2.1 Heat duty = mCp (Tin - Tout)
= 110 * 2177 *(90-50)
= 9578800 W
In second case, the flow rate is increased by 20% hence the new flow rate is 132 kg/s
Hence heat duty is = 132* 2177 *(90 -50) = 11494560 W
2.2 We know that
A = d0 L Nt
Hence the available area is, * (19.05 x 10-3 ) * 2344 * 4.877 = 684 m2
2.3 Required formulas are given below,
From energy balance we can find the mass flow rate of cooling water
11494560 = m * 4187 * (40-30)
Hence m = 274.53 kg/s
Tube side:
Velocity v =
= 2.41553 m/s
Reynolds number Re =
= 52575.52016
Prandtl Number Pr = 5.10955
Nusselt number Nu =
= 235.5706
Heat transfer coefficient = 8824.55 W/m2 K
Jf from standard charts = 3.2 x 10-3
Pressure Drop =
= 121.05086.8676 Pa
Shell side:
Pt =1.25 * 19.05 = 23.8125 mm
de =
= 18.8104 mm
As =
= 0.170128 m2
v =
= 0.9587 m/s
Re =
= 7509.200
Pr = 33.725655
Nu = 485.2256
h = 3146.46 W/m2 K
Jf from standard charts is 5 x 10-2
Pressure Drop =
= 82958.88 N/m2
Uoverall = 850.433 W/m2 K
=
= 32.7407
R = 4 S =0.16667
LMTD correction factor from charts = 0.931
= 0.931 * 32.7404 = 30.501 C
Area required = Q/U
= 443.136 m2
Clearly the HX does not meet the pressure drop requirements. But sufficient area is available for heat transfer
2.4
With the given dimensions,
if No. of passes is made to be 2,
Then v = 1.207665 m/s ( Use the velocity equation, take Np =2)
Re = 26285.5835
Jf = 4 x 10-3
Pressure drop = 18.00722 kPa
Nu= 128.83
h = 4826.009 W/m2 K
U overall = 606.075 W/m2 K
Area = 621.801 m2
Hence all criteria are met
1 CPD4701 Assignment 2/2019 Question 2 shell and-tube heat exchanger was designed for the following service: Cold strea...
1 CPD4701 Assignment 2/2019 Question 2 shell and-tube heat exchanger was designed for the following service: Cold stream Hot stream Crude Oil Fluid Cooling water Tube side Stream allocation Shell side Mass flow rate (kg/s) 110 30 Inlet temperature (C) 90 Outlet temperature (C) Heat capacity (J/kg K) Density (kg/m2) Viscosity (Pa-s) Thermal conductivity (W/m-K) Fouling factor (m2 CW) 40 50 2177 4187 787 995 0.72-10 1.89-103 0.122 0.59 0.0002 0.0004 The shell and tube heat exchanger has the following...
A shell and tube heat exchanger with one shell pass and one tube pass will be used to condense the steam to saturated liquid, which enters the shell side as a saturated vapor at 400 K. The tube side contains R-134a refrigerant with an inlet temperature of 300 K and a mean velocity of 0.4 m/s. The steam flow rate is 1.5 kg/s. The tubes are made from AISI 302 stainless steel and have a 1" nominal diameter (Di =...
Q2. Shell-and-tube heat exchangers with hundreds of tubes housed in a shell are commonly used in practice for heat transfer between two fluids (shown in Figure 1). Such a heat exchanger used in an active solar hot-water system transfers heat from a water-antifreeze solution flowing through the shell and the solar collector to fresh water flowing through the tubes at an average temperature of 60°C at a rate of 15 L/S. The heat exchanger contains 80 brass tubes 1 cm...
A shell and tube heat exchanger with one shell pass and one tube pass will be used to condense the steam to saturated liquid, which enters the shell side as a saturated vapor at 400 K. The tube side contains R-134a refrigerant with an inlet temperature of 300 K and a mean velocity of 0.4 m/s. The steam flow rate is 1.5 kg/s. The tubes are made from AISI 302 stainless steel and have a 1" nominal diameter (Di =...
be clear Problem 3 (60 Points). A 1-2 shell-and-tube heat exchanger must be designed to heat 2.5 kg/s of water from 15 to 85°C. The heating is to be accomplished by passing hot engine oil at a rate of 5.2 kg/s, which is available at 160°C, through the shell side of the exchanger. The oil is known to provide an average convection coefficient of 400 W/m2K on the outside of the tubes. Ten tubes passes the water through the shell....
6. A shell-and-tube heat exchanger with 2-shell passes and 12-tube passes is used to heat water (c 4,180 J/kg K) flowing at a rate of 4.5 kg/s in the tubes from 20°C to 70°C. Heat is supplied by hot oil (cp 2300 J/kg K) that enters the shell side at 170°C at a rate of 10 kg/s. If overall heat transfer coefficient on the tube-side is 350 W/m-K, determine the heat transfer surface area on the tube side.
Required information A shell-and-tube heat exchanger is used for cooling 47 kg/s of a process stream flowing through the tubes from 160°C to 136°C. This heat exchanger has a total of 100 identical tubes. each with an inside diameter of 2.5 cm and negligible wall thickness. The average properties of the process stream are: p = 950 kg/m”, k = 0.50 W/mK, Cp=3.5 kJ/kg.K, and -20 mPas The coolant stream is water (cp=4.18 kJ/kg K) at a flow rate of...
A shell and tube heat exchanger with one shell pass and two tube passes is used to heat 8.82 kg/s of fluid from 15.6 °C to 60 °C by using saturated steam at 150 kPa. The steam is condensing on the outside of the tubes with h= 15 kW/m2.K. There are 50 tubes with an outside diameter of 1.91 cm and a wall thickness of 0.211 cm. If the fouling coefficient on the inside of the tubes is 5678 W/m2.K,...
Question 5 - LMTD Heat Exchangers A 2 shell, 4 tube pass heat exchanger is being used to heat 50 kg/s of a process fluid in the tubes from an inlet temperature of 25°C to a target temperature of 80°C using condensing steam at 150°C. The overall heat transfer coefficient for a clean heat exchanger was U-1500W/m2.°C, however, the design engineer neglected to take into account fouling of the heat exchanger. After 5 years of use, fouling has occurred with...
3. In a shell-and-tube heat exchanger, under nominal condition a process stream (a liquid) is heated from 100°C to 200°C without any phase change using a heating medium in the tube side, temperature of which gets reduced from 300°C to 150°C. The process side has a bypass which remains closed under nominal condition. Under nominal condition, there are equal resistances to heat transfer on shell and tube sides. It is desired that the process stream flowrate be increased by 30%,...