Question

A two-stage compression refrigeration system with an adiabatic liquid-vapor separation unit uses refrigerant-134a as working

0 0
Add a comment Improve this question Transcribed image text
Answer #1

You probably know, how to get enthalpy at all the points right?

I still shown taht in short on first written page.

2 Condenser Compressor 3 Separator Expansion valve 8 + Compressor 4 5 Expansion valve 7 Evaporator 6

The below image solves the section i)

T 16 bar 3 8 8 bar 5 4 4 bar 6 7 QL S

I am not going to show basics like pressure conversion of Mpa to bar and celcius to kelvin to keep solution clear. Its basics. If you have any difficulty regarding such things let me know in the comment

from refrigeration table R134a coe get P, = 8 bar sat vapour } his hg = 415 kJ /kg P2 = 16 bar S2=5, (at & bar) = 1.7144 kJ/k

On below image we used energy balace to calculate mass flow rate

1594630426288_IMG_20200713_141632.png

two answers of section ii) and answer of section III) are on below page

1594630450390_IMG_20200713_141653.png

Hope you are satisfied with the solution

Please give a like

Please don't directly dislike before commenting your query first

THANK YOU

Add a comment
Know the answer?
Add Answer to:
A two-stage compression refrigeration system with an adiabatic liquid-vapor separation unit uses refrigerant-134a as working fluid....
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A two-stage compression refrigeration system with an adiabatic liquid-vapor separation unit uses refrigerant-134a as working fluid....

    A two-stage compression refrigeration system with an adiabatic liquid-vapor separation unit uses refrigerant-134a as working fluid. the system operates the evaporator at 0.4Mpa, the condenser at 1.6Mpa and the separator at 0.8 Mpa. The compressors use 25kW of power. Given that the refrigerant is saturated liquid at the inlet of each compressor, and the compressors are isentropic: i) show the process on a T-s diagram, ii) calculate the rate of cooling provided by the evaporator, the COP of the heat...

  • Thermodynamics. No interpolation needed. Problem #3. Refrigerant 134a is the working fluid for vapor-compression refrigeration cycle....

    Thermodynamics. No interpolation needed. Problem #3. Refrigerant 134a is the working fluid for vapor-compression refrigeration cycle. The evaporator temperature is 8°C and the condenser pressure is 12 bar. Saturated vapor enters the compressor and superheated vapor enters the condenser at 60°C and exits the condenser as saturated liquid. For a refrigeration capacity of 8 tons or 2.816 x104 J/s determine the following: (1) The refrigerant mass flow rate in kg/s; (2) The compressor isentropic efficiency [Hint: Interpolation is required); (3)...

  • 1. An industrial freezer uses a multi-stage vapor-compression cycle with R-134a as the working fluid. The...

    1. An industrial freezer uses a multi-stage vapor-compression cycle with R-134a as the working fluid. The evaporator operates at 140 kPa, the condenser at 1600 kPa, and the flash chamber 600 kPa. The refrigerant leaves the evaporator as a super-heated vapor at -15°C, and leaves the condenser as a sub-cooled liquid at 50°C. Both compressors used in the system have isentropic efficiencies of 85%. For a cooling load of 25 kW, (a) What is the mass flow rate of refrigerant...

  • In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating...

    In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating at a rate of 15 kW to maintain a building at 20 °C year-round. During the heating mode in the winter, the outside temperature is 5 °C. It is also used for cooling in the summer when outside temperature is 34 °C. Saturated vapor at 2.4 bar leaves the evaporator and superheated vapor at 8 bar leaves the compressor. There is no significant heat...

  • In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating...

    In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating at a rate of 15 kW to maintain a building at 20 °C year-round. During the heating mode in the winter, the outside temperature is 5 °C. It is also used for cooling in the summer when outside temperature is 34 °C. Saturated vapor at 2.4 bar leaves the evaporator and superheated vapor at 8 bar leaves the compressor. There is no significant heat...

  • In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating...

    In a vapor-compression refrigeration heat pump cycle with Refrigerant 134a as the working fluid provides heating at a rate of 15 kW to maintain a building at 20 °C year-round. During the heating mode in the winter, the outside temperature is 5 °C. It is also used for cooling in the summer when outside temperature is 34°C. Saturated vapor at 2.4 bar leaves the evaporator and superheated vapor at 8 bar leaves the compressor. There is no significant heat transfer...

  • A vapor-compression heat pump system uses Refrigerant R-134a as the working fluid. The refrigerant enters the...

    A vapor-compression heat pump system uses Refrigerant R-134a as the working fluid. The refrigerant enters the compressor at 2.0bar, -5degC and with a mass-flow rate of 26g/s. Compression is adiabatic to 11.6bar, 60degC and the refrigerant exits the condenser 8degC sub-cooled. a) Draw a P-h chart to visualise the refrigeration cycle and display known data. b) Determine the power input to the compressor in kW c) Determine the heating capacity of the system in kW d) Determine the coefficient of...

  • A vapor compression refrigeration system operates at steady state with refrigerant 134a as the working fluid....

    A vapor compression refrigeration system operates at steady state with refrigerant 134a as the working fluid. Superheated vapor enters the compressor at 10 lbf/in2 , 0 oF. The liquid leaving the condenser is at 180 lbf/in2 , 100 oF. There is no significant pressure drop in the evaporator or condenser. For compressor efficiency of 83% and refrigeration capacity of 6 tons, determine (a) the compressor power input in horsepower, and (b) the coefficient of performance. A vapor compression refrigeration system...

  • 11-11 A refrigerator operates on the ideal vapor-compression refrigeration cycle and uses refrigerant-134a as the working...

    11-11 A refrigerator operates on the ideal vapor-compression refrigeration cycle and uses refrigerant-134a as the working fluid. The condenser operates at 1.6 MPa and the evaporator at -6oC. If an adiabatic, reversible expansion device were available and used to expand the liquid leaving the condenser, how much would the COP improve by using this device instead of the throttle device?

  • Please also draw the T-S diagrams and PH diagrams to facilitate understanding. Thank you. 5. The refrigeration system s...

    Please also draw the T-S diagrams and PH diagrams to facilitate understanding. Thank you. 5. The refrigeration system shown below is another variation of the basic vapor compression refrigeration system which attempts to reduce the compression work. In this system, a heat exchanger is used to superheat the vapor entering the compressor while sub-cooling the liquid exiting from the condenser Consider a system of this type that uses refrigerant-134a as its refrigerant and operates the evaporator at -10°C, and the...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT