Question

Define the following flow terms, average daily flow, maximum day, peak hour, and minimum day. For each of these flow terms, provide at least two sample applications in the design and operation of wastewater treatment facilities. 6

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Average daily flow: the average of the daily volumes to be received for a continuous 12 month period expressed as a volume per unit time.The average daily flowrate is used in evaluating treatment plant capacity and in developing flowrate ratios use d in d i es gn

Maximum day: the largest volume of flow received during a continuous24 hour period expressed as a volume per unit time. The largest volume of flow anticipated to occur during a one-day period, expressed as a daily average. The maximum daily flowrate is important particularly in the design of facilities involving retention time such as e qualization basins.

Peak hour: peak hourly flow is the largest volumeof flow to be received during a one hour periodexpressed as a volume per unit time.Data on peak hourly flows are needed for the design of collection and interceptor sewers, wastewater-pumping stations, wastewate r flow meters, sedimentation tanks and channels in the treatment plant.

Minimum day:  the least volume of flow received during a continuous 24 hour period expressed as a volume per unit time. The smallest volume of flow anticipated to occur during a one-day period, expressed as a daily average. Minimum flow rates are important important in the sizing of the conduits conduits where solids deposition might occur at low flow rates.

Add a comment
Know the answer?
Add Answer to:
Define the following flow terms, average daily flow, maximum day, peak hour, and minimum day. For...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 9.9 Design an aerated grit chamber system to treat a 1-day sustained peak hourly flow of...

    9.9 Design an aerated grit chamber system to treat a 1-day sustained peak hourly flow of 1.6 m/s with an average flow of 0.65 m/s. See Table 9.4 for design guidance. Determine: a. The grit chamber volume (assuming two chambers will be used) b. The dimensions of the two grit chambers. c. The average hydraulic retention time in each grit chamber. d. Air requirements, assuming 0.20 m of air per m length of tank per minute. e. The quantity of...

  • Ex. 4 A water treatment plant with a maximum daily flow of 3 m/s (1.5 times...

    Ex. 4 A water treatment plant with a maximum daily flow of 3 m/s (1.5 times the average flow) is treating a surface water. The water is coagulated with alum and the alum floc was measured to have a settling velocity of 2.2 m/h at 10 °C. Design a horizontal-flow rectangular sedimentation system based on the maximum day flowrate. Include the number of basins, dimensions and criteria checks.

  • Any tips or pointers? characteristics: Maximum daily flow 3 ms Average daily flow 2 m'/s Coagulant...

    Any tips or pointers? characteristics: Maximum daily flow 3 ms Average daily flow 2 m'/s Coagulant Ferric chloride Overflow Rate 3.1 m/m2h It is needed to specify the number of sedimentation basins, the basin dimensions, hydraulic retention time, horizontal velocity and outlet weir loading rate. Assume necessary data. The following items are suggested to be in your design report Title page: Design Problem title, your name, date, etc... Abstract: Contains objective statement, summarize the ma Introduction: Introducing the problem subject...

  • answer both accurately. answer only if u know The needed fire flow is 76380 L/min which...

    answer both accurately. answer only if u know The needed fire flow is 76380 L/min which has to be sustained for 5 hours. Maximum daily demand is 1.62 m3/s. What is the design discharge? Answer: The population of a town is 20000, that is to be supplied with water by a pump. The average property hold 4 people. Each property consumes, on average 0.871/day. Historical data suggests a peak day factor of 1.8 and a peak hour factor of 22....

  • Water and Wastewater Treatment SP-WATER TREATMENT PLANT SEDIMENTATION BASIN Design a rectangular, horizontal flow sedimentation process...

    Water and Wastewater Treatment SP-WATER TREATMENT PLANT SEDIMENTATION BASIN Design a rectangular, horizontal flow sedimentation process for a water treatment plant for turbidity removal Design Maximum Day Flow-20,000 m2ld Two parallel sedimentation tank, each designed for half of the total flow Depth 4.5 m, Width 6 m, Surface Overflow Rate 50 m/day Chain and flight sludge collector will be used, hence the limiting width of 6 m. Minimum Hydraulic Retention Time (detention time) 2 hrs Maximum weir rate 250 m/day/m...

  • Primary clarifier is to be designed for a municipal wastewater treatment plant with a flow of 416...

    primary clarifier is to be designed for a municipal wastewater treatment plant with a flow of 4160 m/d and peak flow during the day of 3.10 times the average hourly flow. Pertinent data are: peak overflow rate 73.3 m/d.-m2, maximum peak weir loading 373 m3/d-m, and minimum tank depth 2.13 m. Determine: A. The clarifier diameter B. The side water deptlh C. The peak weir loading. Is it acceptable? D. The percent suspended solids removal on the basis of the...

  • The average flow rate at a small sewage treatment plant is 20,000 m3/d. Design rectangular primary...

    The average flow rate at a small sewage treatment plant is 20,000 m3/d. Design rectangular primary clarifier with a channel width of 6 m. Use minimum two clarifiers, an overflow rate of 40 m3/m2-day and a side water depth of 4 m.

  • 4.A two-phase signal system is to be designed for an isolated intersection with a peak hour tacto...

    Transportation Can correct the answer 4.A two-phase signal system is to be designed for an isolated intersection with a peak hour tactor 81 0.99. TIL lane volumes are: Phase A-550 veh/hr, Phase B 600 veh/hr, The total lost time L is 14 sec. Determine an appropriate cycle length for the intersection that will satisfy the following conditions: minimum cycle length-45 sec, maximum cycle length = 120 sec, maximum critical ve ratio (Xc)-0.85 and The saturation flow per lane for each...

  • Using the values provided in Table 21-1, minimum sewage elevation in interceptor of 112.60 m, maximum...

    Using the values provided in Table 21-1, minimum sewage elevation in interceptor of 112.60 m, maximum sewage elevation in interceptor of 112.80 m, discharge elevation to stilling well of 116.40 m, an average design flow of 8,600 m3/d, peaking factor for peak hour of 2.8 and minimum factor of 0.49. A. Determine the most efficient screw pump diameter (in m) B. How many flights are recommended C. How many pumps are recommended in the final design? Typical/comment TABLE 21-1 Typical...

  • A small coastal town in Queensland is subject to an increasing permanent population and also a...

    A small coastal town in Queensland is subject to an increasing permanent population and also a transient influx of tourists during the summer period. Council already receives frequent complaints of restricted water supply. The water supply system comprises a rising trunk main from the treatment plant A to the service reservoir B, the service reservoir, and service mains to the consumption areas. Two consumption areas C and D at different elevations are gravity supplied from the service reservoir. The service...