In order for any SIPR access to occur, there must be adequate power generation. The Brigade requires 160 kW of power at all times for full operation of their Tactical Operations Center (TOC). They deploy two 100 kW generators, five 60 kW generators, and four 30 kW generators for this purpose and any number of them can be used at any time to achieve the required power level. However, the transportation contractor reports that an accident damaged seven of these 11 generators during transit to theater. The contractor was not able to specify which ones were damaged. (20 points) Calculate the probability the undamaged generators will provide the required 160 kW.
Total no. Of ways in which 7 generators could be damaged = 11C7 = 330
To achieve required power level, the sum of the capacity of 4 remaining undamaged generators have to be equal to OR greater than 160 kW.
4 undamaged generators will fail to supply required power if all 4 of them are 30W generators
or
one 60W and three 30W generators are left undamaged.
In all remaining, the power requirement will be met easily.
Required probability = 1- ( 4C4 + 5C1 * 4C3 )/330 = 1- 21/330 = 309/330 = 0.9363
In order for any SIPR access to occur, there must be adequate power generation. The Brigade...
I have this case study to solve. i want to ask which type of case study in this like problem, evaluation or decision? if its decision then what are the criterias and all? Stardust Petroleum Sendirian Berhad: how to inculcate the pro-active safety culture? Farzana Quoquab, Nomahaza Mahadi, Taram Satiraksa Wan Abdullah and Jihad Mohammad Coming together is a beginning; keeping together is progress; working together is success. - Henry Ford The beginning Stardust was established in 2013 as a...