(2 points) A section load center contains a 250 kVA single-phase transformer with a turn ration...
Ideal, single-phase two-winding transformer A single-phase two-winding transformer is rated 20 kVA, 480/120 V, 60 Hz A source connected to the 480-V winding supplies an impedance load con- nected to the 120-V winding. The load absorbs 15 kVA at 0.8 p.f. lagging Ideal, single-phase two-winding transformer A single-phase two-winding transformer is rated 20 kVA, 480/120 V, 60 Hz A source connected to the 480-V winding supplies an impedance load con- nected to the 120-V winding. The load absorbs 15 kVA...
A single-phase 100-kVA, 2400/240-volt, 60-Hz distribution transformer is used as a step-down transformer. The load, which is connected to the 240-volt secondary winding, absorbs 80 kVA at 0.8 power factor lagging and is at 230 volts. Assuming an ideal transformer, calculate the following: a) primary voltage. b) load impedance. c) load impedance referred to the primary. d) the real and reactive power supplied to the primary winding
Al. A 1 kVA single-phase step-down transformer is connected to a 220 V, 50 Hz A.C. source and delivers power to a load. The winding resistance and reactance at secondary side are 0.02 2 and 0.1 12 respectively. The maximum value of core flux is 0.248 mWb and the secondary winding contains 1000 turns. Evaluate a. b. the voltage induced on the secondary side; the turn ratio of primary side to secondary side; the rated current on both sides; and...
3.4 A single-phase 100-kVA, 2400/240-volt, 60-Hz distribution transformer is used as a step-down transformer. The load, which is connected to the 240-volt secondary wind- ing, absorbs 80 kVA at 0.8 power factor lagging and is at 230 volts. Assuming an ideal transformer, calculate the following: (a) primary voltage, (b) load impedance, (c) load impedance referred to the primary, and (d) the real and reactive power sup- plied to the primary winding.
A three-phase Yy0 connected transformer has a nominal rating of 250 kVA and a voltage ratio 15:0.4 kV. After conducting the short-circuit test, where the secondary winding is short-circuited, it is found that the primary series resistance is 0.08 pu and the primary series impedance magnitude is 0.1pu. The effect of the parallel branch in the transformer’s equivalent circuit may be neglected. Explain what information ‘Yy0’ gives about the transformer. Draw the per-phase equivalent circuit of the transformer during the...
A single-phase transformer is rated at 10 kVA, 240/100 V. When the secondary terminals are open-circuited and the primary winding is supplied at normal voltage, the input current is 2.6 A at a power factor of 0.3 lag. When the secondary terminals are short-circuited, a voltage of 18 V applied to the primary causes the full-load current to flow in the secondary, the power input to the primary being 240 W. Calculate (a) the regulation (b) the efficiency of the...
Q1 A 1kVA ideal single phase step-up transformer is supplied by a 24 V ac power source and is delivering power to a 10 Ω resistive load connected to the secondary side. If the transformer is operated at full load (1kVA), determine, a) the secondary current IS; (3 marks) b) the secondary voltage VS; (2 marks) c) the primary current IP; (2 marks) d) the turn ratio of primary winding to secondary winding; and (2 marks) e) the number of...
Three single-phase transformers rated at 250 kVA, 7200 V/600 V, 60 Hz, are connected in wye- delta on a 12.47 kv, 3-phase line. If the load is 450 kVA, calculate: a. The currents in the incoming and outgoing transmission lines b. The currents in the primary and secondary windings 1. sratod t 200 w 3o0 v/6oO V 60 Hz are used to raise the
Three single-phase transformers rated at 250 kVA, 7200 V/600 V, 60 Hz, are connected in wye-...
3. Three single-phase, 10 kVA, 460/120 V, 60 Hz transformers are connected to form a three-phase 460/208 V transformer bank. The equivalent impedance of each transformer referred to HV side is 1.0 + j2.0 Ω. The transformer delivers 25 kW at 0.9 pf lagging at rated voltage. Answer the following questions: (a) Draw a schematic diagram showing the transformer connection. Draw three separate single-phase transformers and complete their primary and secondary connections. (b) Determine the magnitude of transformer primary and...
A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting three single phase transformers in the Dynll vector group as shown in Fig.P1. The per phase equivalent circuit parameters on the high voltage side are: R1-0.72 Ω, Xi,-0.92 Ω, R2-0.70 Ω, Xp-0.90 Ω, R.-308.49 Ω, and X,,-44.61 Ω (a) Sketch the corresponding phasor diagram of the primary and secondary voltages for the Dynll vector group; lagging; terminal voltage is 415 V line to line, and...