Question

Two shunt generators running in parallel share a load of 100 kW equally at a terminal...

  1. Two shunt generators running in parallel share a load of 100 kW equally at a terminal voltage of 230 V. On no-load, their voltages rise to 240 V and 245 V respectively. Assuming that their volt-ampere characteristics are rectilinear, find how would they share the load when the total current is reduced to half its original value? Also, find the new terminal voltage.

Answers: 20 kW

30 kW

and 236V.

Complete solution please.

0 0
Add a comment Improve this question Transcribed image text
Know the answer?
Add Answer to:
Two shunt generators running in parallel share a load of 100 kW equally at a terminal...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A long-shunt compound generator running at 1000 r.p.m. supplies 22 kW at a terminal voltage of...

    A long-shunt compound generator running at 1000 r.p.m. supplies 22 kW at a terminal voltage of 220 V. The resistance of the armature, shunt field and series field are 0.05 Ω, 110 Ω, and 0.06 Ω respectively. The overall efficiency at the above load is 88 %. Find (i) Cu losses (ii) iron and friction losses and (iii) torque exerted by the prime mover.

  • A 40 KW shunt generator produces terminal voltage of 220 V when running at 1500 rpm. What will be...

    A 40 KW shunt generator produces terminal voltage of 220 V when running at 1500 rpm. What will be its terminal voltage when running at 1800 rpm? Ra-.3 3. Q and Rsh 150 ohms. A 40 KW shunt generator produces terminal voltage of 220 V when running at 1500 rpm. What will be its terminal voltage when running at 1800 rpm? Ra-.3 3. Q and Rsh 150 ohms.

  • 6. Two identical 15 kV generators are to be connected in parallel. Both are running at...

    6. Two identical 15 kV generators are to be connected in parallel. Both are running at rated speed and voltage. There is an open three pole 6-terminal single-throw fused switch between them, connected to the generator terminals (a1, b1.c1) and (a2,b2,c2) on each side, respectively. a1 b1 c1 = a2 b2 c2 Before we close the switch, we check the voltage across phase a with an ac voltmeter and find that Va1 Va2 = 0. With an oscilloscope, we display...

  • Show all working 1. A 4 pole, 220 V, 10 H.P, d.c. shunt motor is rotating...

    Show all working 1. A 4 pole, 220 V, 10 H.P, d.c. shunt motor is rotating at a speed of 320 rpm. Then the developed useful torque is 2. A 4 pole, lap wound d.c. motor drawing an armature current of 20 A has 360 conductors. If the flux per pole is 0.015 Wb then the gross torque developed by the armature of motor is 3. A 220 V, d.c. motor draws an armature current of 20 A. Its armature...

  • Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW...

    Two three-phase generators supply a three-phase load through separate three-phase lines. The load absorbs 30 kW at 0.8 power factor lagging. The line impedance is (1.4 +J1.6) Ω per phase between generator G1 and the load, and (0.8 +jl ) Ω per phase between generator G2 and the load. If generator Gl supplies 15 kW at 0.8 power factor lagging, with a terminal voltage of 460 V line- to-line, determine 1. The voltage at the load terminals. 2. The voltage...

  • Two dc generators (A) and (B) with the following characteristics: Generator (A): rated voltage = 150...

    Two dc generators (A) and (B) with the following characteristics: Generator (A): rated voltage = 150 V, rated current = 30 Amp, and armature resistance = 0.4 Ω. Generator (B): no-load voltage = 160 V, rated current = 20 Amp, and armature resistance = 0.6 Ω. are connected in parallel. Find: a) Circulating no-load current and terminal voltage. b) The load current when generator B floating. c) The maximum possible load power.

  • A) The input current to a 220 V, short-shunt compound motor at no load is 6 A. The shunt- field c...

    a) The input current to a 220 V, short-shunt compound motor at no load is 6 A. The shunt- field circuit resistance is 220 Ω; the armature resistance is 0.112, and the series-field resistance is 0.1 Ω, what is the stray power loss ? (b) Assume the input rating of the motor in Part (a) to be 66 A at 220 V with a no-load speed of 1000 rpm. If the stray power loss varies as the counter-electromotive force and...

  • please answer 13.16 at rated load of unity power factor and rated terminal voltage, determine efficienc...

    please answer 13.16 at rated load of unity power factor and rated terminal voltage, determine efficienc including field rheostat loss. Ans. 93.139 13.11 A generator under test is rated at 100 KVA, 3-phase, 60-Hz; 2,400 volts. (a) If driven b a de motor unexcited, the motor output is 1.26 KW. (b) If driven by a de motor, generato on open circuit and excited to generate rated potential, the motor output is 2.5 KW. ( Ifdriven by a de motor, generator...

  • [29] SECTION B: TRANSFORMERS QUESTION 2 2.1 A 240:48-volt, 50-F power factor of 0.8 lagging. If...

    [29] SECTION B: TRANSFORMERS QUESTION 2 2.1 A 240:48-volt, 50-F power factor of 0.8 lagging. If the no load current and iron loss of this e transformer supplies a load of 10 ampere at a ampere and 12-watt respectively, calculate the total current supplied and the powe oad current and iron loss of this transformer are factor. (7) KVA, 50-Hz, 1200:230-volt single phase transformer has the following series impedance values: Z1 = (0.047 +0.112) Z2 = (0.00172 +0.00411)2 Calculate: 2.2.1...

  • solve no: 3.14 , 3.16, 3.19 please show each step and solve for beginners 120 Power...

    solve no: 3.14 , 3.16, 3.19 please show each step and solve for beginners 120 Power System Analysis 3.12. A single-phase system similar to that shown in Figure 3.11 has two transformers A-B a B-C connected by a line B feeding a load at the receiving end C. The ratings and parame ter values of the components are 500 V/1.5 kV, 9.6 kVA. leakage reactance 5 % 1.2 kV/120 V, 7.2 kVA, leakage reactance 4 % series impedance (0.5 +...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT