3. A 12.47 kV feeder provides service to an unbalanced wye-connected load specified to be: Phase ...
5.3. Given a 600 kVA 12.47 kV 0.85 pf lagging three-phase load: a. Compute the corresponding complex power. b. Compute the corresponding wye and delta complex impedances Answers: a) S3p - (510 j316.1)kVA,S10 (170 +j105.4)kVA b) Zy (220.3+1 36.5), (660.9j409.5)2
Three single-phase transformers rated at 250 kVA, 7200 V/600 V, 60 Hz, are connected in wye- delta on a 12.47 kv, 3-phase line. If the load is 450 kVA, calculate: a. The currents in the incoming and outgoing transmission lines b. The currents in the primary and secondary windings 1. sratod t 200 w 3o0 v/6oO V 60 Hz are used to raise the Three single-phase transformers rated at 250 kVA, 7200 V/600 V, 60 Hz, are connected in wye-...
I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....
I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....
Question 2: Three phase circuit. (100p) A wye connected generator supplies a delta connected balanced load through short feeder. seree the load line to neutral voltage as reference voltage phase angle zero. 02.1 Q2.2 Q2.3 Q2.4 Draw the equivalent circuit. 10p Calculate the load line-to-neutral voltages and line-to-line voltages. 20p Calculate the delta load currents and feeder currents. 20p Calculate the supply wye connected generator line-to-neutral voltages. Is the obtained values are acceptable? Calculate the generator real and reactive power...
A three-phase feeder has line voltage of 13.8 kV and supplies load of 7000 kVA at power factor of 0.8 lagging. Find: The feeder current in A, real power in kW and Reactive power in kVAr. The capacitor size in kVAr to improve the power factor to 0.98. The feeder power in kW and kVA and current in A, after installing the capacitor bank.
A delta-wye connected transformer is shown in Figure below. This is a 220 kV to 450 kV transformer, line-line, RMS. The 'X' side is the 220 kV side. Assume that Phase A voltage on the X' side has zero phase angle (that is, use VaX as the phase reference) 1) What is the turns ratio NX: NH? 2) Draw phasor diagrams of the primary and secondary voltages. Be sure to get relative phase angles right. 3) If a balanced load...
4.7. Consider a three-phase, 12.47 kV system supplying a 600 kVA load, pf 0.8 lagging. Determine the instantaneous power (a) per phase, and (b) in total.
A commercial office building is to be supplied service at 208Y/120 V from the utility company 12.47 kV distribution feeder (12.47 kV L-L and 7.2 kV L-N). The estimated load is 85 kW at 0.9 lagging power factor. If the service is supplied from a bank of three single-phase overhead transformers (assume single bushing transformers) connected in a grounded-wye configuration, determine the appropriate apparent power rating and voltage rating to serve this load. Assume the load is continuous and allow...
Problem 7 Three three-phase wye-connected loads are in parallel across a three-phase supply. The first load draws a current of 10 A at pf- 0.93 (leading), and the second and third loads (each) draw a current of 20 A at pf= 0.85 (lagging). Suppose the line-to-line voltage is 240 V. Compute the following: a) The transmission line current b) The load power factor c) The complex power supplied by the source Problem 7 Three three-phase wye-connected loads are in parallel...