Consider the distribution system given in Problem 7 and assume that most transformers are shielded from lightning to some extent by buildings or trees. Therefore, use a “reasonable estimate” of 70% fo...

Consider the distribution system given in Problem 7 and assume that most transformers are shielded from lightning to some extent by buildings or trees. Therefore, use a “reasonable estimate” of 70% for the average shielding factor. It is assumed that the total expected number of strikes to the transformer poles is 174 strikes/year and that 5% of lightning return strokes exceed 100 kA. Determine the following:
(a) The total number of strikes per year to the transformers if shielding is taken into consideration
(b) The total number of expected transformer failures per year due to lightning
(c) The annual expected transformer failure rate due to lightning

0 0
Add a comment Improve this question Transcribed image text
Answer #1

(a)

answer = (70/100)*174 = 121.8 strikes per year

(b)

answer = (5/100) * 121.8 = 6.09 failures per year

(c)

answer = 6.09/174 = .035

in percentage = .035*100 = 3.5 %

Add a comment
Know the answer?
Add Answer to:
Consider the distribution system given in Problem 7 and assume that most transformers are shielded from lightning to some extent by buildings or trees. Therefore, use a “reasonable estimate” of 70% fo...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT