Question

2. Three single-phase transformers rated at 300 KVA, 7200 V/600 V, 60 Hz, are used to raise the voltage of a 3-phase, 600 V l
0 0
Add a comment Improve this question Transcribed image text
Answer #1

a) In case of A- connection - You = Vine. Transforma should be connect in A (delta) Primary =6000 secan day = 7.280-7200U 3=

If you have any doubt please make a comment. Thank you

Add a comment
Know the answer?
Add Answer to:
2. Three single-phase transformers rated at 300 KVA, 7200 V/600 V, 60 Hz, are used to...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Three single-phase transformers rated at 250 kVA, 7200 V/600 V, 60 Hz, are connected in wye- delta on a 12.47 kv, 3-phase line. If the load is 450 kVA, calculate: a. The currents in the incoming a...

    Three single-phase transformers rated at 250 kVA, 7200 V/600 V, 60 Hz, are connected in wye- delta on a 12.47 kv, 3-phase line. If the load is 450 kVA, calculate: a. The currents in the incoming and outgoing transmission lines b. The currents in the primary and secondary windings 1. sratod t 200 w 3o0 v/6oO V 60 Hz are used to raise the Three single-phase transformers rated at 250 kVA, 7200 V/600 V, 60 Hz, are connected in wye-...

  • 3. Three single-phase, 10 kVA, 460/120 V, 60 Hz transformers are connected to form a three-phase...

    3. Three single-phase, 10 kVA, 460/120 V, 60 Hz transformers are connected to form a three-phase 460/208 V transformer bank. The equivalent impedance of each transformer referred to HV side is 1.0 + j2.0 Ω. The transformer delivers 25 kW at 0.9 pf lagging at rated voltage. Answer the following questions: (a) Draw a schematic diagram showing the transformer connection. Draw three separate single-phase transformers and complete their primary and secondary connections. (b) Determine the magnitude of transformer primary and...

  • 1. Three single-phase step-up transformers rated at 75 MVA, 13.2 kV/80 kV are connected in delta-...

    1. Three single-phase step-up transformers rated at 75 MVA, 13.2 kV/80 kV are connected in delta- wye on a 13.2 kV transmission line. If they feed a 180 MVA load, calculate the following: a. The secondary line voltage b. The currents in the primary and secondary windings C. The incoming and outgoing transmission line currents

  • A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting thre...

    A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting three single phase transformers in the Dynll vector group as shown in Fig.P1. The per phase equivalent circuit parameters on the high voltage side are: R1-0.72 Ω, Xi,-0.92 Ω, R2-0.70 Ω, Xp-0.90 Ω, R.-308.49 Ω, and X,,-44.61 Ω (a) Sketch the corresponding phasor diagram of the primary and secondary voltages for the Dynll vector group; lagging; terminal voltage is 415 V line to line, and...

  • Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60...

    Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60 Hz. The following results are obtained from open-circuit and short-circuit tests: Test Open-circuit Short-circuit Voltage 7200 V 250 V Current 0.65 A 13.89 A Real Power Input 425 W 1420 W a) Determine the parameters of this transformer, all referred to the primary side. b) The secondary of this transformer is connected to a load that draws 100% of the rated power at rated...

  • 2. In order to meet an emergency, three single-phase transformers rated 100 kVA (each), 13.2 kV/2.4...

    2. In order to meet an emergency, three single-phase transformers rated 100 kVA (each), 13.2 kV/2.4 kV are connected in Y-∆ on a 3-phase, 20 kV line. a. What is the maximum load that can connected to the transformer bank? b. What is the outgoing line voltage?

  • A 200 kVA, 7200/600 V, 60 Hz transformer is operating at rated load and 0.9 p.f....

    A 200 kVA, 7200/600 V, 60 Hz transformer is operating at rated load and 0.9 p.f. lagging. The core loss, winding resistances and leakage reactances, expressed in per unit are 0.0056, 0.0133 and 0.0557 respectively. Determine: a) The efficiency. b) The voltage regulation. c) The efficiency and regulation at 0.3 load and 0.8 p.f. lagging. A 200 kVA, 7200/600 V, 60 Hz transformer is operating at rated load and 0.9 p.f. lagging. The core loss, winding resistances and leakage reactances,...

  • 1. In order to meet an emergency, three single-phase transformers with 12.470/7.200 V are connected in...

    1. In order to meet an emergency, three single-phase transformers with 12.470/7.200 V are connected in Delta-Wye to form a three-phase transformer which is fed by a 12.470 V transmission line. If the transformer supplies 60 MVA to a load, calculate: (3 marks) a. The turns ratio for each transformer b. The currents in the primary and secondary windings of the transformer c. The primary and secondary transmission line currents 2. A Wye-Delta transformer is connected to a 66 kV...

  • Ideal, single-phase two-winding transformer A single-phase two-winding transformer is rated 20 kVA, 480/120 V, 60 Hz...

    Ideal, single-phase two-winding transformer A single-phase two-winding transformer is rated 20 kVA, 480/120 V, 60 Hz A source connected to the 480-V winding supplies an impedance load con- nected to the 120-V winding. The load absorbs 15 kVA at 0.8 p.f. lagging Ideal, single-phase two-winding transformer A single-phase two-winding transformer is rated 20 kVA, 480/120 V, 60 Hz A source connected to the 480-V winding supplies an impedance load con- nected to the 120-V winding. The load absorbs 15 kVA...

  • A tie breaker is accidently closed that parallels three single phase transformers each rated 500 kVA...

    A tie breaker is accidently closed that parallels three single phase transformers each rated 500 kVA connected delta primary wye secondary, with a three phase 1500 kVA transformer connected delta-delta. The equivalent impedance of the delta transformer is 0.056 at an angle of 58o. The equivalent impedance of the wye transformers is 0.022 at an angle of 58o. Both transformer have 12.47kV to 480V. All feeder breakers are open. Calculate the magnitude of the current circulating in each transformer secondary,...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT