500 hp, 600 V, 0.8 pf leading, 6-pole, delta-connected synchronous motor has XS = 1.2 ohm and RA = 0 ohm. Assume motor is lossless.
(a) Calculate EA and IA for 400 hp, 0.85 leading pf load.
(b) What is the torque?
(c) If |EA| is increased by 20% for the 400 hp load, what are the new values of IA and power factor?
500 hp, 600 V, 0.8 pf leading, 6-pole, delta-connected synchronous motor has XS = 1.2 ohm...
2) A 480 V, 60 Hz, 400 hp 0.8 PF-lagging eight-pole A-connected synchronous motor has a synchronous reactance of 0.6 and negligible armature resistance. Ignore the mechanical and core losses. The magnitude of the internal machine voltage is 480 V when the field current is 4 A. Assume magnetic linearity. Initially, the motor operates at the rated conditions. a) Find the speed of this motor. b) Find the armature and field currents. c) What is the developed torque? What is...
Problem 3) [15 marks] A 200-V, 100-hp, 0.6 PF leading, Y-connected, 50 Hz synchronous motor has a synchronous reactance of2.0 Ω and negligible resistance. Its mechanical losses and core losses are 1 .0 Kw and 0.5 KW, respectively. The shaft is supplying a 20-hp load at 0.6 PF leading. a) Sketch the phasor diagram of the machine and find the values of IA, I, and EA. b) The load is now increased to 40 hp. Repeat part (a) and find...
Q3- A synchronous motor's parameters are 220-volt,50 hp, 4-pole, 60Hz, 0.8 pf lagging. The synchronous reactance is 2.4ohm.The armature resistance is negligible. The motor is Y-connected.The motor's friction & windage losses are 1400W and its core loss is 1000W.The motor is supplying power to a 25hp load connected to the shaft, at an initial pf of 0.80 lagging. Calculate: (a)the input power and the efficiency (b)the line and phase currents (c)the internal voltage Ea There has been a change in...
A 3-phase, 600 kVA, 600 V, 60 Hz, 16 pole, Y-connected, round rotor synchronous motor has Xs = 0.492 22 and a negligible armature resistance. The motor is supplied from a 589V infinity bus, and draws 520 kW of real power at a 0.9 leading power factor. Its mechanical loss at the synchronous speed is 20 kW and the core loss is 15 kW. a) [7 marks] Calculate the generated voltage Ef , the load angel 8, and the efficiency...
(Question 1): (4pts) A three-phase, 2300-V, 60-Hz, 10-pole, A-connected cylindrical rotor synchronous motor has a synchronous reactance of 4.0 82/phase. The armature resistance may be neglected. It is connected to 2300-V source and drives a system with its excitation set to give a PF of 0.9-leading when the power is 500-kW. (a) Sketch the phasor diagram of this motor. (b) Calculate the armature current. (c) Calculate the excitation voltage and torque angle. (d) If the load torque is increased by...
A 480-V, 60-Hz, A-connected, four-pole synchronous generator has a synchronous reactance of 0.1 ohm and an armature resistance of 0.0 15 ohm. At full load, the machine supplies 1200 A at 0.8 PF lagging. Under full-load conditions, the friction and windage losses are 40 kW, and the core losses are 30 kW. Ignore any field circuit losses c) How much power is the generator now supplying? How much power is supplied to the generator by the prime mover? What is...
E1Q2
1 0 7 1. A 20 MVA, 6.9 KV 3-phase 4-pole star connected synchronous motor is operating with field current of 20 Amps, at full load and 0.9 power factor leading. The motor has a synchronous reactance of 1.5 ohm and negligible armature resistance. 30 points a. Find the motor full load torque and power angle. b. If the field current is increased by 15% and the load torque is increased by 15% find the motor current and power...
Problem 3 (25p) A 120-V, 60-Hz, three-phase, Y-connected, 6 poles, wound-rotor, synchronous motor has a synchronous reactance of 3 ohms. The motor takes a current of 10 A at 0.8 pf leading when operating at a certain field current. The load is gradually increased until the motor develops its maximum torque while the field current is held constant. Determine: a) The new line current b) The power factor c) Torque developed by the motor
A 230 V synchronous motor (line to line), 60 Hz, 4 poles, connected in Y has a synchronous reactance of Xs = 1.8 Ω and a negligible armature resistance. The field current flowing under these conditions is IA = 3 A. This motor is capable of absorbing a current IA = 60 A for a unit power factor (PF = 1). The linear open circuit characteristics are assumed. (1) Is the field current in the rotor winding direct or alternating...
Q3) A 400-V, 3-phase, 50-HZ, 4-pole Y-connected synchronous machine is operated as a motor and draws 27A at 0.77 PF leading. The motor armature resistance is 0.50/Phase and synchronous reactance is j12Ω /phase. The rotational loss is 200 watts. The field winding has a resistance of 0.4Ω and is supplied by 50V DC sources. Determine the following: a) Real and reactive power drawn by the motor b) The power developed c) The torque angle d) The shaft torque e) Efficiency...