Problem #2 An industrial system bus is fed from an infinite bus thru a 150 MVA, 115kV/38kV, X=5% substation connected to a 75 MVA, 38kV/13.8kV, X-6.5% substation. A 25 MW, 13.8 kV, pf=.85, 3-phase, x=16% diesel generator is also connected to the industrial system bus. Several feeders are connected to the 38kV bus. If a fault occurs in one of such feeders, plot sag voltage at the 13.8kV bus vs. distance to fault with and without the generator contribution. The...
1. A three-phase synchronous generator connected to a 345-KV transmission line through a transformer as shown in Figure P1. Parameters of both generator and transformer are given in the figure. Transformer losses and exciting current are neglected. A three-phase short-circuit occurs on the line side of the circuit breaker when the generator is operated at rated terminal voltage and at no-load. The breaker interrupts the fault three cycles after fault inception. Neglect the effect of the transformer on the time...
Problem 2 (50 points): The synchronous generator shown in the figure below is operated at its rated apparent power (100 MVA), 0.95 pf. lagging, and 5% above rated voltage. Determine the subtransient fault current if a three phase short circuit fault occurs at the terminal of the motor (Bus 2) T1 2 100 MVA 100 MVA 13.8 kV 13.8 kV Δ/138 kVY X" = 0.15 X = 0.10 100 MVA 138 kV Y/13.8 kV Δ X0.10 100 MVA 13.8 kV...
A 50 Hz, 250 MVA synchronous generator having inertia constant H=5 MJ/MVA is connected to an infinite bus through transformer and transmission line as shown below. The transformer reactance is based on 500 MVA, while the other impedances are based on the generator MVA Infinite bus 1 2 3 XL 0.1 pu - oto G1 V= 1.0 pu X 0.1 pu Xd = 0.3 pu at 500 MVA The generator is delivering 0.8 of full load current at a power...
A single line diagram of a power system is shown in Fig. 2. The system data with equipment ratings and assumed sequence reactances are given the following table. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn 0.05 per unit on the motor base. Assume that Pre-fault voltage is takin as VF-1.0 ,0° per unit and Pre- fault load current and Δ-Y transformer phase shift are neglected In the...
The equipment ratings for a five bus system are given as Generator G1: 50 MVA, 12 kV, Xd ’’=X2=0.20, X0= 0.10 per unit Generator G2: 100 MVA, 15 kV, Xd ’’=0.2, X2=0.23, X0= 0.10 per unit Transformer T1: 50 MVA, 10 kV (Y)/138 kV (Y), X=0.10 per unit Transformer T1: 100 MVA, 15 kV (∆)/138 kV (Y), X=0.10 per unit Each 138 kV line: X1=40 Ohms, X0=100 ohms (1) Draw out the zero-, positive-, and negative- sequence reactance diagrams for the original system using a 100-MVA,...
2. A single-line diagram of the power system considered is shown in Figure P2a, where negative- and zero-sequence reactances are also given. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn = 0.05 per unit on the motor base. The per-unit zero-, positive and negative-sequence networks on a 100-MVA is shown in Figure P26, 13.8-kV base in the zone of the generator. a. Reduce the sequence networks to their...
Four-bus power system shown in Fig. 1 are as follows: Generator G1: 200 MVA, 7.2 kv, X -0.15 p.u Generator G2: 250 MVA, 9.6 kV, X-0.12 p.u Generator G3: 500 MVA, 10 kV, X-0.25 p.u Transformer T1:200 MVA, 7.2 Δ /132 Y kV, X= 0.05 p.u Transformer T2: 250 MVA, 9.6 Δ /132 Y kV, X =0.15 p.u Transformer T3: 500 MVA, 10 Δ /132 Y kV, x-0.1 p.u Each 132-kV line:X,-10 Ω 1- A three-phase short circuit occurs at...
Transformer TI : 50 MVA, 10 kV Y/138 kV Y, X=0.10 per unit; Transformer T2: 100 MVA, 15 kV D/138 kV Y, X-0.10 per unit; Each 138-kV line: X1-400 A three-phase short circuit occurs at bus 5, where the prefault voltage is 15 kV. Prefault load current is neglected. (a)Draw the positive-sequence reactance diagram in per-unit on a 100-MVA, 15-kV base in the zone of generator G2. Determine: (b) the The'venin equivalent at the fault, (c) the subtransient fault current...
3. A 200 MVA, 20 kV, 60 Hz Y-connected solidly grounded three phase synchronous generator connected through a 200 MVA 20/138 KV Y-Y transformer to a 138 kV transmission line. The generator reactances to the machine's own base are X-1.10 Both of the transformers Y connections are solidly grounded and its positive, negative and zero sequence series resitances are all 0.10 pu. a. What is the voltage at the terminals of the generator during the sub transient period if a...