Section 2: Three phase circuit Three phase wye connected generator supplies two parallel loads through a...
Problem 2:Three phase droult (42 pts) A three-phase wye connected generator ﹃plies two paral el loads through a feeder. tad is matalaeeday connected load and load 2 is a balanced delta connected loed. System data: Generator: Rating S-5oo MVA; Line Voltage: Veu-25KV; Feeder impedance: 7-(0.08 jo 62) O/mile, length-8 miles Generator reactance Xe- 1108: P.-75MW pf c-o.78 (all the power factors are lagging) (a) Draw the one-line diagram and a three-phase equivalent circuit (8pts) (b) Calculate the generator and feeder...
Question 2: Three phase circuit. (100p) A wye connected generator supplies a delta connected balanced load through short feeder. seree the load line to neutral voltage as reference voltage phase angle zero. 02.1 Q2.2 Q2.3 Q2.4 Draw the equivalent circuit. 10p Calculate the load line-to-neutral voltages and line-to-line voltages. 20p Calculate the delta load currents and feeder currents. 20p Calculate the supply wye connected generator line-to-neutral voltages. Is the obtained values are acceptable? Calculate the generator real and reactive power...
A balanced three-phase network supplies a balanced load through a three-phase wye-wye connected transformer as shown in the following figure. Transformer Supply Network B8 Load Y-Y The wye-wye connected transformer has the following parameter: S 25 MVA Xir 15% 240/132 kV The three-phase load parameters are: Pload 20 MW pfload 0.8 The three-phase supply network line voltage and short circuit current are: Vnet 225 kV Inet_short= 15 kA. A. Calculate primary and secondary current rating. B. Calculate trans former actual...
Problem 7 Three three-phase wye-connected loads are in parallel across a three-phase supply. The first load draws a current of 10 A at pf- 0.93 (leading), and the second and third loads (each) draw a current of 20 A at pf= 0.85 (lagging). Suppose the line-to-line voltage is 240 V. Compute the following: a) The transmission line current b) The load power factor c) The complex power supplied by the source
Problem 7 Three three-phase wye-connected loads are in parallel...
Show the circuit for a three-phase, AC(60Hz), WYE configured generator connected to a balanced load of three resistors(Each 100 Ohms) wire in a delta configuration. Find: a.) current in each coil of the generator b.)the power generated in each coil c.) the total poor output of the generator d.) the current in each line to the load e.) voltage across each resistor f.) current in each resistor g.) power dissipated in each resistor h.) total power in the entire load...
10. Two loads connected in parallel draw a total of 2.4 kW at 0.8 pflagging from a 120-V rms, 60- Hz line. One load absorbs 1.5 kW at a 0.707 pf lagging. Determine: (a) the pf of the second load, INV 11. Calculate the line currents for the system shown in figure. Calculate also the total power and reactive power consumed by the load. w 12. For the balanced three-phase circuit in Fig.. Calculate the line currents, the phase voltage...
2. Two balanced three-phase loads are connected in parallel. One load with per phase impedance 21 ?, is connected in delta, and the other load has per phase impedance 15 2 and is connected in wye. Ignore the line impedance. If the line voltage is a 208230° Vrms, determine (a) the phase voltage for phase-a, ) the line current Ia*, (c) the phase currents in the delta load (d) the complex power of the load and the power factor.
I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....
I. A balanced three-phase positive sequence wye-connected 60Hz source voltage has line-neutral voltage of V, 1000 V. It is connected to a three- phase wye connected load whose impedance is z 50+j37.7 2 a. Find line currents ia ib, ic and line-line voltages Vab, Vbo Vac b. Find the total complex power delivered to the load. c. Find delta-connected capacitor bank needed to bring the PF to 0.95 (lagging) of system. d. Re-calculate currents la, ib, io with Case c....
Problem 4 Three ideal single-phase transformers are connected in a delta/wye configuration with the primary side of the three-phase transformer rated at 120 kV and the secondary side rated at 13.8 kV. The rated power of the transformer bank is 20 MVA. One side of the transformer bank is connected to a 120 kV transmission line, and the other side is connected to a three-phase load of 15 MVA at 0.85 lagging power factor. Compute the following: a) The turns...