Explain the load balance of UPS in a given data center power design (how loaded each of UPS is as compared to its rated capacity.
When sizing UPS it is important to know the phase configuration required by both the mains supply and the loads, in addition to the overall load size. Electrical experts will often state both load size and phase configuration. An example would include ‘120KVA three phase’. This refers to a 120KVA load run from a three phase 415Vac, 50Hz supply. In terms of load sizing, this means that each phase (of the 3 phase electrical supply) will deliver upto 40KVA (or 174Amps at 230Vac). If the statement was 120KVA per phase then we would be looking at 3×120KVA per phase = 360KVA UPS load. The need for a 120KVA three phase UPS could be met with three single phase output 40KVA UPS provided the connected loads are single phase loads. These would be 3/1 configured and installed one per phase. However, the overall capital, installation and energy efficiency costs just rose by a factor of 3 compared to a single 120KVA UPS system installation. 3/1 UPS upto 60KVA are also used in office environment where the loads are single phase and this removes the need to balance the load connections in each of the three phases. Larger 3/1 UPS even upto 200KVA are typically required for DCS and SCADA loads in heavy industries like Power Plant, Steel Plant etc.
UPS Sizing steady state load conditions
Steady state loading conditions
As like any other power source, UPS is a limited power supply and the capacity of the UPS is defined in KVA(apparent Power) and KW (real power).
To arrive at the capacity of UPS and the configuration of UPS, the following steps needs to be followed
• Step 1
Need of Load
• Step 2
Configuration of UPS
• Step 3
Check on the KVA & KW demand supplied by the UPS
Step 1: Need of Load
The load demand of the loads expected to be connected to the UPS.
(Note: The load power factor has to be measured at the site or can be assumed based on the past experience)
Step 2: Configuration of UPS
The criticality, of the loads will determine the necessary availability of the UPS. Based on the criticality the UPS capacity or configuration can be selected.
Where N is the number of UPS, required to support the Load. For critical load with 66% redundancy N>2, where a minimum of 2 UPS is required to support the load and 1 UPS for redundancy
Step 3: Selecting the required UPS capacity
Based on the total demand and the configuration of UPS, the capacity of UPS is selected. The total load in KVA and KW derived in step 1 will have to divided by N as selected in step 2 to arrive the UPS capacity.
When sizing UPS it is important to know the phase configuration required by both the mains supply and the loads, in addition to the overall load size. Electrical experts will often state both load size and phase configuration. An example would include ‘120KVA three phase’. This refers to a 120KVA load run from a three phase 415Vac, 50Hz supply. In terms of load sizing, this means that each phase (of the 3 phase electrical supply) will deliver upto 40KVA (or 174Amps at 230Vac). If the statement was 120KVA per phase then we would be looking at 3×120KVA per phase = 360KVA UPS load. The need for a 120KVA three phase UPS could be met with three single phase output 40KVA UPS provided the connected loads are single phase loads. These would be 3/1 configured and installed one per phase. However, the overall capital, installation and energy efficiency costs just rose by a factor of 3 compared to a single 120KVA UPS system installation. 3/1 UPS upto 60KVA are also used in office environment where the loads are single phase and this removes the need to balance the load connections in each of the three phases. Larger 3/1 UPS even upto 200KVA are typically required for DCS and SCADA loads in heavy industries like Power Plant, Steel Plant etc.
UPS Sizing steady state load conditions
Steady state loading conditions
As like any other power source, UPS is a limited power supply and the capacity of the UPS is defined in KVA(apparent Power) and KW (real power).
To arrive at the capacity of UPS and the configuration of UPS, the following steps needs to be followed
• Step 1
Need of Load
• Step 2
Configuration of UPS
• Step 3
Check on the KVA & KW demand supplied by the UPS
Step 1: Need of Load
The load demand of the loads expected to be connected to the UPS.
(Note: The load power factor has to be measured at the site or can be assumed based on the past experience)
Step 2: Configuration of UPS
The criticality, of the loads will determine the necessary availability of the UPS. Based on the criticality the UPS capacity or configuration can be selected.
Where N is the number of UPS, required to support the Load. For critical load with 66% redundancy N>2, where a minimum of 2 UPS is required to support the load and 1 UPS for redundancy
Step 3: Selecting the required UPS capacity
Based on the total demand and the configuration of UPS, the capacity of UPS is selected. The total load in KVA and KW derived in step 1 will have to divided by N as selected in step 2 to arrive the UPS capacity.
When sizing UPS it is important to know the phase configuration required by both the mains supply and the loads, in addition to the overall load size. Electrical experts will often state both load size and phase configuration. An example would include ‘120KVA three phase’. This refers to a 120KVA load run from a three phase 415Vac, 50Hz supply. In terms of load sizing, this means that each phase (of the 3 phase electrical supply) will deliver upto 40KVA (or 174Amps at 230Vac). If the statement was 120KVA per phase then we would be looking at 3×120KVA per phase = 360KVA UPS load. The need for a 120KVA three phase UPS could be met with three single phase output 40KVA UPS provided the connected loads are single phase loads. These would be 3/1 configured and installed one per phase. However, the overall capital, installation and energy efficiency costs just rose by a factor of 3 compared to a single 120KVA UPS system installation. 3/1 UPS upto 60KVA are also used in office environment where the loads are single phase and this removes the need to balance the load connections in each of the three phases. Larger 3/1 UPS even upto 200KVA are typically required for DCS and SCADA loads in heavy industries like Power Plant, Steel Plant etc.
UPS Sizing steady state load conditions
Steady state loading conditions
As like any other power source, UPS is a limited power supply and the capacity of the UPS is defined in KVA(apparent Power) and KW (real power).
To arrive at the capacity of UPS and the configuration of UPS, the following steps needs to be followed
• Step 1
Need of Load
• Step 2
Configuration of UPS
• Step 3
Check on the KVA & KW demand supplied by the UPS
Step 1: Need of Load
The load demand of the loads expected to be connected to the UPS.
(Note: The load power factor has to be measured at the site or can be assumed based on the past experience)
Step 2: Configuration of UPS
The criticality, of the loads will determine the necessary availability of the UPS. Based on the criticality the UPS capacity or configuration can be selected.
Where N is the number of UPS, required to support the Load. For critical load with 66% redundancy N>2, where a minimum of 2 UPS is required to support the load and 1 UPS for redundancy
Step 3: Selecting the required UPS capacity
Based on the total demand and the configuration of UPS, the capacity of UPS is selected. The total load in KVA and KW derived in step 1 will have to divided by N as selected in step 2 to arrive the UPS capacity.
When sizing UPS it is important to know the phase configuration required by both the mains supply and the loads, in addition to the overall load size. Electrical experts will often state both load size and phase configuration. An example would include ‘120KVA three phase’. This refers to a 120KVA load run from a three phase 415Vac, 50Hz supply. In terms of load sizing, this means that each phase (of the 3 phase electrical supply) will deliver upto 40KVA (or 174Amps at 230Vac). If the statement was 120KVA per phase then we would be looking at 3×120KVA per phase = 360KVA UPS load. The need for a 120KVA three phase UPS could be met with three single phase output 40KVA UPS provided the connected loads are single phase loads. These would be 3/1 configured and installed one per phase. However, the overall capital, installation and energy efficiency costs just rose by a factor of 3 compared to a single 120KVA UPS system installation. 3/1 UPS upto 60KVA are also used in office environment where the loads are single phase and this removes the need to balance the load connections in each of the three phases. Larger 3/1 UPS even upto 200KVA are typically required for DCS and SCADA loads in heavy industries like Power Plant, Steel Plant etc.
UPS Sizing steady state load conditions
Steady state loading conditions
As like any other power source, UPS is a limited power supply and the capacity of the UPS is defined in KVA(apparent Power) and KW (real power).
To arrive at the capacity of UPS and the configuration of UPS, the following steps needs to be followed
• Step 1
Need of Load
• Step 2
Configuration of UPS
• Step 3
Check on the KVA & KW demand supplied by the UPS
Step 1: Need of Load
The load demand of the loads expected to be connected to the UPS.
(Note: The load power factor has to be measured at the site or can be assumed based on the past experience)
Step 2: Configuration of UPS
The criticality, of the loads will determine the necessary availability of the UPS. Based on the criticality the UPS capacity or configuration can be selected.
Where N is the number of UPS, required to support the Load. For critical load with 66% redundancy N>2, where a minimum of 2 UPS is required to support the load and 1 UPS for redundancy
Step 3: Selecting the required UPS capacity
Based on the total demand and the configuration of UPS, the capacity of UPS is selected. The total load in KVA and KW derived in step 1 will have to divided by N as selected in step 2 to arrive the UPS capacity.
When sizing UPS it is important to know the phase configuration required by both the mains supply and the loads, in addition to the overall load size. Electrical experts will often state both load size and phase configuration. An example would include ‘120KVA three phase’. This refers to a 120KVA load run from a three phase 415Vac, 50Hz supply. In terms of load sizing, this means that each phase (of the 3 phase electrical supply) will deliver upto 40KVA (or 174Amps at 230Vac). If the statement was 120KVA per phase then we would be looking at 3×120KVA per phase = 360KVA UPS load. The need for a 120KVA three phase UPS could be met with three single phase output 40KVA UPS provided the connected loads are single phase loads. These would be 3/1 configured and installed one per phase. However, the overall capital, installation and energy efficiency costs just rose by a factor of 3 compared to a single 120KVA UPS system installation. 3/1 UPS upto 60KVA are also used in office environment where the loads are single phase and this removes the need to balance the load connections in each of the three phases. Larger 3/1 UPS even upto 200KVA are typically required for DCS and SCADA loads in heavy industries like Power Plant, Steel Plant etc.
UPS Sizing steady state load conditions
Steady state loading conditions
As like any other power source, UPS is a limited power supply and the capacity of the UPS is defined in KVA(apparent Power) and KW (real power).
To arrive at the capacity of UPS and the configuration of UPS, the following steps needs to be followed
• Step 1
Need of Load
• Step 2
Configuration of UPS
• Step 3
Check on the KVA & KW demand supplied by the UPS
Step 1: Need of Load
The load demand of the loads expected to be connected to the UPS.
(Note: The load power factor has to be measured at the site or can be assumed based on the past experience)
Step 2: Configuration of UPS
The criticality, of the loads will determine the necessary availability of the UPS. Based on the criticality the UPS capacity or configuration can be selected.
Where N is the number of UPS, required to support the Load. For critical load with 66% redundancy N>2, where a minimum of 2 UPS is required to support the load and 1 UPS for redundancy
Step 3: Selecting the required UPS capacity
Based on the total demand and the configuration of UPS, the capacity of UPS is selected. The total load in KVA and KW derived in step 1 will have to divided by N as selected in step 2 to arrive the UPS capacity.
Explain the load balance of UPS in a given data center power design (how loaded each...
For specific data center power design .please explain in-depth the impact of the power factor of AC units to the power design by changing (decreasing) its value.
Question 11 For the given bolt connection, if it is subjected to the design load in tension of 120 kips, the design bearing capacity of the steel plate is 140 kips, the design capacity of the plate pure tension failure 150 kips, the design capacity of bolt shear failure is 170 kips, and the design capacity of the plate bearing failure is 160 kips, can the bolt connection resist the given load without failure? If the connection eventually failures under...
can you please explain how to calculate the axial load for each gear and supporting load for each bearing? thank you! Task 1: A shaft is to be designed to support the spur pinion and helical gear shown in the figure below on two bearings spaced 700 mm center-to-center. Bearing A is a cylindrical roller bearing and has to take only radial load; bearing B has to take the thrust load produced by the helical gear and its share of...
It is better if both can be solved. Design a power generation system by choosing one of the options given below. 1. Geothermal sourced power plant Define the geothermal power plant type (Total Flow/Flash/binary) Define turbine isentropic efficiency Show all the processes on a T-s diagram Calculate how much power can be generated . 2. Wind Power system Assume Rayleigh wind regime Define wind turbine power capacity Define rated power of the turbine Define cut-in, cut out and rated wind...
The figure below shows a concentrically loaded 305BT62.5 compression member. Assumptions and Given Values . Grade 300 Steel » tf- 280 MRa fow- 300 MPa . Consider the effective length for buckling about each axis as 2.2 m Required Determine the maximum design load (N") 305BT 62.5 d - 305 mm by- 229 mm = 19.6 mm =11.9 mm r14 mm A 7970 mm2 r, 92.6 mm 49.7 mm Figure: Concentrically loaded compression member Tips: 1. To find out the...
2 1. (Source: Potter) A coal-fired power plant is served by 25 trucks. When loaded, each truck consists of one single-axle of 14 kips (the front axle), two tandem axles of 32 kips each (the middle axles) and one single axle of 22 kips (back axle). Each truck makes 25 daily trips. The weights on the same axles when the truck is empty and leaving the power plant are 10 kips, 12 kips, and 8 kips, respectively. A twolane road...
please answer 13.16 at rated load of unity power factor and rated terminal voltage, determine efficienc including field rheostat loss. Ans. 93.139 13.11 A generator under test is rated at 100 KVA, 3-phase, 60-Hz; 2,400 volts. (a) If driven b a de motor unexcited, the motor output is 1.26 KW. (b) If driven by a de motor, generato on open circuit and excited to generate rated potential, the motor output is 2.5 KW. ( Ifdriven by a de motor, generator...
(b) The daily design load curve of a residential area is given in the table below. The hydropower facility providing the power has an effective head of 15 m and a plant efficiency of 0.85. What is the minimum daily flow (m3/s) that could meet the demand? What is the minimum required storage capacity (within-day storage) to meet the peak load? If the daily flowrate were 320m3/s, what would be the minimum required storage capacity? Would there be some water...
Load Duration Curve A gas-fired boiler system is being design for a new building. The system will consist of 3 identical boilers, each with rated output = 200 kW. The anticipated LDC is shown below. 600 500 Heating Load 400 [kW] 300 200 100 0 The planned operating sequence is as follows: Boiler-1 fires first to meet whatever load it can, up to its capacity. When Boiler-1 reaches its capacity, Boiler-2 fires second and operates to meet whatever load it...
(b) Explain the function, objective and constraints for each case study. (i) A design of cylindrical tie-rod of specified length 1, to carry a tensile force F without failure, it is to be of minimum mass. Think of golf-club shafts. Consider, then a light beam of square section b x b and length 1 loaded in bending which must meet a constraint on its stiffness S, meaning that it must not deflect more than under a load F. (iii) We...