A shell and tube heat exchanger with one shell pass and one tube pass will be...

A shell and tube heat exchanger with one shell pass and one tube pass will be used to condense the steam to saturated liquid, which enters the shell side as a saturated vapor at 400 K. The tube side contains R-134a refrigerant with an inlet temperature of 300 K and a mean velocity of 0.4 m/s. The steam flow rate is 1.5 kg/s. The tubes are made from AISI 302 stainless steel and have a 1" nominal diameter (Di = 26.6 mm and Do = 33.4 mm). The heat transfer coefficient at the outer surface of the tubes is ho = 10,000 W/m^2K. Assume a fouling resistance of 0.0002 m^2K/W at the inside surface of the tubes and negligible fouling at the outside.

a) If the coolant outlet temperature is not to exceed 320 K, what is the minimum allowable coolant flowrate?

b) How many tubes are required to achieve the desired performance?

c) What tube length is required?

0 0
Add a comment Improve this question Transcribed image text
Answer #1

r o They One sheld one tube pass pass - I - to > THA UTIZOS satunded rapon = 4ook shell side Tube side R-1349 > Tci = 300k Tc0.4 K for Turbulent flow inside Tube: Nu = 0.023 Red piz í oftar Beelter Nuz hidi 20.023 (714678331,4% -ezedsion) ln=3 cco1) a= mcpAT Qzi hay 3) 1.5x2138 2 9 X 1485*C 3280300) 6922183 kJ z) M = 107.augls can) of 4ook 1. * Reborigeran How Log mean

Add a comment
Know the answer?
Add Answer to:
A shell and tube heat exchanger with one shell pass and one tube pass will be...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A shell and tube heat exchanger with one shell pass and one tube pass will be...

    A shell and tube heat exchanger with one shell pass and one tube pass will be used to condense the steam to saturated liquid, which enters the shell side as a saturated vapor at 400 K. The tube side contains R-134a refrigerant with an inlet temperature of 300 K and a mean velocity of 0.4 m/s. The steam flow rate is 1.5 kg/s. The tubes are made from AISI 302 stainless steel and have a 1" nominal diameter (Di =...

  • A shell and tube heat exchanger with one shell pass and two tube passes is used...

    A shell and tube heat exchanger with one shell pass and two tube passes is used to heat 8.82 kg/s of fluid from 15.6 °C to 60 °C by using saturated steam at 150 kPa. The steam is condensing on the outside of the tubes with h= 15 kW/m2.K. There are 50 tubes with an outside diameter of 1.91 cm and a wall thickness of 0.211 cm. If the fouling coefficient on the inside of the tubes is 5678 W/m2.K,...

  • Question 5 - LMTD Heat Exchangers A 2 shell, 4 tube pass heat exchanger is being...

    Question 5 - LMTD Heat Exchangers A 2 shell, 4 tube pass heat exchanger is being used to heat 50 kg/s of a process fluid in the tubes from an inlet temperature of 25°C to a target temperature of 80°C using condensing steam at 150°C. The overall heat transfer coefficient for a clean heat exchanger was U-1500W/m2.°C, however, the design engineer neglected to take into account fouling of the heat exchanger. After 5 years of use, fouling has occurred with...

  • (LMTD method) A 2 shell, 4 tube pass heat exchanger is beingused to heat 40...

    (LMTD method) A 2 shell, 4 tube pass heat exchanger is being used to heat 40 kg/s of a process fluid in the tubes from an inlet temperature of 15°C to a target temperature of 70°C using condensing steam at 150°C. The overall heat transfer coefficient for a clean heat exchanger was Uo=1500W/m2.°C, however, the design engineer neglected to take into account fouling of the heat exchanger. After 5 years of use, fouling has occurred with fouling factors of 0.0005m2.°C/W...

  • A shell-and tube heat exchanger has one-shell pass and 2-tube passes. This heat exchanger is used...

    A shell-and tube heat exchanger has one-shell pass and 2-tube passes. This heat exchanger is used to cool oil, flowing through the tube-side from 140°C to 50°C. The cooling is accomplished by water, flowing through the shell-side, which enters the heat exchanger at 15°C and leaves at 32°C. Each tube pass consists of 60, 2.54-cm-O.D. tubes with a wall thickness of 1.65 mm.if the inside and outside heat transfer coefficients are h1=260 W/(m^2°C) and h°=970 W/(m^2°C), respectively, and the fouling...

  • Section C – shell and tube heat exchanger sizing The vapour condenser for the combined gas-steam ...

    Section C – shell and tube heat exchanger sizing The vapour condenser for the combined gas-steam power cycle described in Section B heats river water from 15 °C to 18 °C. The condenser is a shell and tube heat exchanger with one shell pass and two tube passes. The cooling water is inside the tubes while the shell side has the condensing vapour. More details: a. The tube OD is 1 ¼” (inches), the tube wall thickness is 0.05 inches....

  • heat transfer Test Yourself A Shell-and-tube heat exchanger, consisting of a single shell and 30.000 tubes,...

    heat transfer Test Yourself A Shell-and-tube heat exchanger, consisting of a single shell and 30.000 tubes, each executing two passes, is used in a large steam power plant to condense steam to liquid water. The steam condensed in the shell side of the heat exchanger with an associated convection coefficient (h) of 11.000 W/m2.°C. The heat transfer rate through the heat exchanger (O is 2x10' W. Cooling water is passing through a thin tubes with D = 2.5 cm, at...

  • 1 CPD4701 Assignment 2/2019 Question 2 shell and-tube heat exchanger was designed for the following service: Cold strea...

    1 CPD4701 Assignment 2/2019 Question 2 shell and-tube heat exchanger was designed for the following service: Cold stream Hot stream Crude Oil Fluid Cooling water Tube side Stream allocation Shell side Mass flow rate (kg/s) 110 30 Inlet temperature (C) 90 Outlet temperature (C) Heat capacity (J/kg K) Density (kg/m2) Viscosity (Pa-s) Thermal conductivity (W/m-K) Fouling factor (m2 CW) 40 50 2177 4187 787 995 0.72-10 1.89-103 0.122 0.59 0.0002 0.0004 The shell and tube heat exchanger has the following...

  • 1 CPD4701 Assignment 2/2019 Question 2 shell and-tube heat exchanger was designed for the following service: Cold strea...

    1 CPD4701 Assignment 2/2019 Question 2 shell and-tube heat exchanger was designed for the following service: Cold stream Hot stream Crude Oil Fluid Cooling water Tube side Stream allocation Shell side Mass flow rate (kg/s) 110 30 Inlet temperature (C) 90 Outlet temperature (C) Heat capacity (J/kg K) Density (kg/m2) Viscosity (Pa-s) Thermal conductivity (W/m-K) Fouling factor (m2 CW) 40 50 2177 4187 787 995 0.72-10 1.89-103 0.122 0.59 0.0002 0.0004 The shell and tube heat exchanger has the following...

  • Oil of unknown properties is heated in a shell-and-tube heat exchanger with one shell pass and...

    Oil of unknown properties is heated in a shell-and-tube heat exchanger with one shell pass and 20 tube passes. The oil flows through the shell, and hot water flows inside the single copper tube that has an inner diameter of 20 mm, a wall thickness of 2 mm, and a length of 3 m per pass. The water enters at 360 K at a mass flow rate of 0.2 kg/s and leaves at 300 K. The inlet and outlet temperatures...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT