Question

Mark the following data on PH chart and calculate Coefficient of performance and heat rejected in...

  1. Mark the following data on PH chart and calculate Coefficient of performance and heat rejected in condenser. The mass flow rate of refrigerant is 0.25 kg/s. The refrigerant used is 134a.          

                              Condenser pressure = 10 bar

                               Evaporator pressure = 0.4 bar.

                              Compressor inlet temperature = -20 ℃

                              Expansion device inlet temperature = 30 ℃                                         

                                                                                                          

0 0
Add a comment Improve this question Transcribed image text
Answer #1

In this problem, first find the specific enthalpy of Refrigerant at each state of the cycle from p-h chart of the refrigerant R-134a and then Calculate the coefficient of performance of cycle and heat rejected in condenser as below:-

Ciren data :-( Refrigerant R-1340) (bar) to- 18= constant (+83k/sk) 0.4 Ft- m P, - PA = 0.4 bar P2 = P3= 10 bar T= -20°C Tz =Copa del Rei CoP = 2:176 Heat rejected in condenser (Qc):- de = mp (he-hs) = 8:25 (456 - 240) kW Te = 54 KW

Add a comment
Know the answer?
Add Answer to:
Mark the following data on PH chart and calculate Coefficient of performance and heat rejected in...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 1) A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated...

    1) A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated space at -30°C by rejecting its waste heat to cooling water that enters the condenser at 16 °C at a rate of 0.25 kg/s and leaves at 26°C. The refrigerant enters the condenser at 1.2 MPa and 65°C and leaves at 42°C. The inlet state of the compressor is 60 kPa and -34°C and the compressor is estimated to gain a net heat of...

  • Condenser Compressor An ideal vapor-compression refrigeration cycle is modified to include a counter-flow heat exchanger as...

    Condenser Compressor An ideal vapor-compression refrigeration cycle is modified to include a counter-flow heat exchanger as shown. Refrigerant 134a leaves the evaporator as saturated vapor at 0.10 MPa and is heated at constant pressure to 20°C before entering the compressor. Following isentropic compression to 1.4 MPa, the refrigerant passes through the condenser and exits at 45°C and 1.4 MPa. The liquid then passes through the heat exchanger and enters the expansion valve at 1.4 MPa. The mass flow rate of...

  • 2. (10 points) An ideal vapor-compression refrigeration cycle is modified to include a counter- flow heat...

    2. (10 points) An ideal vapor-compression refrigeration cycle is modified to include a counter- flow heat exchanger, as shown below. Ammonia leaves the evaporator as saturated vapor at 1.0 bar and is heated at constant pressure to 5 "C before entering the compressor. Following isentropic compression to 18 bar, the refrigerant passes through the condenser, exiting at 40 C, 18 bar. The liquid then passes through the heat exchanger, entering the expansion valve at 18 bar. If the mass flow...

  • The coefficient of performance-of vapor-compression refrigeration cycles

    a) The coefficient of performance-of vapor-compression refrigeration cycles improves when the refrigerant is subcooled before it enters the throttling valve Can the refrigerant be subcooled indefinitely to maximize this effect, or is there a lower limit? Explain brieflyb) A two-stage compression refrigeration system with a flash chamber is used to produce chilled water for a commercial building The refrigeration system operates between a pressure limits of 1 2 MPa and 200 kPa with refrigerant-134a as the working fluid. The refrigerant leaves...

  • R134a refrigerant In a vapor compression refrigeration system the following observations were noted. Condenser pressure 2...

    R134a refrigerant In a vapor compression refrigeration system the following observations were noted. Condenser pressure 2 bar. Evaporator pressure 0.02 MPa. Sub-cooling 10°C. Super heating 20°C. Estimate the power consumed by compressor, heat absorbed in evaporator, heat rejected in condenser and coefficient of performance. Mark all given data in PH and TS diagram.

  • 6. An office building requires a heat transfer rate of 20 kW to maintain the inside temperature a...

    6. An office building requires a heat transfer rate of 20 kW to maintain the inside temperature at 21°C when the outside temperature is 0°C. A vapor-compression heat pump with Refrigerant 134a as the working fluid is to be used to provide the necessary heating. The compressor operates adiabatically with an isentropic efficiency of 82%. Specify appropriate evaporator and condenser pressures of a cycle for this purpose assuming Δ1cond-Al evap-10°C, as shown below. The states are numbered as shown below....

  • A heat pump with refrigerant-134a as the working fluid is used to keep a space at 25°C by |absorbing heat from geotherm...

    A heat pump with refrigerant-134a as the working fluid is used to keep a space at 25°C by |absorbing heat from geothermal water that enters the evaporator at 50°C at a rate of 0.046 kg/s and leaves at 40°C. The refrigerant enters the evaporator at 20°C with a quality 23 percent and leaves at the inlet pressure as saturated vapor. The refrigerant loses305 W o heat to the surroundings as it flows through the compressor and the refrigerant leaves the...

  • Exercise 4 In the ideal vapour-compression refrigerator using refrigerant 134a, the evaporator temperature is -20 C,...

    Exercise 4 In the ideal vapour-compression refrigerator using refrigerant 134a, the evaporator temperature is -20 C, and the inlet temperatu enters the compressor. Calculate: re to the condenser is 30°C. Saturated vapour a. The work of the compressor b. The heat transfer from the condenser c. The heat transfer to the evaporator d. The coefficient of performance

  • Refrigerant 134a flows through an ideal vapor compression heat pump system with a heating capacity of...

    Refrigerant 134a flows through an ideal vapor compression heat pump system with a heating capacity of 60,000 Btu/hr. The condenser operates at 200 psi, and the evaporator temperature is 0°F. The refrigerant is a saturated vapor at the evaporator exit and a saturated liquid at the condenser exit. The temperature at the compressor exit is 180°F. Assuming the compressor is not 100% isentropic, determine: a) Mass flow rate (lbm/min) b) Compressor power (hp) c) Isentropic compressor efficiency d) Coefficient of...