    A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel connected loads: • Load 1 absorbs a total of 125 kW and 100 KVAR • Load 2 is a delta-connected impedance load with (125+j 40)ohms/phase • Load 3 absorbs 120 kVA at 0.8 power factor (lagging) Given that the line-neutral voltage at the load end of the line is 2400 V, determine the magnitude of the line-to- line voltage at the source end of...

  • 3. A 12.47 kV feeder provides service to an unbalanced wye-connected load specified to be: Phase ...

    Response: Me neither :/ 3. A 12.47 kV feeder provides service to an unbalanced wye-connected load specified to be: Phase a: 1000 kVA, 0.9 lagging power factor Phase b: 800 kVA, 0.95 lagging power factor Phase c: 1100 kVA, 0.85 lagging power factor a) Compute the initial load currents assuming that 60% of the load is complex power, 25% constant current, and 15% constant impedance. b) Determine the currents at the start of the second iteration if the load voltages...

  • Problem 3. Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs...

    Problem 3. Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW at 0.8 power factor lagging. The line impedance is (1.4 + j1.6) 12 per phase between generator G1 and the load, and (0.8 + jl) 2 per phase between generator G2 and the load. If generator G1 supplies 15 kW at 0.8 power factor lagging, with a terminal voltage of 460 V line-to-line, determine: 1. The voltage at the load terminals. 2....

  • Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW...

    Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW at 0.8 power factor lagging. The line impedance is (1.4 +J1.6) Ω per phase between generator G1 and the load, and (0.8 +jl ) Ω per phase between generator G2 and the load. If generator Gl supplies 15 kW at 0.8 power factor lagging, with a terminal voltage of 460 V line- to-line, determine 1. The voltage at the load terminals. 2. The voltage...

  • 3. (40 points) Three-phase loads are connected in parallel across a 24 KV (line-line three-phase power...

    3. (40 points) Three-phase loads are connected in parallel across a 24 KV (line-line three-phase power supply. Load 1: 120 KVA at 0.8 power factor leading; Load 2: 180 KW at 0.6 power factor lagging, Load 3: 40 KW at unity power factor Find the total complex power of three loads; (ii) Draw the power triangle of the combined load (ii) Find the overall power factor (iv) Find the line current (magnitude only) in the power supply line.

  • Please show detailed steps. Thanks Problem # 1: Three Phase Power [35 points] A three-phase substation...

    Please show detailed steps. Thanks Problem # 1: Three Phase Power [35 points] A three-phase substation bus supplies three wye-connected three phase loads that are connected in parallel through a three-phase feeder with an impedance of 0.3 30 per phase Load 1 draws 75kVA at 0.866 lagging power factor, load 2 draws 45 kW at 0.70 leading power factor and load 3 draws 20 kVAR at 0.85 lagging power factor. The line-line voltage at the load is 460V Take the...

  • can you answer this question and explain why? thanks. A 50-Hz 10-MVA, 66/22-kV distribution transformer has...

    can you answer this question and explain why? thanks. A 50-Hz 10-MVA, 66/22-kV distribution transformer has a full-load efficiency of 98% at 0.8 lagging power factor. The transformer core loss is 80 kW. The transformer supplies an industrial load that has a constant demand of 5000 kW at 0.65 lagging power factor. The cost of energy is $0.1 per kWh. 1. In the following questions, assume that the voltage at the load terminal is maintained constant at 22 kV. calculations....

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT