The single-line diagram of a three-phase power system is shown. Equipment ratings are given as follows:
The inductor connected to generator 3 neutral has a reactance of \(0.05\) pu using generator 3 ratings as a base.
1. Draw the zero-, positive-, and negative -sequence reactance diagrams using a \(1000 \mathrm{MVA}, 765 \mathrm{kV}\) base in the zone of line \(1-2\).
2. Faults at bus 2 are of interest. Determine the Thevenin equivalent of each sequence network as viewed from the fault bus. Prefault voltage is \(1.0\) pu. Prefault load currents are neglected.
3. Determine the subtransient fault current in pu and kA during a bolted three-phase fault at the fault bus \(2 .\)
4. Determine the subtransient fault current in pu and kA during a bolted single line-to-ground fault at the fault bus \(2 .\)
5. Determine the subtransient fault current in pu and kA during a bolted line-to-line fault at the fault bus \(2 .\)
6. Determine the subtransient fault current in pu and kA during a bolted double line-to- ground fault at the fault bus \(2 .\)
7. Verify the results of calculations by performing computer simulation using ETAP software.
8. Present a written repot with the results of all calculations and simulation. Make conclusions.
The single-line diagram of a three-phase power system is shown. Equipment ratings are given as follows
A single line diagram of a power system is shown in Fig. 2. The system data with equipment ratings and assumed sequence reactances are given the following table. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn 0.05 per unit on the motor base. Assume that Pre-fault voltage is takin as VF-1.0 ,0° per unit and Pre- fault load current and Δ-Y transformer phase shift are neglected In the...
2. A single-line diagram of the power system considered is shown in Figure P2a, where negative- and zero-sequence reactances are also given. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn = 0.05 per unit on the motor base. The per-unit zero-, positive and negative-sequence networks on a 100-MVA is shown in Figure P26, 13.8-kV base in the zone of the generator. a. Reduce the sequence networks to their...
QUESTION 4. A single-line diagram of a power system is shown in Figure Q3 below, where negative and zero-sequence reactances are also given. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance X.=0.05 per unit on the motor base. Prefault voltage is VF1.05<Oº per unit whereas prefault load current is zero. Take A-Y transformer phase shifts into consideration. M Line tool X, - X2 - 200 100 MVA X =...
The Fig. P1.1 is a one-line diagram of a simple power system. There prefault system is on no-load with 1.0 pu voltage and prefault currents are zero. A BOLTED THREE-PHASE FAULT occurs at point P. (a) Draw the pre-fault single-phase equivalent circuit showing numerical values. (b) (i) Calculate the subtransient current in the fault (ii) Calculate the voltages at the busses during the fault. (iii)Calculate the e subtransient current in the lines. (c)) Determine the Zbus relating the bus currents...
the single-line diagram of a three-phase power system is shown in figure 9.17. equipment ratings are given as follows: The inductor connected to Generator 3 neutral has a reactance of 0.05 per unit using generator 3 ratings as a base. Draw the zero-, positive-, and negative-sequence reactance diagrams using a 1000-MVA, 765-kV base in the zone of line 1-2. Neglect the Δ—Y. transformer phase shifts.
3.13 A single-line diagram of a three-phase power system is shown in Fig. 3.51. The ratings of the equipment are shown below Generator G: 100 MVA, 11 kV, Xi -X2-0.20 pu, Xo -0.05 pu Generator G2 : 100 MVA, 20 kV, Xi=X2=0.25 pu, Xo=0.03 pu, X,,-0.05 pu Transformer T: 100 MVA, 11/66 kV, Xi -X2-Xo 0.06 pu Transformer T2: 100 MVA, 11/66 kV, Xi-X2 = Xo 0.06 pu Line: 100 MVA, X,-X2 = 0.15 pu, Xo = 0.65 pu A...
3) The single-line diagram of a three-phase power system is shown in Fig. 1. Equipment ratings are given as follows: G1 1,000 MVA, 15.0 kV, 20.18, o 0.07 pu G2 : 1,000 MVA. 15.0 kV, 攻=エ1 =エ2 = 0.20, ro = 0.10 pu G3 : 500 MVA, 13.8 kV. 1" = 띠 z2 = 0.15, zo 0.05 pu G4 : 750 MVA, 13.8 kV. ェd =ェ1 = 0.30, T2 = 0.40 ro = 0.10 pu Ti : 1,000 MVA. 15.0Δ/765Y...
The zero-, positive-, and negative-sequence bus impedance matrices for a three bus power system are given below 5. T0.10 0.15 0.121 Bu0.15 0.10 0.08 pu [0.16 0.10 0.15] Lo.15 0.14 0.30 0.12 0.08 0.35 ZBus ZBus0.10 0.20 0.14 pu Determine the per unit fault current and the bus voltages during fault for (a) A bolted three-phase fault at bus 2. (b) A bolted single line-to-ground fault at bus 2. (c) A bolted line-to-line fault at bus 2 (d) A bolted...
The reactance data for the power system shown in figure 10.30 in per unit on a common base is as follows: *************Remember calculations are needed at bus 2 **************** 10.15. The reactance data for the power system shown in Figure 10.30 in per unit on a common base is as follows Item X1 G1 0.10 0.10 0.05 G2 0.10 0.10 0.05 T, 0.25 0.25 0.25 T 0.25 0.25 0.25 Line 1-2 0.30 0.30 0.50 Ti 1 3 2 FIGURE 10.30...
Transformer TI : 50 MVA, 10 kV Y/138 kV Y, X=0.10 per unit; Transformer T2: 100 MVA, 15 kV D/138 kV Y, X-0.10 per unit; Each 138-kV line: X1-400 A three-phase short circuit occurs at bus 5, where the prefault voltage is 15 kV. Prefault load current is neglected. (a)Draw the positive-sequence reactance diagram in per-unit on a 100-MVA, 15-kV base in the zone of generator G2. Determine: (b) the The'venin equivalent at the fault, (c) the subtransient fault current...