Question

Determine the magnitude of the line current that flows to a load that consumes 3MW at...

Determine the magnitude of the line current that flows to a load that consumes 3MW at a power factor of 0.8 overdue and that operates at 13.2 kV voltage

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Here the type of the system is not given either single phase or 3-phase. Usually 13.2kv exists in 3-phase supply.

1) Assuming it as 3-phase supply :-

Given :-

Power = 3MW

Power factor = 0.8 ( since, magnitude of current is asked, there is no need of lag/ lead. Answer is same for both )

Line Voltage = 13.2kv

We know that P= √3 * V​​​​​​​​​​​​​​L*I​​​L*PF

From that , I​​​​​​L = P/( √3 * V​​​​​​L *PF)

I​​​​​​L = 3M/(√3 * 13.2k * 0.8 )

I​​​​​​L = 164.02 A.

B) Assuming it as a single phase supply:-

Power = V*I*PF

Current I = P/( V*PF)

I = 3M/( 13.2k * 0.8 )

I = 284.09 A

Usually 13.2kv supply is a exists in India as three-phase supply.

Add a comment
Know the answer?
Add Answer to:
Determine the magnitude of the line current that flows to a load that consumes 3MW at...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A three-phase blanced load connected in Y consumes 3kW(total of the 3 phases) at a power...

    A three-phase blanced load connected in Y consumes 3kW(total of the 3 phases) at a power factor of 0.8(-). A balanced Y load of capacitors will be added in parallel so that the power factor of the combination improves to 0.85(-). If the frecuency is 60 Hz and the line-to-line voltages a a balanced set of 200 Vrms, get: a) The magnitude of the line current IaA that the line consumes before placing the capacitors. b) The value of the...

  • A 3-phase 60 Hz 50 km transmission line delivers 20 MW of power to a load...

    A 3-phase 60 Hz 50 km transmission line delivers 20 MW of power to a load at 69 kV and a power factor of 0.8 lagging. The line has the following parameters r = 0.1112/km L = 1.11 mH/km C = negligible Determine: The line impedance. (4 Marks) The "receiving end" phase voltage and current (7 Marks) The "sending end" voltage and current (10 Marks) The voltage regulation. (4 Marks)

  • A three-phase feeder has line voltage of 13.8 kV and supplies load of 7000 kVA at...

    A three-phase feeder has line voltage of 13.8 kV and supplies load of 7000 kVA at power factor of 0.8 lagging. Find: The feeder current in A, real power in kW and Reactive power in kVAr. The capacitor size in kVAr to improve the power factor to 0.98. The feeder power in kW and kVA and current in A, after installing the capacitor bank.

  • The infinite bus in the Figure operates at 480 V. Load 1 consumes 100 kW at...

    The infinite bus in the Figure operates at 480 V. Load 1 consumes 100 kW at 0.9 Pflagging and load 2 consumes 80 KVA O Plagne load is synchronous motor whose real power consumption is 74.6 kW at 0.8 PF leading (a) If the switch was initially open what is the equivalent power factor of the system (b) When the switch is finally closed, what is the new equivalent power factor of the system Bus 1 Load 1 100 KW...

  • Consider a Delta generator supplying Wye load. The generator has the following data: Line to line...

    Consider a Delta generator supplying Wye load. The generator has the following data: Line to line voltage of 11kV Rated power of 55 MVA Power factor capability of 0.7 lagging The load the following rated data Line to line voltage of 11kV Rated power of 40 MVA Lagging power factor of 0.8 For the above system: Design the Current Transformer system using the load data

  • Problem 4: A plant consumes 20 kW of power. If the load power factor is 0.9...

    Problem 4: A plant consumes 20 kW of power. If the load power factor is 0.9 lagging, what is the angle by which the load current lags the load voltage? What is the load current, I, if the load voltage is 240/10° VrMS? Answers: 25.84,-92.59/-15.849 ARMS

  • UISIZULU Problem 4 A three phase, 5 kW, wye-connected load operate onnected load operates at 0.8...

    UISIZULU Problem 4 A three phase, 5 kW, wye-connected load operate onnected load operates at 0.8 power factor lagging with a terminal voltage of 100 V (line to line). The cables connecting e bles connecting each phase of the load to the wye-connected supply has an impedance of (0.25 +0.25) 12. Compute the following: a) Reactive power drawn by the load. b) Real and reactive power losses in the system. me current and line voltage at the source terminals and...

  • kV/phase, 60 Hz, lossless short transmission line has a short-circuit power of 500 MVA/phase. Consider 7. A a unity power factor load connected at the receiving end. Assume that the sending end volta...

    kV/phase, 60 Hz, lossless short transmission line has a short-circuit power of 500 MVA/phase. Consider 7. A a unity power factor load connected at the receiving end. Assume that the sending end voltage is equal to the nominal voltage. a. Determine the maximum active power this line can transmit (5 points) b. Determine the reactance of the line (5 points) c. Using basic equations of circuit analysis, show that the magnitude of the receiving end voltage (VR) is approximately 71%...

  • 3. (40 points) Three-phase loads are connected in parallel across a 24 KV (line-line three-phase power...

    3. (40 points) Three-phase loads are connected in parallel across a 24 KV (line-line three-phase power supply. Load 1: 120 KVA at 0.8 power factor leading; Load 2: 180 KW at 0.6 power factor lagging, Load 3: 40 KW at unity power factor Find the total complex power of three loads; (ii) Draw the power triangle of the combined load (ii) Find the overall power factor (iv) Find the line current (magnitude only) in the power supply line.

  • A 50 kW load operates from a 60 Hz and 10kV line with a power factor...

    A 50 kW load operates from a 60 Hz and 10kV line with a power factor of 0.6 lagging. Compute the capacitance that must be placed in parallel with the load to achieve 0.9 lagging power factor. In-Class #10 Problem A 50 kW load operates from a 60 Hz and 10 kV line with a power factor of 0.6 lagging. Compute the capacitance that must be placed in parallel with the load to achieve 0.9 lagging power factor.

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT