Question

2. A single-line diagram of the power system considered is shown in Figure P2a, where negative- and zero-sequence reactances

lingo Imotoro 10.10 j0.10 ¡0.315 10.05 10.10 ¡0.15 (a) Zero-sequence network line 10.10 ¡0.10 10.105 10.15 10.20 E = 1.00200

0 0
Add a comment Improve this question Transcribed image text
Answer #1

rool on toon 3.2 BY loomia 13-86V x=0.15 X ₂ 2017 Xozo.rs 2202 Xoz for Man tal Toorra Tw1974 -0. 27 TWITVA 138kN/13-8K0 X =Xos sерилсе е -ooo jo.315 , e jo.) Zero € 13 2 JA s 3 Zelf joultjais al - jo.25 for t-G faulte २७ 9 joins Cratory In 192 120(2) Joinede when 0.145 +200 Lo .: 3.533 L-9s po 3.5321. 10:283? La 120 jo:138+ j0.145 ein: Is a J3 * 3.533 (1 - 6-12 p.o = 6.

Add a comment
Know the answer?
Add Answer to:
2. A single-line diagram of the power system considered is shown in Figure P2a, where negative-...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • QUESTION 4. A single-line diagram of a power system is shown in Figure Q3 below, where...

    QUESTION 4. A single-line diagram of a power system is shown in Figure Q3 below, where negative and zero-sequence reactances are also given. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance X.=0.05 per unit on the motor base. Prefault voltage is VF1.05<Oº per unit whereas prefault load current is zero. Take A-Y transformer phase shifts into consideration. M Line tool X, - X2 - 200 100 MVA X =...

  • A single line diagram of a power system is shown in Fig. 2. The system data with equipment ratings and assumed sequence reactances are given the following table. The neutrals of the generator and A-Y...

    A single line diagram of a power system is shown in Fig. 2. The system data with equipment ratings and assumed sequence reactances are given the following table. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn 0.05 per unit on the motor base. Assume that Pre-fault voltage is takin as VF-1.0 ,0° per unit and Pre- fault load current and Δ-Y transformer phase shift are neglected In the...

  • The single-line diagram of a three-phase power system is shown. Equipment ratings are given as follows

    The single-line diagram of a three-phase power system is shown. Equipment ratings are given as follows: The inductor connected to generator 3 neutral has a reactance of \(0.05\) pu using generator 3 ratings as a base.1. Draw the zero-, positive-, and negative -sequence  reactance diagrams using a \(1000 \mathrm{MVA}, 765 \mathrm{kV}\) base in the zone of line \(1-2\).2. Faults at bus 2 are of interest. Determine the Thevenin equivalent of each sequence network as viewed from the fault bus. Prefault voltage...

  • The one-line diagram of a simple power system is shown in Figure 1. The neutral of...

    The one-line diagram of a simple power system is shown in Figure 1. The neutral of each generator is grounded through a current-limiting reactor of 0.25/3 per unit on a 100-MVA base. The system data expressed in per unit on a common 100-MVA base is tabulated below. The generators are running on no-load at their rated voltage and rated frequency with their emfs in phase. Determine the fault current for the following faults giving Zo = 0.35, Z = 0.22...

  • Figure 1 Single line diagram b2 b3 b1 b4 grid Τι 13 A power system single line diagram is shown...

    Figure 1 Single line diagram b2 b3 b1 b4 grid Τι 13 A power system single line diagram is shown in Figure 1. The single line diagram shows a synchronous generator G connected to a large 50 Hz grid via its unit transformer T and a network of three transmission lines. Relevant details of the grid, transformer, generator and overhead lines are provided in Tables I,II,II & IV respectively. A double line to ground fault occurs at bus 3 Questions....

  • a five bus system

    The equipment ratings for a five bus system are given as Generator G1: 50 MVA, 12 kV, Xd ’’=X2=0.20, X0= 0.10 per unit Generator G2: 100 MVA, 15 kV, Xd ’’=0.2, X2=0.23, X0= 0.10 per unit Transformer T1: 50 MVA, 10 kV (Y)/138 kV (Y), X=0.10 per unit Transformer T1: 100 MVA, 15 kV (∆)/138 kV (Y), X=0.10 per unit Each 138 kV line: X1=40 Ohms, X0=100 ohms (1) Draw out the zero-, positive-, and negative- sequence reactance diagrams for the original system using a 100-MVA,...

  • Transformer TI : 50 MVA, 10 kV Y/138 kV Y, X=0.10 per unit; Transformer T2: 100 MVA, 15 kV D/138 kV Y, X-0.10 per unit; Each 138-kV line: X1-400 A three-phase short circuit occurs at bus 5,...

    Transformer TI : 50 MVA, 10 kV Y/138 kV Y, X=0.10 per unit; Transformer T2: 100 MVA, 15 kV D/138 kV Y, X-0.10 per unit; Each 138-kV line: X1-400 A three-phase short circuit occurs at bus 5, where the prefault voltage is 15 kV. Prefault load current is neglected. (a)Draw the positive-sequence reactance diagram in per-unit on a 100-MVA, 15-kV base in the zone of generator G2. Determine: (b) the The'venin equivalent at the fault, (c) the subtransient fault current...

  • Problem 2 (50 points): The synchronous generator shown in the figure below is operated at its rat...

    Problem 2 (50 points): The synchronous generator shown in the figure below is operated at its rated apparent power (100 MVA), 0.95 pf. lagging, and 5% above rated voltage. Determine the subtransient fault current if a three phase short circuit fault occurs at the terminal of the motor (Bus 2) T1 2 100 MVA 100 MVA 13.8 kV 13.8 kV Δ/138 kVY X" = 0.15 X = 0.10 100 MVA 138 kV Y/13.8 kV Δ X0.10 100 MVA 13.8 kV...

  • The component parameters for the power system shown in Figure 2 are given in Table 1. The pre-fau...

    The component parameters for the power system shown in Figure 2 are given in Table 1. The pre-fault voltage is 120° pu and Zx-j0.1 pu. Table 1 Ratings X2-Xi (pu)Xo (pu) 0.05 0.10 0.20 0.20 Components G1, G2 200 MVA, 20 kV 0.10 0.10 0.10 0.10 T1, T2, T3200 MVA, 20/200 kV L1 200 MVA, 200 kV し2 200 MVA, 20 kV (a) Draw the three sequence networks and determine the per-unit Thevenin impedance of each sequence network seen from...

  • 2. A three-phase short circuit occurs at the bus 1 for the system shown in figure...

    2. A three-phase short circuit occurs at the bus 1 for the system shown in figure below. Neglecting prefault currents and assuming that the generator is operating at its rated voltage, determine the subtransient fault current using superposition. bus 1 bus 2 j6522 ww m AY 25 MVA 13.8 kV 15% 25 MVA 13.2/69 KV 11% 25 MVA 69/13.2 kV 11% 15 MVA 13 kV 15%