5.11-7 Select an A992 W-shape for beam AB of the floor system shown in Fig ure P5.11-7. In addition to the weight of the beam

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Tributary width of beam=5 ft

Dead weight of floor=(5/12)*150=62.5 psf

Umiform dead load on beam=62.5*5=312.5 plf=0.3125 kip/ft

Uniform live load on beam=(80+20)*5=500 plf=0.5 kip/ft

Total service level load on beam=0.3125+0.5=0.8125 kip/ft

Span of beam=30 ft

a)

Factored load on beam=1.2*0.3125+1.6*0.5=1.175 kip/ft

Factored momemt in beam=1.175*30²/8=132.2 kip-ft

Lightest section with this strength=W12x26

Moment of inertia=204 in⁴

Total service load=0.8125 kip/ft=0.0677 kip/in

Total deflection=(5/384)*0.0677*(30*12)⁴/(29000*204)=2.5 in

Allowable deflection=30*12/240=1.5 in

Minimum moment of inertia required=204*(2.5/1.5)=340 in⁴

Lightet section with moment of inertia greater than 340 is W16x26

Therefore section required is W16x26

It has LRFD strength of 166 kip-ft

b)

Deflection check is same as in LRFD

ASD strength of W16x26=110 kip-ft

ASD demand on beam=0.8125*30²/8=91.4 kip-ft

Therefore,W16x26 is required

Add a comment
Know the answer?
Add Answer to:
Can I get a solution for this question? It's quite hard to solve 5.11-7 Select an...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Check the adequacy of a W18X35 for a beam (the beam in the vertical direction in...

    Check the adequacy of a W18X35 for a beam (the beam in the vertical direction in the plan) in a floor framing system in terms of 1) bending strength; 2) shear strength and 3) deflection. The beams support a 4-inch-thick reinforced concreted floor slab (with a density of 150 lbs/ft?). Besides the weight of the structure, loads consist of a uniform live load of 80 psf and moveable partitions (with a uniformly distributed load of 20 psf of floor surface)....

  • Could you please help me on question 7. Thank you very much. The floor system shown...

    Could you please help me on question 7. Thank you very much. The floor system shown below consists of normalweight concrete (150 pcf). Beams C2 ! LT 1 7.0 inch ! h=20 in G2! 12 in Girders BI 1 7.0 inch Slab 8 ft span h 24 in ----- - -- - --- 15 in 15 ft 15 ft Use 4000 psi concrete and Gr. 60 reinforcing steel. Assume 0.75 inch clear cover. Include concrete self-weight and a superimposed dead...

  • 4. A two story office building has interior columns spaced 25 ft apart in two perpendicular...

    4. A two story office building has interior columns spaced 25 ft apart in two perpendicular directions. The columns are fixed at the roof, the second floor and the ground floor in both directions. Consider the dead load (4 inch-thick reinforced concrete slab at the roof and 6 inch thick reinforced concrete slab at the floor) as well as appropriate live load. Ignore other dead weight other than shown. Determine the following using A992 steel: (20 points) 1) Dead load...

  • IL. A W 14x 22 acts compositely with a 4-inch-thick floor slab whose effective width b is 90 inch...

    IL. A W 14x 22 acts compositely with a 4-inch-thick floor slab whose effective width b is 90 inches. The beams are spaced at 6 feet, and the span length is 30 feet. The superimposed loads are as follows: construction load 20psf, partition load-10psf, weight of ceiling and light fixtures-5 and live load-60 psf . A992 steel is used, and fo 4 ksi a. Compute the maximum deflection before the concrete has cured b. Compute the maximum deflection after composite...

  • *please solve ALL questions Assume that the floor between Beams B7 and B8 is supported directly...

    *please solve ALL questions Assume that the floor between Beams B7 and B8 is supported directly by these two beams only (not by Girders G2 and G3). Beam B7 has a self-weight of 30 plf. The floor slab consists of a 4-in.-thick, normal-weight, reinforced concrete slab (unit weight = 150 pcf). An additional floor dead load of 15 psf is specified to account for the weight of suspended utilities and fixtures. As an exterior beam, B7 must also support one...

  • is the second floor of a four-story building. a flat Consider the floor framing plan shown...

    is the second floor of a four-story building. a flat Consider the floor framing plan shown below. Thi The design floor live load is 90 psf. The design roof live load is 20 psf. The structure has roof G1 G4 /2 G2 GS 2o G3 FLOOR FRAMING PLAN Assume that the floor between Beams B7 and B8 is supported directly by these two beams only (not by Girders G2 and G3). Beam B7 has a self-weight of 30 plf. The...

  • structural design in steel Q4) Select a W-shape beam for the following conditio Beam spacing 8...

    structural design in steel Q4) Select a W-shape beam for the following conditio Beam spacing 8 ft - Span length 32 ft Slab and deck combination weight- 50 psf Partition load 20 psf; - Ceiling weight 7 psf Live load 120 psf; The maximum live load deflection cannot exceed L/360. F, = 50 ksi

  • I just need help with (I). I can not seem to find the self-weight equation to...

    I just need help with (I). I can not seem to find the self-weight equation to add to my dead load. 1. A reinforced slab built integrally with beam consists of four spans (8' 6" on- center). The clear span of the slab is 7' 6" for all spans including the end span. The service live load is 160 psf and the service dead load is 30 psf (excluding self-weight). Given: f'.= 4,000 psi, normal weight concrete, fy= 60,000 psi....

  • 10, A w24x 55 floor beam supports a 4-inch-thick reinforced concrete slab with an effective width...

    10, A w24x 55 floor beam supports a 4-inch-thick reinforced concrete slab with an effective width of 78 inches. The 28-day compressive strength of the concrete is 4 ksi. a. Determine required number of anchors to make the beam fully composite. b. Calculate resisting moment of the steel beam before concrete hardens,pMn. c. Calculate resisting moment of the composite beam, Mn. d. If number of studs are reduced by 25%, determine the available flexural strength of composite beam,oMn. Calculate final...

  • The plan view of a typical floor of a four-story heavy storage facility is shown below. The floor and roof live load is...

    The plan view of a typical floor of a four-story heavy storage facility is shown below. The floor and roof live load is 250 psf, and the dead load on all foors and the roof consists of the structure self-weight plus 10 psf for utilities. W 12:96 beams are spaced at 12 ft; w 18x106 reinforced one-way concrete floor/roof slab is 8" thick, each story is 12' high, and the reinforced concrete columns have a 14" x 14" cross-section girders...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT