What size Intermediate Metal Conduit is required for Four (4) #600 kcmil Type THW Conductors?
A. |
2" |
|
B. |
2 1/2" |
|
C. |
3" |
|
D. |
3 1/2" |
|
E. |
4" |
|
F. |
5" |
|
G. |
6" |
What is the minimum number of duplex outlets required along a 32 foot living room wall?
A. |
2 |
|
B. |
3 |
|
C. |
4 |
|
D. |
5 |
|
E. |
6 |
|
F. |
7 |
|
G. |
8 |
|
H. |
9 |
ANSWER - 1 ==> Area of one #600 kcmil Type THW Conductor = 0.9729 sq. inches
Therefore, Area of 4 #600 kcmil Type THW Conductor = 4*0.9729 sq. inches = 3.8916 sq. inches
For Intermediate Metal Conduit with 4 conductors (3 or more conductors), the filling is 40 %. Using "Dimension and fill Table", we have ==>
3 inch corresponds to 3.169 sq-inch wire area
3-1/2 inch corresponds to 4.234 sq-inch wire area
Our area is 3.8916 sq. inches. So, 3-1/2 inch is appropriate for us.
Therefore, (D) is correct answer.
ANSWER - 2 ==> According to standards, along a wall in a living room, you have to ensure that distance along the wall of any point in the room must not be more than 6 ft. This means a receptacle can cover 12 ft along the wall. Here, wall size is 32 ft.
Therefore, number of receptacles required = nearest greater integer (32 ft / 12 ft) = 3
Therefore, (B) is correct answer.
What size Intermediate Metal Conduit is required for Four (4) #600 kcmil Type THW Conductors? A....
What is the correct size of Rigid Metal Conduit to install Six #250 kcmil copper type THW conductors?
D. trade size 1 1/2 (41). Atrade size 4 (21). B.trade size 1 (27). (53). Ctrade size 1 1/4(35). E. trade size 2 Code reference 29. The general use 125-volt receptacles in a commercial building are supplied by 20- ampere rated multiwire branch-circuits with three ungrounded conductors anda common neutral from a 208/120-volt, 4-wire, 3-phase electrical system. The con ductors for nine circuits are run in a single raceway to an area of the building includ ing nine ungrounded conductors...
10. What is the conductor ampacity required for a 20 KW, 240 volt central space heater? 11. What is the ampacity of three No. 4 THWN conductors installed in an ambient temperature of 30 degree Celsius? 12. What is the ampacity of three No. 3/0 conductors installed in free-air? 13. What is the ampacity of eight 4/O THHN conductors installed a raceway in an ambient temperature of 100 degreee F? 14. What is the ampacity of ten No. 6 THWN...
pleas help me in this do any question you know using National Electrical Code 2011 Applied Electricity NEC worksheet t hree Copper conductors with THHN insulation run in Electrical A branch-circuit Consther conductors. The conductor terminations are rated for a maximum ure in the area of this installation is not expected to exceed 30C size 8 AWG, the maximum ampacity of the conductors If the conductors for this circuit are permitted A 40 amperes. B. 50 amperes. to be used...
1. The color of the outer finish of the insulation or tape marking a grounded conductor must be A. black B. green. C. white or gray D. yellow finish. 2. When the main bonding jumper in a residential el ectrical system is a screw only, the screw must be identified with a A. white B. red C. green D. black The grounding electrode conductor should be installed without a splice, unless the splice is made using exothermic welding or by...
they are true and false questions. 1. A power line is shown on a plot plan using two continuous lines. F 2. A lateral electrical service is run from a pole to a dwelling. F 3. The minimum size service-entrance conductor for a dwelling is #6. F 4. The minimum size branch circuit for a dwelling is 20 A. F 5. EMT must be supported every 10' and within 3' of each outlet box, junction box, cabinet, or fiting. F...
13. Type SE-R Service-Entrance Cable with three insulated conductors and a bare equipment grounding conductor contained within the outer nonmetallic sheath is used as a feeder to provide power from the service panel to a panelboard located in another part of the building as shown in Figure 1.44. The cable run along the flat surface of structural materials is required to be supported at intervals not to exceed: A 6 ft (1.8m). B. 41/2ft(1.4m). C 3 ft (900 mm) D....
dwelling un 4. Type NM-B Cable enters a metal device box and is secured by a cable clamp at the bottom of the box. The cable is installed so the cable jacket extends "1/4 in. (6 mm beyond the cable clamp and free conductors begin at the end of the cable jacket a shown in Figure 1.39. If the device box has a depth of 3.5 in. (90 mm), the minimum permitted length of free conductor in this box is...
6 (4 points): 4 3 2 1 0 Use Kruskal's algorithm to find the minimum spanning tree for the graph G defined by V(G) E(G) a, b, c, d, e ac, ad, ae, be, bd, be Vo(ad) = (a, d) (ae) a, e (be) b,e) using the weight function f : E(G)Rgiven by f(ac)-(ad)-3 f(ae)-2 f(be) =4 f(bd) = 5 f(be) = 3 6 (4 points): 4 3 2 1 0 Use Kruskal's algorithm to find the minimum spanning tree...