Question

The temperature of the condenser in the absorption system shown in Figure 1 drops down to 34°C. Determine the concentration and enthalpy of the solution at point 4 and comment on the results obtained. Assume that all other temperatures are unchanged. (6 marks)

(5) Water vapor Dots Qe a Condenser Generator 95 °C 40 °C To L Heat exchanger t o Water vapor LiBr solution water vapor Absor

0 0
Add a comment Improve this question Transcribed image text
Answer #1

# Solution # Mass flow rate of Libr - ma. mass flow rate of water = mw. spacific heat of Libr c = 0.59 kJ Spacific heat of wafor Heat exchanger Heat loss by 3-2 = Heat gain by 1-2 mac (T3-T4) z mo e (T2 -T.) 0.45 (95 - Ty) = 0.65X(54-30) - Tu = 6oc A

Add a comment
Know the answer?
Add Answer to:
The temperature of the condenser in the absorption system shown in Figure 1 drops down to...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 3/ A LiBr-H2O absorption cooling system contains of one solution heat exchanger, generator, condense an evaporator,...

    3/ A LiBr-H2O absorption cooling system contains of one solution heat exchanger, generator, condense an evaporator, and an absorber. The temperatures of the main components °C at condenser, 10 °C at evaporator, and 30 °C at absorber. The cooling capacity at the evaporator is are 100 °C at generator, 40 100 Ton, and the flow rate of the pump is 34.2 kg/min. And the temperature at outlet of heat exchanger and the inlet to the generator is 52 °C Find...

  • QV An absorption system use LiBr-H2O solution. The system consists of two he exchangers (refrigerant heat exchanger...

    QV An absorption system use LiBr-H2O solution. The system consists of two he exchangers (refrigerant heat exchanger and solution heat exchanger). All temperatures are shown in figure 2 below. The cooling capacity at the evaporator is 100 Tons. Calculate the rate of heat transfer at the generator, the temperatures at point 4 & 9 and the overall COP. 5 cond, 40°C- Gen. 100 c 43 C Ref.Heat Solution Heat Exchanger E.v Abs. 30 C Pump. QV An absorption system use...

  • A Refrigeration System Using R-134A In a refrigeration system, the refrigerant R-134A begins as s...

    A Refrigeration System Using R-134A In a refrigeration system, the refrigerant R-134A begins as saturated vapor at -15°(State 1). It then goes through a reversible adiabatic compressor to reach State 2. After flowing through the condenser (a heat exchanger), the refrigerant exits as saturated liquid at 70°C (State 3). It is then throttled by going through an expansion valve, to reach State 4. It finishes the cycle by going through another heat exchanger (the evaporator), to return to State 1....

  • now pleassse QUESTI 20 points Save An The heat-pump system shown is designed to provide water...

    now pleassse QUESTI 20 points Save An The heat-pump system shown is designed to provide water heating and space-cooling. The system includes a heat exchanger to subcool the R134a refrigerant at the outlet of the water heater while heating the refrigerant at the outlet of the evaporator. Given the following data, determine the enthalpy at each station, 1 through 6, using the R134a property tables (click here). Type your answers hy through h6 in the space provided below, and show...

  • 5-6 Figure 5-6 shows the schematic diagram for a two-stage cascade refrigeration system. Each stage operates...

    5-6 Figure 5-6 shows the schematic diagram for a two-stage cascade refrigeration system. Each stage operates on an ideal vapor-compression refrigeration cycle with refrigerant- 134a as the working fluid. All the important data and refrigerant phases are given in the schematic diagrams. By referring to the diagrams, determine: (a) The ratio of mass flow rate of the system and draw a T-s diagram complete with the data given. Enthalpy values for each states. Compressor power input for Cycle A and...

  • The heat-pump system shown is designed to provide water-heating and space-cooling. The system includes a heat...

    The heat-pump system shown is designed to provide water-heating and space-cooling. The system includes a heat exchanger to subcool the R134a refrigerant at the outlet of the water heater while heating the refrigerant at the outlet of the evaporator. Given the following data, determine the enthalpy at each station, 1 through 6, using the R134a property tables (click here). Type your answers hy through h6 in the space provided below, and show all your work on your paper. · At...

  • PLEASE ANSWER QUICKLY!! I WILL THUMBS UP! Thank you so much in advance!! The heat-pump system...

    PLEASE ANSWER QUICKLY!! I WILL THUMBS UP! Thank you so much in advance!! The heat-pump system shown is designed to provide water-heating and space-cooling. The system includes a heat exchanger to subcool the R134a refrigerant at the outlet of the water heater while heating the refrigerant at the outlet of the evaporator. Given the following data, determine the enthalpy at each station, 1 through 6, using the R134a property tables (click here). Type your answers hy through h6 in the...

  • 1. (20 points) Consider a cogeneration system operating at steady state. Superheated steam enters the first...

    1. (20 points) Consider a cogeneration system operating at steady state. Superheated steam enters the first turbine stage at 6 MPa, 540 °C. Between the first and second stages, 45% of the steam is extracted at 500 kPa and diverted to a process heating load of 5 x 108 kl/h. Condensate exits the process heat exchanger at 450 kPa with specific enthalpy of 589.13 kl/kg and is mixed with liquid exiting the lower pressure pump at 450 kPa. The entire...

  • Problem (2) (weight 40%) Figure Q2 shows a steam power system which is consisting of the...

    Problem (2) (weight 40%) Figure Q2 shows a steam power system which is consisting of the following processes: Process 1-2: heat addition at constant pressure of 100 bar. Process 2-3: Expansion in a high pressure turbine to 10 bars. Process 3-4: heat addition at constant pressure of 10 bar. Process 4-5: Expansion in a low pressure turbine to 0.1 bar. Process 5-6: Heat removal in a heat exchanger at constant pressure of 0.1 bar. The different water and steam operating...

  • Problem #1 (40 Marks) A refrigeration system is designed to maintain a cool space at -20°C in arn environment of +50°C....

    Problem #1 (40 Marks) A refrigeration system is designed to maintain a cool space at -20°C in arn environment of +50°C. The wide temperature range is difficult to achieve with a single refrigerant, because the refrigerant will generally be at excessively high pressures at the top of the temperature range, and sub-atmospheric pressures at the bottom end The problem is solved with a 2-stage cascaded system that uses refrigerant 134a (R134a) and refrigerant 22 (R22) respectively for the high temperature...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT