infinite bus through a step-up transformer Consider a synchronous generator connected to an Given the single phase equi...
A synchronous generator is connected to an infinite bus via a transformer and a network of transmission lines, as illustrated in Figure 1 below. Per unit reactances for all elements are shown to a common system base. The generator is delivering 1.1 per unit real power to the infinite bus, and the infinite bus voltage is regulated to 1.05 per unit. The excitation voltage of the synchronous generator is set to 1.30 per unit. The inertia constant of the generator...
A 100MVA synchronous generator is connected to a 25kV infinite bus through two parallel transmission lines. The synchronous reactance of the generator is 2.5Ω. Each transmission line has inductive reactance of 2Ω and 0.2Ω resistance. The generator delivers 90MVA to the infinite bus at 0.8 power factor lagging. For the above conditions, calculate: a. The terminal voltage of the generator b. The equivalent field voltage and power angle c. The real power output at the generator terminals d. The reactive...
A 3-phase, 1000-MVA, \(20-\mathrm{kV}, 60-\mathrm{Hz}\) synchronous generator is connected to an infinite bus as shown below. All impedances are given in pu values. The generator delivers \(0.9\) pu power at unity power factor to the infinite bus whose voltage is at 1 pu.If phase 'A' of circuit 2 (CCT 2) between buses H1 and H2 is suddenly opened at point ' \(\mathrm{F}\) ' near bus H1 due to the opening of a circuit breaker, determine:(a) [10 marks] The internal voltage...
A 50-Hz generator, connected directly to an infinite bus operating at a voltage of 120° pu, has a synchronous reactance of 1.35 pu. The generator no-load voltage is 1.1 pu, and its inertia constant H is 4 MJ/MVA. The generator is suddenly loaded to 60 percent of its maximum power limit. Determine the frequency of the resulting natural oscillations of the generator rotor. A 50-Hz generator, connected directly to an infinite bus operating at a voltage of 120° pu, has...
A 50 Hz, 250 MVA synchronous generator having inertia constant H=5 MJ/MVA is connected to an infinite bus through transformer and transmission line as shown below. The transformer reactance is based on 500 MVA, while the other impedances are based on the generator MVA Infinite bus 1 2 3 XL 0.1 pu - oto G1 V= 1.0 pu X 0.1 pu Xd = 0.3 pu at 500 MVA The generator is delivering 0.8 of full load current at a power...
Problem 2. A 3-phase star-connected turbo-generator feeds power to 11 kV infinite bus, through two parallel transmission lines each having a reactance of452. The generator synchronous reactance is 3 Ω. (a) The mechanical input to alternator and its excitation are adjusted as that the operating power factor at alternator terminals is unity and rated current of 500 A is delivered. Calculate the alternator terminal and excitation voltages. Also determine the active and reactive powers delivered to the infinite bus. (b)...
Figure 1 shows a single-line diagram of a three phase, 60-Hz, synchronous generator, connected through a transformer and parallel transmission lines to an infinite bus. All reactances are given in per unit on a common system base. In steady state, the infinite bus receives 1.0 per unit real power at 0.95 power factor lagging. The generator in Figure 1 is initially operating in steady state, when circuit breaker B12 inadvertently opens. Use the equal area criterion to calculate the maximum...
A 480 V, 60 Hz, 470 kVA, 0.85 PF lagging, 2-pole, Y-connected synchronous generator has a synchronous reactance of XS=0.016 Ω and an armature resistance of RA=0.016 Ω. At rated conditions the core losses are 7 kW. Friction losses and field winding losses are 8 kW. Suppose the machine is connected to an infinite bus (hence the terminal voltage is fixed) and it is running at the rated conditions. a) What is the rotor speed in rpm? b) Calculate the...
5. Consider the one-ine diagram shown below. The three-phase transformer bank is made up of three identical single-phase transformer, each specified by X1-0.004 Ω (on the high-voltage side), negligible resistance and magnetizing current, and turns ratio N2/N,-10. The transformer bank is delivering is delivering 110MW at 0.9 power factor leading to a substation bus voltage is 230kV. Determine the reactive power supplied by the source. (3.47) whose To rest of the system Generator ΔΥ 230-kV substation bus Step-up transformer bank...
Question 2 A 60 Hz synchronous generator with Xd 0.2 pu transient reactance is connected to an infinite us through a transformer and the transmisiones as shown in the Figure. All system reactances are marked on the diagram and are expressed on a common MVA base. The generator dies a power of Auto busbar 1. The magnitude of the generator's excitation voltage e'is 12 pu, and the infinite bus voltage is -1.00u. If a 3-phase fault occurs at the middle...