Given:
VP-L-L=VP-L-N =13.2KV
Rated Individual Windings Voltage
H = 7.2KV
X = 0.48KV
M = 1.4KV
Assumption:
Let us assume that the Voltage rating of the H windings are given as V L-N
Proof:
a.
The turn ratio for Primary and H winding is VP-L-N / V S- L-N = 13.2/7.2 = 1.833, Here the phase difference is 30o because of different windings
Now for the Primary and X windings, the turns ration is VP-L-N / V S- L-N = 13.2 / 0.48 = 27.5, Here the Phase shift is 0o between primary and secondary because of similar windings.
EE 488 HW 15 For the three-phase transformers shown, the individual windings are rated: primary "...
1. Three single-phase step-up transformers rated at 75 MVA, 13.2 kV/80 kV are connected in delta- wye on a 13.2 kV transmission line. If they feed a 180 MVA load, calculate the following: a. The secondary line voltage b. The currents in the primary and secondary windings C. The incoming and outgoing transmission line currents
Problem 4 Three ideal single-phase transformers are connected in a delta/wye configuration with the primary side of the three-phase transformer rated at 120 kV and the secondary side rated at 13.8 kV. The rated power of the transformer bank is 20 MVA. One side of the transformer bank is connected to a 120 kV transmission line, and the other side is connected to a three-phase load of 15 MVA at 0.85 lagging power factor. Compute the following: a) The turns...
Three single-phase transformers rated at 250 kVA, 7200 V/600 V, 60 Hz, are connected in wye- delta on a 12.47 kv, 3-phase line. If the load is 450 kVA, calculate: a. The currents in the incoming and outgoing transmission lines b. The currents in the primary and secondary windings 1. sratod t 200 w 3o0 v/6oO V 60 Hz are used to raise the
Three single-phase transformers rated at 250 kVA, 7200 V/600 V, 60 Hz, are connected in wye-...
a. Three single phase step-up transformers rated at 40 MVA, 13.2 kV/80 kV are connected in delta-wye on a 13.2 kV transmission line. If they feed a 90 MVA load calculate the following: i. The secondary line voltage ii. The current in the transformer windings iii. The incoming line currents iv. If the transformer types are two (2) additive and one (1) subtractive draw the connection diagram for the configuration stated using physical representation. b. A 3-phase squirrel cage motor has twelve (12) leads (labelled 1 to...
The ratings of a three-phase, three-winding transformer are Y connected, 66 kV, 20 MVA Primary (1): Secondary (2):Y connected, 13.2 kV, 15 MVA Tertiary (3): A connected, 2.3 kV, 5 MVA Neglecting winding resistances and exciting current, the per-unit leakage reactances are: X12 0.08 on a 20-MVA, 66-kV base X13 0.10 on a 20-MVA, 66-kV base X23 0.09 on a 15-MVA, 13.2-kV base (a) Determine the per-unit reactances Xi, X2, X3 of the equivalent circuit on a 20- MVA, 66-kV...
Problem 1: A three-phase transformer has the following name plate data: Rated Power Primary voltage Secondary Voltage Excitation reactance Series Impedance 150 MVA 230 kV 32 kV 30 (pu) 0.02+0.15j (pu) The transformer is Y/A connected. Answer the following questions: a) What are the nominal (rated) primary and secondary line currents?| b) What is the nominal value of the Delta-side winding (internal) current? c) What is the secondary to primary winding turn ratio? d) The transformer is supplying 150 MVA...
2. Three single-phase transformers rated at 300 KVA, 7200 V/600 V, 60 Hz, are used to raise the voltage of a 3-phase, 600 V line to 7.2 kv. a. How must they be connected? b. Calculate the line currents for a load of 750 kVA. C. Calculate the corresponding primary and secondary currents.
4. Three ideal single-phase transformers are connected as shown below. The turns ratio of each single-phase transformer is 2400/480. Assume a perfectly balanced three- phase system (with ABC sequence) and that the delta side is the high-voltage side. (a) If IA is 8 amperes at 20 degrees, determine the phasor current Ix. (b) If the three-phase load is 100 kW at 0.87 lagging power factor and 465 V, determine how much current is flowing in the primary winding of T3....
1. In order to meet an emergency, three single-phase transformers with 12.470/7.200 V are connected in Delta-Wye to form a three-phase transformer which is fed by a 12.470 V transmission line. If the transformer supplies 60 MVA to a load, calculate: (3 marks) a. The turns ratio for each transformer b. The currents in the primary and secondary windings of the transformer c. The primary and secondary transmission line currents 2. A Wye-Delta transformer is connected to a 66 kV...
A tie breaker is accidently closed that parallels three single phase transformers each rated 500 kVA connected delta primary wye secondary, with a three phase 1500 kVA transformer connected delta-delta. The equivalent impedance of the delta transformer is 0.056 at an angle of 58o. The equivalent impedance of the wye transformers is 0.022 at an angle of 58o. Both transformer have 12.47kV to 480V. All feeder breakers are open. Calculate the magnitude of the current circulating in each transformer secondary,...