QUESTION 4. A single-line diagram of a power system is shown in Figure Q3 below, where...
2. A single-line diagram of the power system considered is shown in Figure P2a, where negative- and zero-sequence reactances are also given. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn = 0.05 per unit on the motor base. The per-unit zero-, positive and negative-sequence networks on a 100-MVA is shown in Figure P26, 13.8-kV base in the zone of the generator. a. Reduce the sequence networks to their...
A single line diagram of a power system is shown in Fig. 2. The system data with equipment ratings and assumed sequence reactances are given the following table. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn 0.05 per unit on the motor base. Assume that Pre-fault voltage is takin as VF-1.0 ,0° per unit and Pre- fault load current and Δ-Y transformer phase shift are neglected In the...
Problem 2 (50 points): The synchronous generator shown in the figure below is operated at its rated apparent power (100 MVA), 0.95 pf. lagging, and 5% above rated voltage. Determine the subtransient fault current if a three phase short circuit fault occurs at the terminal of the motor (Bus 2) T1 2 100 MVA 100 MVA 13.8 kV 13.8 kV Δ/138 kVY X" = 0.15 X = 0.10 100 MVA 138 kV Y/13.8 kV Δ X0.10 100 MVA 13.8 kV...
Transformer TI : 50 MVA, 10 kV Y/138 kV Y, X=0.10 per unit; Transformer T2: 100 MVA, 15 kV D/138 kV Y, X-0.10 per unit; Each 138-kV line: X1-400 A three-phase short circuit occurs at bus 5, where the prefault voltage is 15 kV. Prefault load current is neglected. (a)Draw the positive-sequence reactance diagram in per-unit on a 100-MVA, 15-kV base in the zone of generator G2. Determine: (b) the The'venin equivalent at the fault, (c) the subtransient fault current...
The single-line diagram of a three-phase power system is shown. Equipment ratings are given as follows: The inductor connected to generator 3 neutral has a reactance of \(0.05\) pu using generator 3 ratings as a base.1. Draw the zero-, positive-, and negative -sequence reactance diagrams using a \(1000 \mathrm{MVA}, 765 \mathrm{kV}\) base in the zone of line \(1-2\).2. Faults at bus 2 are of interest. Determine the Thevenin equivalent of each sequence network as viewed from the fault bus. Prefault voltage...
The equipment ratings for a five bus system are given as Generator G1: 50 MVA, 12 kV, Xd ’’=X2=0.20, X0= 0.10 per unit Generator G2: 100 MVA, 15 kV, Xd ’’=0.2, X2=0.23, X0= 0.10 per unit Transformer T1: 50 MVA, 10 kV (Y)/138 kV (Y), X=0.10 per unit Transformer T1: 100 MVA, 15 kV (∆)/138 kV (Y), X=0.10 per unit Each 138 kV line: X1=40 Ohms, X0=100 ohms (1) Draw out the zero-, positive-, and negative- sequence reactance diagrams for the original system using a 100-MVA,...
The one-line diagram of a simple power system is shown in Figure 1. The neutral of each generator is grounded through a current-limiting reactor of 0.25/3 per unit on a 100-MVA base. The system data expressed in per unit on a common 100-MVA base is tabulated below. The generators are running on no-load at their rated voltage and rated frequency with their emfs in phase. Determine the fault current for the following faults giving Zo = 0.35, Z = 0.22...
Q3: (15 Points) Equi below are given as follows: pment ratings and per-unit reactances for the system shown in circuit 2 4 T1 TL12 T2b G1 G2 TL13 TL23 0.03 j0.03 Synchronous Generators: G1 100 MVA 25 kV G2 100 MVA 3.8 kV Transformers: T1 100 MVA 25/230 kV T2 100 MVA 13.8 /230 kV X1=X2= 0.2 X0-0.05 X1-X2-0.2 X0 0.05 X1 = X2-X0 = 0.05 Transmission lines: TL12 100 MVA TL13 100 MVA TL23 100 MVA X0 0.3 XO...
A simple three-phase power system is shown in Figure 2. Assume that the ratings of the various devices in this system are as follows: • Generators G1, G2: 40 MVA, 13.2 kV, = 0.15 pu, = 0.15 pu, = 0.08 • Generator G3: 60 MVA, 13.8 kV, = 0.20 pu, 0.20 pu, - 0.08 • Transformers T1, T2, T3, T4: 40 MVA, 13.8/138 kV, X1 = X2 = 0.10 pu, XO 0.08 pu Transformers T5, T6: 30 MVA, 13.8/138 kV, X1 = X2...
Figure 1 Single line diagram b2 b3 b1 b4 grid Τι 13 A power system single line diagram is shown in Figure 1. The single line diagram shows a synchronous generator G connected to a large 50 Hz grid via its unit transformer T and a network of three transmission lines. Relevant details of the grid, transformer, generator and overhead lines are provided in Tables I,II,II & IV respectively. A double line to ground fault occurs at bus 3 Questions....