111-find the magnitude and phase of the impedance where V=(16+j8)V and current =(3-j12)A

111b-An ac power system has the following loads connected: load1=400W at 0,8pf lagging,Load 2=200VAr at pf 0,8 lagging and load 3=250VA at 0,70pf lagging

calculate the total active power, reactive power and apparent power for the given ac power system

0 0
Add a comment Improve this question Transcribed image text
Answer #1

(G418) C3e2) VOltage 16ti8 fmpedance 3-j2 (3jiai Cunent 48-96t1 (244 192) -484j216 9+144 153 - 1.447180-141 ,S.001-7M-1 magnieactve power Qit 2t Q2 Total 300+ 200ot 118-534 618.536 VAR To tal appavent fower Crota t jototal 841. 664j 678. 536 UA 2 lo8

Add a comment
Know the answer?
Add Answer to:
111-find the magnitude and phase of the impedance where V=(16+j8)V and current =(3-j12)A 111b-An ac power...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A three phase line has an Impedance of 0.4+j2.7 Ω per phase. The line feeds two...

    A three phase line has an Impedance of 0.4+j2.7 Ω per phase. The line feeds two balanced three phase loads that are connected in parallel. The first load is absorbing 560.1kVA @ PF=0.707 lagging and the second load absorbs 132kW @ PF=1. The line-to-line voltage at the load side is 3810.5/_30° V. Determine: a) The magnitude of the line voltage at the source side b) Total active & reactive power loss in the line c) Active and reactive power at...

  • The impedance of a three-phase line is 0.3 + j 2.4 per phase. The line feeds...

    The impedance of a three-phase line is 0.3 + j 2.4 per phase. The line feeds two balanced three- phase loads connected in parallel. The first load takes 600 kVA at 0.7 p.f. lagging. The second takes 150 kW at unity power factor. The line to line voltage at the load end of the line is 3810.5 V. Find a) The magnitude of the line voltage at the source end of the line. b) The total active and reactive power...

  • I have seen similar examples of this question. However, for both 208V and 280V AC power...

    I have seen similar examples of this question. However, for both 208V and 280V AC power system, the line-to-line voltage seems to be the same which 120V and that does not make sense. Can you please justify that in the solution? A 280-V, 3Ø AC power system, Y-connected three-phase generator connected through a three-phase transmission line to a A-connected load. The transmission line has an impedance of (0.06+j0.12) S2/phase, and the load has an impedance of (12+j9) 92 per phase....

  • The following three-phase, balanced loads are connected across a three-phase, Y-connected 60 Hz source with a...

    The following three-phase, balanced loads are connected across a three-phase, Y-connected 60 Hz source with a line-to-line voltage of 480 V. The loads are described below: • Load 1: ∆-connected, total three-phase apparent power is 30 kVA at 0.95 power factor lagging. • Load 2: ∆-connected, total three-phase active power is 20 kW at 0.7 power factor lagging. • Load 3: Y-connected, phase current is 30 A, and power factor is 0.9 pf leading. (a) Calculate the total complex power...

  • 1 A single phase AC system Consider a single phase AC distribution system in which there...

    1 A single phase AC system Consider a single phase AC distribution system in which there a single home connected to a 10kVA service transformer. Let’s assume that the primary of the distribution transformer can be modeled as an ideal 240V (rms) AC source and that the effective impedance of the transformer is 2% resistance and 3% reactance. (See lecture notes for converting % to Ohms). Connected to the secondary of the transformer is 200 ft of #6 AWG aluminum...

  • A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel...

    A three-phase line with an impedance of (0.25+j1.25) ohms/phase supplies power to three balanced 3-phase parallel connected loads: • Load 1 absorbs a total of 125 kW and 100 KVAR • Load 2 is a delta-connected impedance load with (125+j 40)ohms/phase • Load 3 absorbs 120 kVA at 0.8 power factor (lagging) Given that the line-neutral voltage at the load end of the line is 2400 V, determine the magnitude of the line-to- line voltage at the source end of...

  • 2. A load is connected to a voltage of 1320 volts at 60 Hz. The load...

    2. A load is connected to a voltage of 1320 volts at 60 Hz. The load dissipates 100 kW with a 0.867 power factor. Specify the capacitance needed to correct the power factor to being 1. 3. Consider a circuit for a single-phase AC power system, where a 200 volt AC voltage source is delivering power to a loads. Find the true power, reactive power and apparent power delivered by 150 mA current (Impedance phase angle 0 = 30°) 3....

  • A 240V three phase power system supplies two loads in parallel: Load 1: measured line current...

    A 240V three phase power system supplies two loads in parallel: Load 1: measured line current 30A, power factor 0.85 lagging, and Load 2: measured power 10kW, reactive power -7.5kVar A. Determine the power factor of load 2. B. Determine the total real power (in kW), reactive power (in kVAR), apparent power (in kVA), power factor and line current (in A) of the two loads.

  • A three-phase line, which has an impedance of (2 + j4) Ω per phase, feeds two...

    A three-phase line, which has an impedance of (2 + j4) Ω per phase, feeds two balanced three-phase loads that are connected in parallel. One of the loads is Y- connected with an impedance of (30 + j40) Ω per phase, and the other is delta- connected with an impedance of (60 + j45) Ω per phase. The line is energized at the sending end from a 60-Hz, three phase, balanced voltage source of 120√3 V (rms, line- to-line). Determine...

  • Problem 1 A 3-phase, Y/Y system is supplied from a 450 V (line). The load impedance...

    Problem 1 A 3-phase, Y/Y system is supplied from a 450 V (line). The load impedance is 6tj 10 Ω/phase. Please do the following a) Draw the single-phase equivalent circuit of phase A b) Find the magnitude of all line and phase currents c) Find the real power delivered to the load d) Find the reactive power delivered to the load e) Find the apparent power delivered to the load f) Find the power factor of the load