A 400 v, 50 Hz, three phase alternator, rated at 75 kVA, is star connected and...

A 400 v, 50 Hz, three phase alternator, rated at 75 kVA, is star connected and driven at 1000 r/min. The windings of the alternator have a resistance, per phase, of 0.03 Ω and synchronous reactance, at 50 Hz per phase, of j0.325 Ω. The stator of the alternator has 108 slots, with 8 conductors, per slots, in a double layer. The maximum pole flux is 8.772 x 10-3 Wb. To improve the wave form only 80% of the pole pitch is wound.
a. Determine the smallest lagging power factor at which the alternator can deliver its rated load [0.823]
b. According to available information about the alternator described above it may be driven 1200 r/min. When operated at 1200 r/min the rated voltage is 480 V and the maximum phase current is to be kept to the same value as the rated phase current when it is driven at 1000 r/min.

Determine for the alternator, when driven at 1200 r/min, the

(i) Rated output and,[305.95 Volts]
(ii) Smallest lagging power factor at which the alternator can deliver its rated load [0.815]
0 0
Add a comment Improve this question Transcribed image text
Request Professional Answer

Request Answer!

We need at least 10 more requests to produce the answer.

0 / 10 have requested this problem solution

The more requests, the faster the answer.

Request! (Login Required)


All students who have requested the answer will be notified once they are available.
Know the answer?
Add Answer to:
A 400 v, 50 Hz, three phase alternator, rated at 75 kVA, is star connected and...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Similar Homework Help Questions
  • 1- A 25-kVA, 3-phase, wye-connected, 400-V alternator has a synchronous reactance of 1.6 ohms per phase....

    1- A 25-kVA, 3-phase, wye-connected, 400-V alternator has a synchronous reactance of 1.6 ohms per phase. The alternator is to have zero voltage regulation at half-load. Neglecting the armature resistance, find the operating power factor and the developed power 2. A 500-kVA, 3600-V, 3-phase, 60-Hz alternator has an effective armature resistance per phase of 0.40 ohm Mechanical and iron losses is 10 kW, field current at full load unity power factor is 70 A. The exciter voltage is constant at...

  • Determine the number of stator conductors per slot for a three-phase 50 Hz alternator if the...

    Determine the number of stator conductors per slot for a three-phase 50 Hz alternator if the winding is star connected and generates a line voltage of 44kV at 1 500 r/min during open circuit. Take the flux per pole as 0,3 Wb and the distribution factor as 0,96. The coils are full pitched and the stator has 4 slot per pole per phase. Show all work, show all diagram and choose the answer form bellow. Group of answer choices 50...

  • A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.5Q/phase and a...

    A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.5Q/phase and a synchronous reactance of 5Q/phase. The generator is supplying its rated power at its rated voltage and at a power factor lagging. The rotational loss is 2 kW. Calculate: (a) the power developed, (b) the power angle, (c) the voltage regulation, and (d) the shaft torque. A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.50/phase and a synchronous...

  • A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting thre...

    A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting three single phase transformers in the Dynll vector group as shown in Fig.P1. The per phase equivalent circuit parameters on the high voltage side are: R1-0.72 Ω, Xi,-0.92 Ω, R2-0.70 Ω, Xp-0.90 Ω, R.-308.49 Ω, and X,,-44.61 Ω (a) Sketch the corresponding phasor diagram of the primary and secondary voltages for the Dynll vector group; lagging; terminal voltage is 415 V line to line, and...

  • A 3-phase, 60 Hz, 6 pole alternator has an air gap flux that is sinusoidally distributed....

    A 3-phase, 60 Hz, 6 pole alternator has an air gap flux that is sinusoidally distributed. The stator has 5 slots per pole per phase and each slot contains 4 conductors arranged in two layers. The coil pitch is 12 slots. With normal excitation and rated speed, the voltage induced per conductor is 25 volts. What is the open-circuit emf between the terminals when this machine is wye-connected and all the conductors per phase are connected in series?

  • A 3-phase, 60 Hz, 6 pole alternator has an air gap flux that is sinusoidally distributed....

    A 3-phase, 60 Hz, 6 pole alternator has an air gap flux that is sinusoidally distributed. The stator has 5 slots per pole per phase and each slot contains 4 conductors arranged in two layers. The coil pitch is 12 slots. With normal excitation and rated speed, the voltage induced per conductor is 25 volts. What is the open-circuit emf between the terminals when this machine is wye-connected and all the conductors per phase are connected in series?

  • 1. A six pole, 240V, 50 Hz three phase squirrel-cage induction motor has a no-load speed...

    1. A six pole, 240V, 50 Hz three phase squirrel-cage induction motor has a no-load speed of 103 rad/s and a speed regulation of 5% at rated load. Find the amount of slip (in rpm) at full load for this motor. 2.. A 2 HP, 240 VAC, 60 Hz, capacitor-start motor is 75% efficient and draws 10 A at full load. What is this motor's power factor at rated load? 3. A wound rotor, 3 phase induction motor in Mr....

  • QUESTION 6 (MULTI-PHASE SYSTEMS) A 400 v, 50 Hz, three-phase distribution system supplies a 20 kVA, three-phase induction motor load at a power factor of 0 8 lagging, and a star-connected set of...

    QUESTION 6 (MULTI-PHASE SYSTEMS) A 400 v, 50 Hz, three-phase distribution system supplies a 20 kVA, three-phase induction motor load at a power factor of 0 8 lagging, and a star-connected set of impedances, each having a resistance of 10 Ω and an inductive reactance of 8 Ω Calculate the capacitance of delta-connected capacitors required to improve the overalil power factor to 0 95 lagging [14] TOTAL 1001 QUESTION 6 (MULTI-PHASE SYSTEMS) A 400 v, 50 Hz, three-phase distribution system...

  • A two-pole, 75kW, 440 V, 50 Hz, Y-connected, three-phase squirrel cage induction motor has the fo...

    Please solve this question. Thank you. A two-pole, 75kW, 440 V, 50 Hz, Y-connected, three-phase squirrel cage induction motor has the following parameters, in Ω/phase referred to the stator: R1-0.075, XI 0.17, xm-72, R2-0.065 and X-0.17. Its rated slip is 4%. Assume that the mechanical losses are 1 kW and the core losses are 1.1 kW. Compute: a. The rated input current b. The rated power factor. c. The pullout torque d. The induced and load torques at rated conditions....

  • 1. A three-phase, 5 kVA, 208 V, four-pole, 60 Hz, wye-connected synchronous machine has...

    A three-phase, 5 kVA, 208 V, four-pole, 60 Hz, wye-connected synchronous machine has negligible stator winding resistance and a synchronous reactance of 8 Wper phase. It is operated in parallel with a three-phase, 208 V, 60 Hz power supply.Determine the excitation voltage and the power angle when the machine is delivering rated kVA at 0.8 pf lagging. Draw the phasor diagram

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT