Ex 3 3-phase network. Un= 15 kV (take it in point 0), S=35 mm7, y= 34...
Ex 3 3-phase network. Un= 15 kV (take it in point 0), S=35 mm7, y= 34 m/(Q-mm2), X'-0,4 Q/km. L01 L12 23 2 2 13 Length of lines: L23 4,2 km L12 800 m Lo1 2,5 km, Load currents: 38,5-8,1 A, 2 44,8-18,1 A a 25,4 j4,1 A. Calculate: Total voltage loss SU03 [V] ? (complex number!) Total voltage drop Δυ03 [V] ? AP03 Total active power loss [W] ? Total reactive power loss [var] ΔQ03 ? Ex 3 3-phase...
Ex 2 15 kV 110 kV T1 L1 L2 C A Ska Power system: S ka 1500 MVA HV Line L1 S 240 mm2 (AFL-6 240), y 34 m/(-mm2), X 0,4 /km | 25 km Transformer T1 9 121/15,75 kv U2 11% APcu 90 kW SN 16 MVA MV Line L2 S 70 mm2 | 15 km y 34 m/(-mm2), X 0,4 /km Calculate 3-phase short-circuit currents in point B and D: Ikзв %3D?, Load Ex 2 15 kV 110...