Question

A 33 kV power cable 7 km long has a capacitance of 0.32 uF/km and a conductance associated with its insulation of 5 LS /km. I

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Given

Length = 7km

Capacitance = 0.32×10-6F/Km

Total capacitance (C)= 0.32×10-6×7=2.24×10-6 F

Coductance=5×10-6S/km

Total conductance (g)=5×10-6×7 = 35×10-6 S

Resistance R= 1/g= 1/[35×10-6]=0.0285714×106 ohm

a) tan\delta= 1/WRC

W= 2πf= 2×π×50= 314.16 rad/s

Tan\delta= 1/(314.16×0.0285714×106×2.24×10-6)=0.0497

\therefore tan\delta= 0.0497

b) power dissipation = WCV​2\delta

\delta= tan\delta=0.0497 and V = Phase voltage = 33/√3 kV= 19.0525kv

powerdissipation = 314.26×2.24×10-6×19.05252×106×0.0497

= 12699.81 Watts

Power dissipation = 12699.81 W

​​​

Add a comment
Know the answer?
Add Answer to:
A 33 kV power cable 7 km long has a capacitance of 0.32 uF/km and a...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • . A single core concentric cable 6 km long has a capacitance of 0.22 ut per...

    . A single core concentric cable 6 km long has a capacitance of 0.22 ut per km, the relative permittivity of the dielectric being 3.0. The diameter of the inner conductor is 1.4 cm and the supply voltage is 69 kV at 60 Hz. Calculate the outer diameter of the cable, the voltage gradient at the surface of the inner conductor and the charging current

  • Phase of a three-phase, 60 Hz, 300 km long power transmission line with a nominal operating...

    Phase of a three-phase, 60 Hz, 300 km long power transmission line with a nominal operating line voltage of 500 kV. its inductance per 291 mH/phase, and its capacitance is 3.45uF/phase. Voltage between 500 kV phases from the end of the energy transmission line Under it, a load of 1000 MVA is fed with a power factor of 0.8 back. Power transmission line lossless assumption. This according to the operating conditions, a.) The line's phase constant (61), characteristic impedance (ZC)...

  • 3.8 A 275 kV three-phase transmission line of length 96 km is rated at 800 A....

    3.8 A 275 kV three-phase transmission line of length 96 km is rated at 800 A. The values of resistance, inductance and capacitance per phase per kilometre are 0.078 12, 1.056 mH and 0.029 F, respectively. The receiving-end voltage is 275 kV when full load is transmitted at 0.9 power factor lagging. Calculate the sending-end voltage and current, and the transmission efficiency, and com- pare with the answer obtained by the short-line representation. Use the nomi- nal n and T...

  • A long, lossless, three-phase transmission line is operating with 60 Hz with a nominal voltage of 400 kV. The distance between sending and receiving sides of the line is 350 km and the line’s series i...

    A long, lossless, three-phase transmission line is operating with 60 Hz with a nominal voltage of 400 kV. The distance between sending and receiving sides of the line is 350 km and the line’s series inductance and shunt capacitance per length per phase are 0.92 mH/km and 0.016µF/km, respectively.  If the line delivers 667.2461 MW at 400 kV with unity power factor at its receiving side, what would be the line-line voltage magnitude in the middle of the line?

  • A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters...

    A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters of r = 0.09 Ohm/km, x = 0.88 Ohm/km, y = 4.1 * 10^-6 s/km. Calculate the ABCD constants of this transmission line. What is the sending end voltage if the line is supplying rated voltage and apparent power at 0.85 PF lagging? What is the voltage regulation of the transmission line for the conditions in question 11. What is the efficiency of the...

  • A 220-kv, 150 MVA, 60-Hz three phase transmission line is 50 km long. The characteristic parameters...

    A 220-kv, 150 MVA, 60-Hz three phase transmission line is 50 km long. The characteristic parameters of the transmission line are r-0.05 2/km x-0.88 /km 1. The voltag at the reeioransmisson line is215 kV What is the suppling end voltage if the line is supplying rated voltage at unity PF? What is the voltage regulation of the transmission line? What is the efficiency of the transmission line? a. b. c.

  • A 3-phase, 50 Hz, long 300 Km transmission line delivers 60 MVA at 124 kV and...

    A 3-phase, 50 Hz, long 300 Km transmission line delivers 60 MVA at 124 kV and 0-8 p.f. lagging. The total resistance 25.3 ohm and total reactance is 66.5 ohm and the admittance due to capacitance is 0.442*10-3 mho. Determine: (i) (ii) (iii) A,B, C and D constants of long T.L Sending end voltage, current and power factor Transmission efficiency, Voltage regulation

  • A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters...

    A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters of r = 0.09 Ohm/km, x = 0.88 Ohm/km, y = 4.1*10^-6 S/km. What is the sending end voltage if the line is supplying rated voltage and apparent power at 0.85 PF lagging? What is the voltage regulation of the transmission line for the conditions in question 11.

  • A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters...

    A 220-kV, 150 MVA, 60-Hz, three-phase transmission line is 140 km long with the characteristic parameters of r = 0.09 ohm/km, x = 0.88 ohm/km, y = 4.1 * 10^-6 S/km. 10. Calculate the ABCD constants of this transmission line. 11. What is the sending end voltage if the line is supplying rated voltage and apparent power at 0.85 PF lagging? 12. What is the voltage regulation of the transmission line for the conditions in question 11. 13. What is...

  • 4-130%) A 60-Hz, 3-phase, 10-km long, fully transposed, 69-kV following conductor arrangement: 5 ...

    thank you and def thumps up. 4-130%) A 60-Hz, 3-phase, 10-km long, fully transposed, 69-kV following conductor arrangement: 5 m 8 m The conductors are made of solid aluminum with resistivity of 2.83-10* m at 20 °C, temperature coefficient of 0.39%"C, diameter of 250 mils (0.25 in), operating at 120 °C with skin effect ot 4.5%. (a) Obtain the series impedance per phase of the line. Zs (b) Obtain the shunt admittance to ground per phase of the line, the...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT