Question

Page 1 of 2 0.5: The parameters of a 500/1000V 50Hz single phase transformer are given below: 2=1.2 + 32.4 6. Z=2.3 +j6.5 A,

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Que Home ferooting all Parcometers to poimary- 2 = 1.a+js un Zg 2.3t joun en Ro=loon E = 2.3 +964*( 500 500)? 3 = 0.575+3 1So I; = I, - I. = 4520°-4.672-24.92 I 40.80/2.77 so x 40.80%2.77 de vý = E; - (0.575+3,16) x 40.80 458.897-43-61-(0-575+)1.

Add a comment
Know the answer?
Add Answer to:
Page 1 of 2 0.5: The parameters of a 500/1000V 50Hz single phase transformer are given...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Three-phase, 50Hz, 6600/1000/440 Y V transformer

    A 3-phase, 50 Hz, 6600 /1000  /440 Y V. transformer. 1. Determine suitable numbers of turns to ensure the peak flux does not exceed 0.03 Web.                                                                                                            2. Determine the...

  • Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Prima...

    Please show full working Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Primary resistance-1562, secondary resistance-0.02 Ω Primary leakage reactance-140Q, Secondary leakage reactance-0.15Q, Magnetising reactance 30 k2, Core loss resistance 200 k2 (a) The transformer is connected to two loads in parallel. The first load is 10 kW at 0.866 power factor lagging and the second load is 15kVA with a power factor of 0.8 lagging. Find the percentage regulation and power efficiency...

  • Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Prima...

    Help me answer c and d Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Primary resistance-1562, secondary resistance-0.02 Ω Primary leakage reactance-140Q, Secondary leakage reactance-0.15Q, Magnetising reactance 30 k2, Core loss resistance 200 k2 (a) The transformer is connected to two loads in parallel. The first load is 10 kW at 0.866 power factor lagging and the second load is 15kVA with a power factor of 0.8 lagging. Find the percentage regulation and...

  • QUESTION 3 3.1 A single-phase 39 kW, 380 V, 50Hz induction motor operates on full load...

    QUESTION 3 3.1 A single-phase 39 kW, 380 V, 50Hz induction motor operates on full load with an efficiency of 89% and at a power factor of 0.809 lagging. Three identical parallel- connected capacitors are used to raise the power factor to 0.96. 3.1.1 Calculate the kVAr rating of the capacitor bank. (9) 3.1.2 Calculate the capacitance of each capacitor. (6) [15]

  • A single-phase transformer is rated at 10 kVA, 240/100 V. When the secondary terminals are open-circuited...

    A single-phase transformer is rated at 10 kVA, 240/100 V. When the secondary terminals are open-circuited and the primary winding is supplied at normal voltage, the input current is 2.6 A at a power factor of 0.3 lag. When the secondary terminals are short-circuited, a voltage of 18 V applied to the primary causes the full-load current to flow in the secondary, the power input to the primary being 240 W. Calculate (a) the regulation (b) the efficiency of the...

  • Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60...

    Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60 Hz. The following results are obtained from open-circuit and short-circuit tests: Test Open-circuit Short-circuit Voltage 7200 V 250 V Current 0.65 A 13.89 A Real Power Input 425 W 1420 W a) Determine the parameters of this transformer, all referred to the primary side. b) The secondary of this transformer is connected to a load that draws 100% of the rated power at rated...

  • A 60 Hz 20KVA 8000/240 Vrms transformer has the equivalent circuit parameters given in the table...

    A 60 Hz 20KVA 8000/240 Vrms transformer has the equivalent circuit parameters given in the table below, a) For the rated load having a lagging power factor of 0.8, find the magnitude of the load current in Amperes. 15 Primary resistance 0.02 econdary resistance 120 Primary leakage reactance X2wL2 0.15 Secondary leakage reactance Xm=wLm Magnetizing reactance 30 k Re 200 k Core-loss resistance Answer: Check b) Find the phase of he load current in degrees (note: sign is important). Answer:...

  • The S.C. test on a 1-phase transformer, with the primary winding short-circuited and 30 V applied...

    The S.C. test on a 1-phase transformer, with the primary winding short-circuited and 30 V applied to the secondary gave a wattmeter reading of 60 W and secondary current of 10 A. II the normal applied primary voltage is 200 V, the transformation ratio 1:2 and the full-load secondary current 10 A, calculate the secondary p.d. at full-load current for (a) unity power factor (b) power factor 0.8 lagging. these are the answers [ 394 V; 377.6 V ]

  • A single-phase transformer of nominal values of 10kVA, 440/220 V and 60 Hz supplies nominal load...

    A single-phase transformer of nominal values of 10kVA, 440/220 V and 60 Hz supplies nominal load at a power factor of 0.85 lagging connected to the side of low voltage. The load operates at a nominal voltage and the transformer has the following parameters: R=0.160, X,=0.48 , R=0.040, X=0.12, R900, Xy=1300. Determine: 1. The voltage regulation of the transformer. 2. The efficiency of the transformer.

  • QUESTION 3 A 200 - MVA, 15/200 kV single-phase power transformer has a per – unit...

    QUESTION 3 A 200 - MVA, 15/200 kV single-phase power transformer has a per – unit resistance of 1.2 percent and a per-unit reactance of 5 percent (data taken from the transformer's nameplate). The magnetizing impedance is impedance is j80 per unit. a. Find the equivalent circuit referred to the low-voltage side of this transformer. b. Calculate the voltage regulation of this transformer for a full-load current at power factor of 0.8 lagging. c. Assume that the primary voltage of...