Question

A 280-V, 3Ø AC power system, Y-connected three-phase generator connected through a three-phase transmission line to a A-conne

I have seen similar examples of this question. However, for both 208V and 280V AC power system, the line-to-line voltage seems to be the same which 120V and that does not make sense. Can you please justify that in the solution?
0 0
Add a comment Improve this question Transcribed image text
Answer #1

O mo A RT see RL RL agovim t вк, с Rp R, 0.06+j12r LI Árpuns For star comeuton R 12tjan V • 3 x V phare line I line Iphane fo28ov (nas) applies! acron load side also parallely cowweeetes Vac = Vab=&bc=2801 as they are SON a) Line current 3 Iphone = 2SI Loap.US P. load(active 12.546W SJON load 13 Velone I line wind : 13 x 280 x 32:33 foro (-36.86 5 – 9.405kW 1 Apparent powe

Add a comment
Know the answer?
Add Answer to:
I have seen similar examples of this question. However, for both 208V and 280V AC power...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A balanced A-connected load of Z,=12+39.0 12 is connected to a power supply via a transmission...

    A balanced A-connected load of Z,=12+39.0 12 is connected to a power supply via a transmission line with impedance of Zrl=0.6+j2.5 12, find Transmission Lines o 20820 V AC 2084(0–240°) v umaza 10 AC 2084(0-120°) v mm | za | Three-Phase 208 V, 60 HZ Power Supply Three-Phase A-Connected Balanced Load @@OGO E the load line and phase voltages (magnitude and angle), the load line and phase currents (magnitude and angle), the total load's real, reactive, and apparent powers, the...

  • 111-find the magnitude and phase of the impedance where V=(16+j8)V and current =(3-j12)A 111b-An ac power...

    111-find the magnitude and phase of the impedance where V=(16+j8)V and current =(3-j12)A 111b-An ac power system has the following loads connected: load1=400W at 0,8pf lagging,Load 2=200VAr at pf 0,8 lagging and load 3=250VA at 0,70pf lagging calculate the total active power, reactive power and apparent power for the given ac power system

  • 1) Figure- generator is producing a line voltage of 480 V, and the line impedance is...

    1) Figure- generator is producing a line voltage of 480 V, and the line impedance is 0.09 + j0.16 . Load 1 is Y connected, with a phase impedance of 2.5236.87° 0 and load 2 is A connected, with a phase impedance of 54-20° n. shows a three-phase power system with two loads. The A-connected 2 0.09 j0.16 n w Vca= 4802-240° V + Vab = 48020 V Vhc = 480-120° V 0.09 j0.16 0.09 j0.16 Load 1 Load 2...

  • 3. A 345-KV, three-phase transmission line delivers 500MVA, 0.866 power factor lagging, to a three phase...

    3. A 345-KV, three-phase transmission line delivers 500MVA, 0.866 power factor lagging, to a three phase wve-connected load connected to its receiving-end terminals, the voltage at the receiving end is 345kV. a) Find the complex load impedance per phase. b) Find the real and reactive power per phase. 15 pts.

  • Problem 3ph [10 pts]: Y-connected source: A Y-connected balanced three-phase source is feeding a ...

    Please show how this transformers problem is done. Thanks! Problem 3ph [10 pts]: Y-connected source: A Y-connected balanced three-phase source is feeding a balanced three-phase load (it doesn't matter whether the load is Y or Delta connected). The voltage and current of the source are: van (t) - 340 sin (377t + 0.5236) ia(t) 100sin (377t 0.87266) Calculate the following: (a) The rms phase voltage (Van, magnitude and phase). (b) The rms line-to-line voltage (Vab, magnitude and phase) (c) The...

  • 12. For a three-phase balanced system, a generator serves a remote load through two parallel tran...

    12. For a three-phase balanced system, a generator serves a remote load through two parallel transmission lines with 4 transformers. The system parameters are as follows: Generator: T1: (A-Y, with Y side voltage leading) T2: (A-Y, with Y side voltage leading) T3: (A-Y, with Y side voltage leading) T4: (A-Y, with Y side voltage leading) Line-1 Line-2 Load 100MVA, 21kV, x-0.15pu 120MVA, 20Д/165Y kV, x-O.12pu 80MVA, 20A/1 10Y kV, x-O.1pu 120MVA, 165A/33Y kV, x-0.12pu 80MVA, 11ОД/33Y kV, x-O.1pu 30+j100 O...

  • EXPLAIN THESE QUESTIONS WITH THE HELP OF DIAGRAMS AND LABEL DIAGRAMS IN SUCH A WAY THAT...

    EXPLAIN THESE QUESTIONS WITH THE HELP OF DIAGRAMS AND LABEL DIAGRAMS IN SUCH A WAY THAT I CAN EASILY UNDERSTAND WHAT WE ARE FINDING AND HOW WE ARE FINDING THE REQUIRED THINGS .I AM POSTING MY QUESTION 4TH TIME PLEASE DONOT WASTE IT AND PLEASE DO ALL STEPS I NEED MY ANSWER STEP BY STEP by the line Two balanced Y-connected loads, one drawing 10 kW at 0.8 power factor lagging and the other 15 kW at 0.9 power factor...

  • I am having trouble with 3.20, 3.19 is included for the information. any help would be...

    I am having trouble with 3.20, 3.19 is included for the information. any help would be awesome, thanks. 3.19 A 345-kV, three-phase transmission line delivers 500 MVA, 0.866 power factor lagging, to a three-phase load connected to its receiving-end terminals. Assume that the load is Δ connected and the voltage at the receiving end is 345 kv. a. Find the complex load impedance per phase. Iculate the line and phase currents c. Find the real and reactive power per phase....

  • INTRODUCTION TO POWER SYSTEM

    1. The one-line diagram of a three-pha  se power system is shown in Figure 3.29. Select a common base of 100 MVA and 15 kV on the motor side. Draw an impedance diagram with all impedances including the load impedance marked in per-unit. The manufacturer's data for each device is given as follow:The three-phase load at bus 4 absorbs 57 MVA, 0.6 power factor lagging at 10.45 kV. Line 1 and line 2 have reactances of 48.4 Ω and 65.43...

  • The impedance of a three-phase line is 0.3 + j 2.4 per phase. The line feeds...

    The impedance of a three-phase line is 0.3 + j 2.4 per phase. The line feeds two balanced three- phase loads connected in parallel. The first load takes 600 kVA at 0.7 p.f. lagging. The second takes 150 kW at unity power factor. The line to line voltage at the load end of the line is 3810.5 V. Find a) The magnitude of the line voltage at the source end of the line. b) The total active and reactive power...