Question

A heat pump operates on the ideal vapor compression refrigeration cycle with R-134a. The condenser pressure...

A heat pump operates on the ideal vapor compression refrigeration cycle with R-134a. The condenser pressure is 1.2 MPa and the specific enthalpy at the inlet to condenser is 279 kJ/kg. If the mass flow rate of the refrigerant is 0.193 kg/s, the rate of heat supply to the heated space is

answer is 31.1 kw

0 0
Add a comment Improve this question Transcribed image text
Answer #1

In ideal vapor compression refrigeration cycle ,

  Warm Environmet Qh Saturated liquid - Condenser 2

Rate of Heat supply to heated space is \dot{Q_{h}} given by,

  \dot{Q_{h}}=\dot{m}(h_{1}-h_{2}) -------(1)

from R134a properties table we can get the enthaly values

at inlet of condenser:

  h_{1}=279kJ/kg

at outlet of condenser :

refrigerant leaved as saturated liquid from condenser

at 1.2 MPa condenser pressure

=>h_{2}=117.8kJ/kg

From equation-(1) we can get

=>\dot{Q_{h}}=\dot{m}(h_{1}-h_{2})

=>\dot{Q_{h}}=0.193(279-117.8)

  \dot{Q_{h}}=31.1116 kW

So Rate of heat supply to the heated space is 31.1kw

Add a comment
Know the answer?
Add Answer to:
A heat pump operates on the ideal vapor compression refrigeration cycle with R-134a. The condenser pressure...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A refrigerator operates on an ideal vapor compression refrigeration cycle with R-134a as the working fluid....

    A refrigerator operates on an ideal vapor compression refrigeration cycle with R-134a as the working fluid. The evaporator pressure is 0.12 MPa and the condenser pressure is 0.8 MPa. If the rate of heat removal from the refrigerated space is 32 kJ/s, the mass flow rate of refrigerant is

  • QUESTION 3 A heat pump that operates on the ideal vapor compression cycle with refrigerant-134a is...

    QUESTION 3 A heat pump that operates on the ideal vapor compression cycle with refrigerant-134a is used to heat water from 15°C to 45°C at a rate of 0.12 kg/s. the condenser and evaporator pressures are 1.4 and 0.32 MPa, respectively Determine: (a) The power input to the heat pump QUESTION 3 A heat pump that operates on the ideal vapor compression cycle with refrigerant-134a is used to heat water from 15°C to 45°C at a rate of 0.12 kg/s....

  • Condenser Compressor An ideal vapor-compression refrigeration cycle is modified to include a counter-flow heat exchanger as...

    Condenser Compressor An ideal vapor-compression refrigeration cycle is modified to include a counter-flow heat exchanger as shown. Refrigerant 134a leaves the evaporator as saturated vapor at 0.10 MPa and is heated at constant pressure to 20°C before entering the compressor. Following isentropic compression to 1.4 MPa, the refrigerant passes through the condenser and exits at 45°C and 1.4 MPa. The liquid then passes through the heat exchanger and enters the expansion valve at 1.4 MPa. The mass flow rate of...

  • An ideal vapor-compression refrigerant cycle operates at steady state with Refrigerant 134a as the working fluid....

    An ideal vapor-compression refrigerant cycle operates at steady state with Refrigerant 134a as the working fluid. Saturated vapor enters the compressor at -10°C, and saturated liquid leaves the condenser at 28°C. The mass flow rate of refrigerant is 5 kg/min. Determine (a) The compressor power, in kW (b) The refrigerating capacity, in tons. (c) The coefficient of performance. Sketch the system on a T-s diagram with full label. A vapor-compression heat pump with a heating capacity of 500 kJ/min is...

  • 11-14 A refrigerator uses refrigerant-134a as the working fluid and operates on an ideal vapor-compression refrigeration...

    11-14 A refrigerator uses refrigerant-134a as the working fluid and operates on an ideal vapor-compression refrigeration cycle between 0.12 and 0.7 MPa. The mass flow rate of the refrigerant is 0.05 kg/s. Show the cycle on a T-s diagram with respect to saturation lines. Determine (a) the rate of heat removal from the refrigerated space and the power input to the compressor, (b) the rate of heat rejection to the environment, and (c) the coefficient of performance. Answers: (a) 7.41...

  • (12 points) A refrigerator using refrigerant-134a as the working fluid operates on the vapor compression cycle....

    (12 points) A refrigerator using refrigerant-134a as the working fluid operates on the vapor compression cycle. The cycle operates between 200 kPa and 1.2 MPa. The refrigerant flows through the cycle at a rate of 0.019 kg/s. The (actual) refrigerator has a compressor with an isentropic efficiency of 85%. The refrigerant enters the compressor slightly superheated by 56 C hint add this to the saturation temperature). The refrigerant leaves the condenser slightly subcooled by 1.9°C. What is the rate of...

  • In a heat pump operating according to the vapor compression refrigeration cycle, the refrigerant is R-134a....

    In a heat pump operating according to the vapor compression refrigeration cycle, the refrigerant is R-134a. A water source of 11 °C is used to heat a house with a heating load of 17 kW. Refrigerant enters the compressor as saturated steam at 100 kPa pressure and rises at 1.6 MPa, 60 ° C. The temperature of the refrigerant at the outlet of the condenser is 30°C. a) The amount of heat at the beginning of the water, b) Compressor...

  • An ideal vapor-compression refrigeration cycle operates at steady state with Refrigerant 134a as the working fluid....

    An ideal vapor-compression refrigeration cycle operates at steady state with Refrigerant 134a as the working fluid. Saturated vapor enters the compressor at 1.25 bar, and saturated liquid exits the condenser at 5 bar. The mass flow rate of refrigerant is 8.5 kg/min. A. Determine the magnitude of the compressor power input required, in kW (report as a positive number). B. Determine the refrigerating capacity, in tons. C. Determine the coefficient of performance. Please answer all parts of the question. Thanks!

  • A heat pump uses R-134a as the working fluid and operates on an ideal vapor-compression refrigeration...

    A heat pump uses R-134a as the working fluid and operates on an ideal vapor-compression refrigeration cycle between 26 psia and 138 psia. Determine (on a per unit mass basis) (a) the amount of heat transferred from the refrigerated space, (b) the amount of heat rejected by the cycle, (c) the work input required by the compressor, (d) the quality at the exit of the throttle valve, and (e) and the COP.

  • A two-stage compression refrigeration system with an adiabatic liquid-vapor separation unit uses refrigerant-134a as working fluid....

    A two-stage compression refrigeration system with an adiabatic liquid-vapor separation unit uses refrigerant-134a as working fluid. The system operates the evaporator at 0.4 MPa, the condenser at 1.6 MPa, and the separator at 0.8 MPa. The compressors use 25 kW of power. Given that the refrigerant is saturated liquid at the inlet of each expansion valve and saturated vapor at the inlet of each compressor, and the compressors are isentropic: (0) show the process on a T-s diagram; ) calculate...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT