Question

4.7. Consider a three-phase, 12.47 kV system supplying a 600 kVA load, pf 0.8 lagging. Determine the instantaneous power (a) per phase, and (b) in total.
0 0
Add a comment Improve this question Transcribed image text
Answer #1


Calculate the line current S. 3V 600 x10 V3 ( 12.47 × 10° -27.78 A Calculate the phase voltage 12.47 x10 3 Calculate the phas Calculate the remaining phase currents Po (t)-160000 + 200000 cos(20r-36.870 + 120°) W 160000 200000 cos(2cvt +83.13o) W And,

Add a comment
Know the answer?
Add Answer to:
4.7. Consider a three-phase, 12.47 kV system supplying a 600 kVA load, pf 0.8 lagging. Determine...
Your Answer: