A circuit must handle an adjusted load (165 amps x 1.25) of 206 amps. Per Table...

A circuit must handle an adjusted load (165 amps x 1.25) of 206 amps. Per Table 28.2, 75 C column, this will require a 4/0 conductor. It has been decided that it will be more cost effective to install parallel conductors to serve the load. Which of the following parallel conductors will be sufficient for this circuit?

Note: the number in parentheses represents the quantity of conductors to be used, i.e (2) is two conductors.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

4/0 wire gauge size conductor can handle current of ampacity level 230A. Rating size is 206 A.

As per NEC wire gauge size of 2 handle 115 A current.

So two conductor of wire gauge size (2) can be used in parallel.

Add a comment
Know the answer?
Add Answer to:
A circuit must handle an adjusted load (165 amps x 1.25) of 206 amps. Per Table...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • summarizr the followung info and write them in your own words and break them into different...

    summarizr the followung info and write them in your own words and break them into different key points.   6.5 Metering Chamber: 6.5.1 The minimum size of the metering box is governed by the metering area required to obtain a representative test area for the specimen (see 7.2) and for maintenance of reasonable test accuracy. For example, for specimens incorporating air spaces or stud spaces, the metering area shall span an integral number of spaces (see 5.5). The depth of...

  • summatize the following info and break them into differeng key points. write them in yojr own...

    summatize the following info and break them into differeng key points. write them in yojr own words   apartus 6.1 Introduction—The design of a successful hot box appa- ratus is influenced by many factors. Before beginning the design of an apparatus meeting this standard, the designer shall review the discussion on the limitations and accuracy, Section 13, discussions of the energy flows in a hot box, Annex A2, the metering box wall loss flow, Annex A3, and flanking loss, Annex...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT