Question

The following figure shows the one-line diagram of a single power network which has the line admittances shown on the figure. Each generator connected to buses 1 and 4 has a sub-transient reactance of 0.25 pu. Determine for the network

a. Ybus

b. Zbus

c. The sub-transient current in per unit in a three-phase fault on bus 3 and

d. The contributions to the fault current from line 1-3 and from 4-3

૩૦.૦૬૦-૬ ૬ . ૦૩72 , 30.23 90.0372૬ ૬૦.૦૦૩% 350.25

0 0
Add a comment Improve this question Transcribed image text
Answer #1

0.0372 50-25 0.626025 _0.0120TE + L 0.25 + 1 0.0372 = 50.72 0.0504 50.72 ·25 0.03a Yize = -19.84 0.0504 13= 1 = -26.88 0.0312 Y = 412 = -19.84 9222 - AL -50.22 -19.84 -26.78 o 19.84 46.72 o -26.8 .-26.88 42.6 IS.AZ -26.88 15.72 46.66 (6) abus & stepte - Adding Bus (6 (Ground) tostop 4 & adding Bes to ou 3.0504 & 0.0322 27 - loer OiRT 0.25 0.25 025 0.3004 0.25 0.3604 025 0.25 0.2872 0.25 0-3004 025 0.1By Corners rule : Z-Z1-715251 455 Z122 Zz Zirk 212 et & so on.. Zan [2]buy ons oes ons 825 l5 - 025 0.25 0.25 0.25 6.3004 0.25. Cosis is : 0.14 0 12 0.1 0.14 0.14 0.12 0.1 0.13 0.14 0.14 0.18 0.ll Bill 6.13 0.11 0.14 (6 or fault Canent on bus 3i- afs2® NEU - (-35.dion) - 12:0.3328 {q® - Vef. 168(-:-<6) (...) - Upt 0.3894 Redrawing Roone vagram 0.25 20.0372 & 0.0636 80.25 *+ 3 floud analysise-cē bu) Consides a simple power System Consisting of Connected to apptor through a lie Generator 30 fautNxti between o open circuit weltage LG je pre facet willage 9 I Reactance dragham + * Power System 2 y com 2th = org | ; (Ym+Io nebus system upava (842n] [v+] by : [v] bue & [ 2 ] [F] was tn 24... 2 2 Z tuyen 2. 2 ..2 , --- Sauet bus Zhu satria prefa2 V. VE V8 = Pf tor + Vf Vgo - Effort afz V 24 (2 423) try at

Add a comment
Know the answer?
Add Answer to:
The following figure shows the one-line diagram of a single power network which has the line...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 3- The bus impedance matrix of a four-bus network with values in per unit is Z???...

    3- The bus impedance matrix of a four-bus network with values in per unit is Z??? = [?0.15 ?0.08 ?0.04 ?0.07 ?0.08 ?0.15 ?0.06 ?0.09 ?0.04 ?0.06 ?0.13 ?0.05 ?0.07 ?0.09 ?0.05 ?0.12 ] Generators connected to busses 1 and 2 have their sub-transient reactances included in Zbus. Neglect pre-fault currents and find sub-transient current in pu in the fault for a three-phase fault on bus 4. Assume the voltage at fault is 1∠0 before the fault occurs. Also, find...

  • The one-line diagram of a three-bus power system is shown in Figure 4. All impedances are...

    The one-line diagram of a three-bus power system is shown in Figure 4. All impedances are expressed in per unit on a common MVA base. All resistances and shunt capacitances are neglected. Information on each component in this system is given below: • Each generator is represented by an emf behind the sub-transient reactance of j0.045 and their neutrals are connected to the ground. • Line 1-2 has reactance of j0.88 • Line 2-3 has reactance of j0.65 • Line...

  • The single-line diagram of a three-phase power system is shown. Equipment ratings are given as follows

    The single-line diagram of a three-phase power system is shown. Equipment ratings are given as follows: The inductor connected to generator 3 neutral has a reactance of \(0.05\) pu using generator 3 ratings as a base.1. Draw the zero-, positive-, and negative -sequence  reactance diagrams using a \(1000 \mathrm{MVA}, 765 \mathrm{kV}\) base in the zone of line \(1-2\).2. Faults at bus 2 are of interest. Determine the Thevenin equivalent of each sequence network as viewed from the fault bus. Prefault voltage...

  • The single-line diagram of a four-bus system and its bus impedance matrix are shown below BUS...

    The single-line diagram of a four-bus system and its bus impedance matrix are shown below BUS 2 0.25 j0.2 0.125 0.25 0.4 BUS 3 BUS 1 BUS 4 j0.1 0.1 j0.2 j0.2 ground is the reference node) 0.25 0.2 0.16 0.14 0.2 0.23 0.15 0.151 ZBUs =기0.16 0.15 0.196 0.1 0.14 0.151 0. 0.195 A solid three-phase fault occurs at bus 2 of the network. (a) Calculate the initial symmetrical RMS current in the fault. (b) Determine the voltages during...

  • The one-line diagram of a simple power system is shown in Figure 1. The neutral of...

    The one-line diagram of a simple power system is shown in Figure 1. The neutral of each generator is grounded through a current-limiting reactor of 0.25/3 per unit on a 100-MVA base. The system data expressed in per unit on a common 100-MVA base is tabulated below. The generators are running on no-load at their rated voltage and rated frequency with their emfs in phase. Determine the fault current for the following faults giving Zo = 0.35, Z = 0.22...

  • 2. The Fig. P2.1 shows the one-line diagram of a simple four-bus system. Table P2.1 gives...

    2. The Fig. P2.1 shows the one-line diagram of a simple four-bus system. Table P2.1 gives the line impedances identified by the buses on which these terminate. The shunt admittance at all the buses is assumed negligible (a) Convert the network impedances to admittances. (b) Obtain the bus admittance YBUS assuming that the line shown dotted is not connected. (c) (i) What modifications need to be carried out in YBUS if the dotted line is now connected. (ii) Obtain the...

  • A single line diagram of a power system is shown in Fig. 2. The system data with equipment ratings and assumed sequence reactances are given the following table. The neutrals of the generator and A-Y...

    A single line diagram of a power system is shown in Fig. 2. The system data with equipment ratings and assumed sequence reactances are given the following table. The neutrals of the generator and A-Y transformers are solidly grounded. The motor neutral is grounded through a reactance Xn 0.05 per unit on the motor base. Assume that Pre-fault voltage is takin as VF-1.0 ,0° per unit and Pre- fault load current and Δ-Y transformer phase shift are neglected In the...

  • PLEASE SOLVE THIS POWER / LOAD FLOW 07-Elec-B December 2016 Page 7 of 7 Problem 7...

    PLEASE SOLVE THIS POWER / LOAD FLOW 07-Elec-B December 2016 Page 7 of 7 Problem 7 Consider the system shown in the single-line diagram of Figure (5). Here, a 60-Hz synchronous generator having a transient reactance of 0.15 pu. is connected to an infinite bus through a transformer whose reactance is 0.1 p. u. and a double circuit transmission line with circuits having a reactance of 0.6 p.u each as indicated in the figurc. The generator delivers a real power...

  • Figure 1 Single line diagram b2 b3 b1 b4 grid Τι 13 A power system single line diagram is shown...

    Figure 1 Single line diagram b2 b3 b1 b4 grid Τι 13 A power system single line diagram is shown in Figure 1. The single line diagram shows a synchronous generator G connected to a large 50 Hz grid via its unit transformer T and a network of three transmission lines. Relevant details of the grid, transformer, generator and overhead lines are provided in Tables I,II,II & IV respectively. A double line to ground fault occurs at bus 3 Questions....

  • The Fig. P1.1 is a one-line diagram of a simple power system. There prefault system is...

    The Fig. P1.1 is a one-line diagram of a simple power system. There prefault system is on no-load with 1.0 pu voltage and prefault currents are zero. A BOLTED THREE-PHASE FAULT occurs at point P. (a) Draw the pre-fault single-phase equivalent circuit showing numerical values. (b) (i) Calculate the subtransient current in the fault (ii) Calculate the voltages at the busses during the fault. (iii)Calculate the e subtransient current in the lines. (c)) Determine the Zbus relating the bus currents...