Question

Note Unless otherwise specified, three phase systems are rated in terms of their line-to-line rms voltages So, for instance,Problem 8 The line-to-line voltage of a three-phase transmission line is Vbc-120 2.20° kV. Suppose the load is in a Y-configu

Note Unless otherwise specified, three phase systems are rated in terms of their line-to-line rms voltages So, for instance, a three-phase 230 kV transmission line has an rms phase voltage of 230/V3 kV. If you encounter a three-phase system specified with two voltages, e.g., 480/277 V, that implies that the line-to-line rms voltage is 480 V and the rms phase voltage is 277 v.
Problem 8 The line-to-line voltage of a three-phase transmission line is Vbc-120 2.20° kV. Suppose the load is in a Y-configuration with an impedance of Z = 20 L 400 Ω. Compute the following: a) The phase A to neutral voltage phasor, Vam b) The transmission line current, Ic c) The current in the neutral line, In
0 0
Add a comment Improve this question Transcribed image text
Answer #1

oblen 8 . Nak Noe: Ass abc Se^ene. atn cn Cn 온 2Vbrn 2 2olyó

Add a comment
Know the answer?
Add Answer to:
Note Unless otherwise specified, three phase systems are rated in terms of their line-to-line rms voltages So, for instance, a three-phase 230 kV transmission line has an rms phase voltage of 230/V3...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A balanced positive-sequence wye-connected 60-Hz three-phase source has line-to-line voltages of VL = 440 V rms....

    A balanced positive-sequence wye-connected 60-Hz three-phase source has line-to-line voltages of VL = 440 V rms. This source is connected to a balanced wye-connected load. Each phase of the load consists of a 0.5-H inductance in series with a 50-Ω resistance. Assume that the phase of Van is zero. home / study / engineering / electrical engineering / electrical engineering questions and answers / A Balanced Positive-sequence Wye-connected 60-Hz Three-phase Source Has Line-to-line Voltages ... Question: A balanced positive-sequence wye-connected...

  • A 230-kV, three-phase transmission line has a per phase series impedance of z = 0.05j0.45 2...

    A 230-kV, three-phase transmission line has a per phase series impedance of z = 0.05j0.45 2 per km and a per phase shunt admittance ofy = j3.4 x 10-6 siemens per km. The line is 80 km long. Using the nominal r model, determine (a) The transmission line ABCD constants. Find the sending end voltage and current, voltage regulation, the sending end power and the transmission efficiency when the line delivers (b) 200 MVA, 0.8 lagging power factor at 220...

  • PROBLEM: A 230-kV, 50 Hz, three-phase transmission line is 120 km long. The line has a per phase ...

    PROBLEM: A 230-kV, 50 Hz, three-phase transmission line is 120 km long. The line has a per phase series impedance of z-0.05 +j0.45 Ω per km, and a per phase shunt admittance of y 3.4x10-6 Siemens per km. The line delivers (at the receiving end) 200 MVA, 0.8 lagging power factor at 220 kV. Now consider two cases: A- Assume that shunt parameters of the transmission line are ignored (i.e. even if this is a medium length transmission line, under...

  • Show the solution for the following problem 1. A short, 230 kV transmission line has an...

    Show the solution for the following problem 1. A short, 230 kV transmission line has an impedance of 5 cis 78 ohms. The load at the receiving end is 100 MW at 230 kV, 85% lagging power factor. What is the voltage at the sending end? a. 235.43 kV b. 226.3 kV c. 231.78 kV d. 238.21 kV 2. A 66 kv medium length transmission line delivers a load of 10 MW at 66 kv and 80% lagging P.F. the...

  • 3.8 A 275 kV three-phase transmission line of length 96 km is rated at 800 A....

    3.8 A 275 kV three-phase transmission line of length 96 km is rated at 800 A. The values of resistance, inductance and capacitance per phase per kilometre are 0.078 12, 1.056 mH and 0.029 F, respectively. The receiving-end voltage is 275 kV when full load is transmitted at 0.9 power factor lagging. Calculate the sending-end voltage and current, and the transmission efficiency, and com- pare with the answer obtained by the short-line representation. Use the nomi- nal n and T...

  • 1. A three-phase synchronous generator connected to a 345-KV transmission line through a transformer as shown...

    1. A three-phase synchronous generator connected to a 345-KV transmission line through a transformer as shown in Figure P1. Parameters of both generator and transformer are given in the figure. Transformer losses and exciting current are neglected. A three-phase short-circuit occurs on the line side of the circuit breaker when the generator is operated at rated terminal voltage and at no-load. The breaker interrupts the fault three cycles after fault inception. Neglect the effect of the transformer on the time...

  • 1. A balanced three-phase Y load has one phase voltage of Vcn = 277∠45◦ V ....

    1. A balanced three-phase Y load has one phase voltage of Vcn = 277∠45◦ V . If the phase sequence is negative sequence i.e. acb, calculate the line voltages Vca, Vab, and Vbc . 2. What are the phase voltages for a balanced three-phase Y load, if Vba = 12.47∠−35◦kV ? The phase sequence is positive sequence i.e. abc. Please help me solve this with full working out step by step.

  • Problem #2 (60 pts). A balanced three-phase 240-V (rms, line-to-line source supplies a balanced three-phase load....

    Problem #2 (60 pts). A balanced three-phase 240-V (rms, line-to-line source supplies a balanced three-phase load. If the line current IA is measured to be 15 A and is in phase with the line-to-line voltage, VBc, find the per-phase load impedance if the load is (a) Y-connected (b) A-connected. Calculate the complex ower S for each case.

  • QUESTIONS 1- A 69-kV, three-phase transmission line is 20 km long. The line has a per...

    QUESTIONS 1- A 69-kV, three-phase transmission line is 20 km long. The line has a per phase series impedance of 0,120 + 10,4325 per km. Detemine the sending end voltage, voltage regulation, the sending end power, and the transmission efficiency when the line delivers (a) 60 MVA, 0.8 lagging power factor at 60 kV. (b) 110 MW, unity power factor at 60 kV

  • A 400-MVA, 200-kV/20-kV, three phase Y-Y transformer has an equivalent series impedance of ZTL = 0.012...

    A 400-MVA, 200-kV/20-kV, three phase Y-Y transformer has an equivalent series impedance of ZTL = 0.012 + 20.0162 per phase referred to the low-voltage side (secondary side). The transformer is supplying a three-phase load of 300-MVA, 0.8 power factor lagging at terminal voltage of 20 kV (line-to-line) on its low-voltage side (secondary side) as shown in Fig. 22. The primary is supplied from a transmission line with an impedance of ZL = 0.5 + j1.0 per phase. The line-to-neutral load...