Question

A 3-phase, 1000-MVA, 20-kV, 60-Hz synchronous generator is connected to an infinite bus as shown below. All impedances are given in pu values. The generator delivers 0.9 pu power at unity power factor to the infinite bus whose voltage is at 1 p

image.png

A 3-phase, 1000-MVA, \(20-\mathrm{kV}, 60-\mathrm{Hz}\) synchronous generator is connected to an infinite bus as shown below. All impedances are given in pu values. The generator delivers \(0.9\) pu power at unity power factor to the infinite bus whose voltage is at 1 pu.

If phase 'A' of circuit 2 (CCT 2) between buses H1 and H2 is suddenly opened at point ' \(\mathrm{F}\) ' near bus H1 due to the opening of a circuit breaker, determine:

(a) [10 marks] The internal voltage of the generator prior to the circuit breaker opening.

(b) [15 marks] The resulting phase ' \(\mathrm{B}^{\prime}\) and phase 'C' currents in circuit 2 (in pu) after the circuit breaker opening.

Generator internal impedances: \(X_{1}=1.8\) pu, \(X 2=0.25\) pu, \(x 0=0.04\) pu

Infinite bus internal impedance: Negligible.

For transformers and transmission lines, assume \(\mathrm{X} 1=\mathrm{X} 2\) (positive sequence reactance is equal to negative sequence reactance).

\(\mathrm{X} 0\) is the zero sequence reactance.

1 0
Add a comment Improve this question Transcribed image text
Request Professional Answer

Request Answer!

We need at least 10 more requests to produce the answer.

0 / 10 have requested this problem solution

The more requests, the faster the answer.

Request! (Login Required)


All students who have requested the answer will be notified once they are available.
Know the answer?
Add Answer to:
A 3-phase, 1000-MVA, 20-kV, 60-Hz synchronous generator is connected to an infinite bus as shown below. All impedances are given in pu values. The generator delivers 0.9 pu power at unity power factor to the infinite bus whose voltage is at 1 p
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Similar Homework Help Questions
  • 3. A 722-MVA, 19-kV steam turbine generator has a per-phase synchronous reactance of 1.3 PU, and...

    3. A 722-MVA, 19-kV steam turbine generator has a per-phase synchronous reactance of 1.3 PU, and its internal (excitation) voltage is adjusted to 1.2 PU. The generator is connected to a 19 kV (line) infinite-bus. If the voltage angle (d) between the infinite-bus and the generator internal voltage is 20°, calculate, The generator active power output. The generator line current. Draw the phasor diagram for one phase.

  • A 50-Hz generator, connected directly to an infinite bus operating at a voltage of 120° pu, has a synchronous reactance...

    A 50-Hz generator, connected directly to an infinite bus operating at a voltage of 120° pu, has a synchronous reactance of 1.35 pu. The generator no-load voltage is 1.1 pu, and its inertia constant H is 4 MJ/MVA. The generator is suddenly loaded to 60 percent of its maximum power limit. Determine the frequency of the resulting natural oscillations of the generator rotor. A 50-Hz generator, connected directly to an infinite bus operating at a voltage of 120° pu, has...

  • A 50 Hz, 250 MVA synchronous generator having inertia constant H=5 MJ/MVA is connected to an infinite bus through trans...

    A 50 Hz, 250 MVA synchronous generator having inertia constant H=5 MJ/MVA is connected to an infinite bus through transformer and transmission line as shown below. The transformer reactance is based on 500 MVA, while the other impedances are based on the generator MVA Infinite bus 1 2 3 XL 0.1 pu - oto G1 V= 1.0 pu X 0.1 pu Xd = 0.3 pu at 500 MVA The generator is delivering 0.8 of full load current at a power...

  • A 3-phase, 60-Hz, synchronous generator has the following data

    A 3 -phase, \(60-\mathrm{H} 2\), synchronous generator has the following data:Rated MVA \(=22.8 \mathrm{MVA}\)Rated voltage \(=13.8 \mathrm{kV}\)\(X_{d}=1.8\) pu on rated MVA and rated voltage base \(X_{d}^{\prime}=0.3\) pu on rated MVA and rated voltage base CT ratio \(=1200 \mathrm{~A}: 5 \mathrm{~A}\)PT ratio \(=14.4 \mathrm{kV}: 120 \mathrm{~V}\)a) Explain why it is important to have synchronous generator under-exciation or loss of excitation protection. [5 marks]b) Design a loss of excitation relay for this generator based on the standard single mho circle design, and...

  • Question 2 A 60 Hz synchronous generator with Xd 0.2 pu transient reactance is connected to...

    Question 2 A 60 Hz synchronous generator with Xd 0.2 pu transient reactance is connected to an infinite us through a transformer and the transmisiones as shown in the Figure. All system reactances are marked on the diagram and are expressed on a common MVA base. The generator dies a power of Auto busbar 1. The magnitude of the generator's excitation voltage e'is 12 pu, and the infinite bus voltage is -1.00u. If a 3-phase fault occurs at the middle...

  • A 75 MVA, 25 Kv, three-phase, 60 Hz synchronous generator has a synchronous reactance of X=...

    A 75 MVA, 25 Kv, three-phase, 60 Hz synchronous generator has a synchronous reactance of X= 9 Ω per phase and a negligible resistance. The generator is delivrimg rated power at a 0.8 power factor lagging at the rated terminal voltage to an infinitie bus, as shown in the following figure 1. Figure 1.The synchronous generator connected to infinite bus in single phase. 1)   The excitation voltage is E = 26.87 KV, The generator delivring 60 MW. Compute the powe...

  • A 3-phase, 100 MVA, 11 kV, 60 Hz, 200 rpm synchronous generator has synchronous reactance of...

    A 3-phase, 100 MVA, 11 kV, 60 Hz, 200 rpm synchronous generator has synchronous reactance of 12 2 and negligible stator resistance. a. The generator is connected to an infinite bus and delivers 80 MW at 0.8 leading power factor. Determine the power angle and excitation voltage EA. Draw the phasor diagram. b. The field current of the generator is now slowly reduced until the generator reaches its static stability limit (5=0). For this condition, determine the power angle, excitation...

  • A 60-MVA, 69.3-kV, three-phase synchronous generator has a synchronous reactance of 15 Ω/phase and negligible armature...

    A 60-MVA, 69.3-kV, three-phase synchronous generator has a synchronous reactance of 15 Ω/phase and negligible armature resistance. -a. The generator is delivering rated power at 0.8 power factor lagging at the rated terminal voltage to an infinite bus bar. Determine the magnitude of the generated emfper phase and the power angle δ. -b. If the generated emfis 36 kV per phase, what is the maximum three-phase power that the generator can deliver before losing its synchronism? Winter

  • 3. A 200 MVA, 20 kV, 60 Hz Y-connected solidly grounded three phase synchronous generator connect...

    3. A 200 MVA, 20 kV, 60 Hz Y-connected solidly grounded three phase synchronous generator connected through a 200 MVA 20/138 KV Y-Y transformer to a 138 kV transmission line. The generator reactances to the machine's own base are X-1.10 Both of the transformers Y connections are solidly grounded and its positive, negative and zero sequence series resitances are all 0.10 pu. a. What is the voltage at the terminals of the generator during the sub transient period if a...

  • infinite bus through a step-up transformer Consider a synchronous generator connected to an Given the single phase equi...

    infinite bus through a step-up transformer Consider a synchronous generator connected to an Given the single phase equivalent circuit information EZS= generator phase to neutral EMF VZ0 infinite bus phase to neutral voltage referred to the generator side of the step-up transformer generator synchronous reactance Zg jX, jX, transformer impedance referred to the generator side of the transformer Z, a) Sketch the capability diagram of a synchronous generator. Label all boundaries and explain their significance. Show clearly the safe operation...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT