9. D
If a conductor termination does not have a marked temperature
rating, 110.14(C)(1) sets the temperature rating based upon the
rating of overcurrent device or conductor size.
If the conductor is size 1/0 AWG or larger, the termination is
required to have a minimum rating of 75°C unless otherwise
marked.
10. C
Allowable ampacity for 3 conductors in raceaway, when the
terminations are rated at 75 degree celsius, for THHW copper
conductor from the table would be found from the 75 degree Celsius
column of Table 310.16.
Lighting load is a continuous load, therefore, the minimum
conductor size, according to 210.19(A), is required to be not less
than 1.25 times the load supplied, which is 1.25 x 14.2 = 17.75
Amperes.
So, per Table 310.16, a size 14 AWG copper conductor is rated 20
amperes.
Further the rule in 240.4(D) only permits a 15-ampere overcurrent
device on a size 14 AWG copper conductor. So, a size 12 AWG copper
conductor is the minimum permitted because the overcurrent device
is rated 20 amperes (branch circuit is rated at 20 Amperes).
11. E
590.4(D) does not permit receptacles to be installed on the same
circuit with temporary lighting.
12. C
Air-handling duct (Busway) is a factory-assembled metal enclosure
containing electrical conductors, usually in the form of copper or
aluminum bars insulated from the metal enclosure. Busway is
frequently used in commercial and industrial work areas by
attaching to the ceiling with a spacing not to exceed 5 ft (1.5
m)
Busway height = Ceiling height - 1.5m = 4.5 -1.5 = 3m
Panel board height = 1.8 m. So, Busway height from above the panel
board = 3m -1.8m = 1.2 m.
Code Reference: 368.30
O AWG copper conductor without any markings to indicate the The terminal for dh s terminal is assumed to have a min...
pleas help me in this do any question you know using National Electrical Code 2011 Applied Electricity NEC worksheet t hree Copper conductors with THHN insulation run in Electrical A branch-circuit Consther conductors. The conductor terminations are rated for a maximum ure in the area of this installation is not expected to exceed 30C size 8 AWG, the maximum ampacity of the conductors If the conductors for this circuit are permitted A 40 amperes. B. 50 amperes. to be used...
dwelling un 4. Type NM-B Cable enters a metal device box and is secured by a cable clamp at the bottom of the box. The cable is installed so the cable jacket extends "1/4 in. (6 mm beyond the cable clamp and free conductors begin at the end of the cable jacket a shown in Figure 1.39. If the device box has a depth of 3.5 in. (90 mm), the minimum permitted length of free conductor in this box is...
can anyone help me with this test please? I'm struggling with it QUESTION 1 A permanently installed overhead strip light is a ____. a.foot light b.track light c.border light d.head light QUESTION 2 Egress lighting for carnivals, circuses and fairs shall not ____. a.contain metal raceways b.be integrated into a central switchboard c.contain branch circuits d.be protected by a GFCI protection device QUESTION 3 The attachment plug cap in a mobile home shall be a ____, rated 50...
(1). In regard to installation of electrical conductions and equipment, who may grant exceptions to the requirements of the NEC? A. nfpa b. ahj c. ieee d. ul. (2). Exceptions to the Code permit alternate methods to the general (main) rule. Exceptions are permitted. A. when all of the provisions of the exception are met. B. when a written request is submitted to and approved by the NEC. C. any time the electrician deems it necessary. D. not more than...