Question

Determine the limit power for static stability in a system where a generator with a reactance...

Determine the limit power for static stability in a system where a generator with a reactance of j0.5 p.u. is connected to an impedance of j1.0 p.u. through a rigid network. The generator pole voltage is maintained at 1.2 p.u. ∠? and the rigid network voltage is 1.0 p.u. ∠ 0 °.

a. Draw a substitution

b. Solve for angle ? (for static stability boundary power).

c. Solve the generator source voltage

d. Solve the Limit Power for Static Stability

0 0
Add a comment Improve this question Transcribed image text
Answer #1

b. Angle ? (for static stability boundary power) is 73.87 degree

c. generator source voltage = 1.728 pu angle 90 degree

d. Limit Power for Static Stability is 1.152 pu

Add a comment
Know the answer?
Add Answer to:
Determine the limit power for static stability in a system where a generator with a reactance...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A 3-phase, 100 MVA, 11 kV, 60 Hz, 200 rpm synchronous generator has synchronous reactance of...

    A 3-phase, 100 MVA, 11 kV, 60 Hz, 200 rpm synchronous generator has synchronous reactance of 12 2 and negligible stator resistance. a. The generator is connected to an infinite bus and delivers 80 MW at 0.8 leading power factor. Determine the power angle and excitation voltage EA. Draw the phasor diagram. b. The field current of the generator is now slowly reduced until the generator reaches its static stability limit (5=0). For this condition, determine the power angle, excitation...

  • transient system stability is the subject (Q2) Suppose you are working as a testing engineer at...

    transient system stability is the subject (Q2) Suppose you are working as a testing engineer at AI Rusail Power Plant, Oman. You are going to test the newly erected 4 pole synchronous gererator having H = 6000KJ/MVA which is going to be connected with a synchronous motor having H = 4000 KJ/MVA through a network of reactances. Assume the generator is delivering power of 1.0 p.u. to the motor when a fault occurs which reduces the delivered power. What would...

  • Question 2 A 60 Hz synchronous generator with Xd 0.2 pu transient reactance is connected to...

    Question 2 A 60 Hz synchronous generator with Xd 0.2 pu transient reactance is connected to an infinite us through a transformer and the transmisiones as shown in the Figure. All system reactances are marked on the diagram and are expressed on a common MVA base. The generator dies a power of Auto busbar 1. The magnitude of the generator's excitation voltage e'is 12 pu, and the infinite bus voltage is -1.00u. If a 3-phase fault occurs at the middle...

  • A three-phase, delta-connected, two-pole, synchronous generator is connected to a 60 Hz, 13.5 kV (line-to-line), system....

    A three-phase, delta-connected, two-pole, synchronous generator is connected to a 60 Hz, 13.5 kV (line-to-line), system. The generator is delivering its rated output power, under which conditions pfload = 0.8 lagging and |SI = 20 MVA. The generator per-phase model parameters at rated load are. RA = 0.5 2 Xss = 522 9. What is the generator's line-to-line voltage regulation? Is the voltage regulation positive or negative? 10. If the field current is held at the rated load value, but...

  • A remote generator transmits energy to a major load/generation via a system shown in the drawing....

    A remote generator transmits energy to a major load/generation via a system shown in the drawing. Assume the generators voltage behind transient reactance to be 1.1pu, the infinite bus voltage to be 1.0 pu and the power transfer to be 0.3 pu during the steady state condition of the network. The line reactance is j0. 5 pu per line and the transient reactance of the generator isj0. 2 pu. The normalised constant of the generator H- 3KWS7KVA A 3 phase...

  • #1(i) For the one line 3-phse power system shown in Fig.1, show that the real power,...

    #1(i) For the one line 3-phse power system shown in Fig.1, show that the real power, P in per unit, delivered to bus-2 by the generator, is P = (I Egl IVrl sin δ)/(Xg + Xr), where Eg, is the generated voltage of the alternator in per unit and Xg its synchronous reactance in per unit, V, is the bus-2 voltage at the receiving end of the transmission line with reactance x, all in per unit, and δ is the...

  • A 10MVA 13.8-kV 60-Hz four-pole Y-connected synchronous generator is delivering rated power at unity power factor....

    A 10MVA 13.8-kV 60-Hz four-pole Y-connected synchronous generator is delivering rated power at unity power factor. a) Draw the equivalent circuit for the analysis of this problem b) Find the synchronous reactance given that the field excitation voltage is 6.89kV (per phase) and leads the terminal voltage by an angle π/4. c) In a special occasion, the generator is operated as a motor (the synchronous reactance is the one derived in (a)). At rated terminal voltage, what is the minimum...

  • 3. A 722-MVA, 19-kV steam turbine generator has a per-phase synchronous reactance of 1.3 PU, and...

    3. A 722-MVA, 19-kV steam turbine generator has a per-phase synchronous reactance of 1.3 PU, and its internal (excitation) voltage is adjusted to 1.2 PU. The generator is connected to a 19 kV (line) infinite-bus. If the voltage angle (d) between the infinite-bus and the generator internal voltage is 20°, calculate, The generator active power output. The generator line current. Draw the phasor diagram for one phase.

  • A 450 MVA, 26-kV generator is connected to a 345-kV power system through a 500MVA, 26-kV:345-kV t...

    A 450 MVA, 26-kV generator is connected to a 345-kV power system through a 500MVA, 26-kV:345-kV transformer which can be represented by a series reactance of 95 m Ω when referred to its low-voltage terminals. The generator has a saturated synchronous reactance of 1.73 per unit and a rated-open- circuit-voltage field current of 2140 A. Under normal operating procedures, the generator is operated under automatic voltage regulation set to maintain its terminal voltage at 26 kV. In this problem you...

  • Q2 (a) A star connected 6.6kV, 8MVA synchronous generator operating at 7MW and a 0.88 lagging power factor is connected to the Grid. The synchronous reactance is 1.5Ω (i) Calculate the phase current,...

    Q2 (a) A star connected 6.6kV, 8MVA synchronous generator operating at 7MW and a 0.88 lagging power factor is connected to the Grid. The synchronous reactance is 1.5Ω (i) Calculate the phase current, excitation voltage and load angle. [10] (ii) What is the maximum theoretical power at this excitation? Draw a phasor diagram (to scale) and from this estimate the phase current and power factor when operating at this point. 151 Q2 (a) A star connected 6.6kV, 8MVA synchronous generator...