Step1 :
D.L=22 kips
L.L=45 kips
Pu=1.2(22)+1.6(45)
Pu=98.4 kips is the point load acting on each side
Step 2:
Maximum bending moment=WL/3
B.M=98.4x30/3
B.M=984 ft-kips
Step 3:
Calculate the section modulus
Zx=Mu/(0.9Fy)
Zx=984x12/(0.9x50)
Zx=262.4 in3
From the Zx tables, select a W section and consider self weight also
Step 4:
Consider W21x111 having Zx=279 in3,
Now check for self weight
D.L=1.2(22+0.111)
L.L=1.6(45)
Pu=98.53 kips
M=98.51x10=985.3 ft-kips
Zx=Mu/(0.9Fy)
Zx=985.3x12/(0.9x50)
Zx=263 in3 is required, 279 in3 is provided
Step 5:
Check for Lp, Lb and Lr values
Lb=10 ft
Lp=10.2 ft
Lr=31.3 ft
As Lp>Lb, no local torsional buckling occurs
Mn=Mp=FyZx
Mp=50x279
Mp=13950 kip-in=1162.5 ft-kips
LRFD design strength=0.9x1162.5=1046.25 ft-kips
Mn>Mu, so the beam is safe in bending
(2)
Check for shear:
Vu=98.4 kips
Vn=0.6Fydtw
Vn=0.6x50x21.5x0.55
Vn=354.75 kips, this beam is safe in shear also
(3)
P=45 kips (deflection is calculated only for unfactored live load)
Span/240=30x12/240=1.5 in
=Pa(3L2-4a2)/24EI
=45x120(3x3602-4x1202)/24x29000x2670
=0.96 in
The beam W21X111 is safe in bending, shear and deflection, so it can be safely used
Problem 5: Select the lightest steel beam. Fy=50 ksi. The lateral bracing is provided at the...
Problem 3: Design of Steel Beam for Bending with Varying Unbraced Lengths Select the lightest A992 steel W-shape for the beam shown below using LRFD. Only consider design (neglect shear a bracing situations: a. Continuous lateral support of the compression flange b. Lateral support at beam ends and at the point of the concentrated load c. Lateral support only at beam ends PD = 10k PL-20k WD-3.33 k/ft w, = 6.67 k/ft 10' 20' 30'
1) Select the lightest section that can be used for the beam shown below if lateral bracing is provided only at the ends of the beam. Given loads are service loads (dead load given includes beam dead weight). Use Fy= 50ksi. The point load is applied at midspan. 4) Select the lightest section that can be used for the beam shown below if lateral bracing is provided only at the ends of the beam. Given loads are service loads (dead...
Problem 1 (100 pts) Select the lightest W24 beam section with Fy = 50 ksi using LRFD for the following span and loading. The unbraced length of the compression flange is 30 ft (Lb = 30'). Consider Cb > 1. The given dead load does not include beam weight. Verify that the selected beam has adequate shear strength. Maximum allowable deflection due to live load is L720. Maximum allowable deflection due to total load is L/360. WD = 1.2 k/ft...
Please complete the 3 design problems. Problem 1. Select the lightest W12 section available to support working tensile loads of PD - 250k and PL - 325k. The member is to be 30ft long and is assumed to have two lines of holes for 1-inch bolts in each flange. There will be at least three bolts in each line 4-in on center. Neglect Block Shear Problem 2. Select the lightest available W12 section to support the axial loads PD -...
Select the lightest W shape for the beam shown. Assume A36 steel and full lateral support. Consider moment and shear. 4-34. 50 220 80* 2-0 10-0 10-0 8-0 PROBLEM 4-34 Select the lightest W shape for the beam shown. Assume A36 steel and full lateral support. Consider moment and shear. 4-34. 50 220 80* 2-0 10-0 10-0 8-0 PROBLEM 4-34
22-3: Select the lightest available section for the span and loading shown using A992 steel. The member is assumed to have full lateral bracing. Be sure to check the shear capacity of your selection. You will need to draw shear and moment diagrams. P 85 kips PU 170 kips PU= 110 kips 12 ft 2 ft 12 ft 3 ft A
04:05%) For the beam shown in the figure select the shallower W section of Fy 50 ksi steel for moment assume the beam is compact and has full laterally support. (Neglect the self-weight of the beam), (Pu 1.2DL+1.6LL) Pu=60 k 10f 15ft 04:05%) For the beam shown in the figure select the shallower W section of Fy 50 ksi steel for moment assume the beam is compact and has full laterally support. (Neglect the self-weight of the beam), (Pu 1.2DL+1.6LL)...
Select the lightest W shape for the loading below. All loads are dead loads and the 2 k/ft includes th beam weight. The steel is A992, the compression flange is supported at the ends and at the concentrated load and C 1.0. The maximum service load deflection cannot exceed 1/1000 of the span. Design for moment and check shear and deflection. Identify what zone the beam is in and check that it does not exceed zone 1 maximum strength. 13...
Select the lightest C section that will safely support the service tensile loads PD = 50 k and PL = 65 k. The member is to be 14 ft long and is assumed to have two lines of holes for 4-in bolts in the web. Assume that there are at least three holes in each line 3-in on center. Use A36 steel. Neglect block shear.
***NOTE*** you *MUST draw complete FBD, and complete Shear-Force and Bending-Moment diagrams Select the lightest-weight steel wide-flange (W) overhanging beam from Appendix B that will safely support the loading. Assume the support at A is a pin and the support at B is a roller. The allowable bending stress is allow (see email data) and the allowable shear stress is "Zaitow -- 14 ksi. 8 ft + Non 4ft af Selected beam section is: W X P (kip) = 3...