Question

Transformation Ratio not given for this question.

Three identical Y-connected resistors of 1.0/0° per unit form a load bank that is supplied from the low-voltage Y-side of a Y

0 0
Add a comment Improve this question Transcribed image text
Answer #1

- reko a supplied is from low voltage Side (y side) and we have to Calculate the line voltage and line Current on high voltagIa = n Iara Ian Taot Ia), t iah ot ( [45° + 0.56250° 1L4.5° I given 0.5 ( 250 here in po lale and -Phale In = 1 24.5+ 0.52200

Add a comment
Know the answer?
Add Answer to:
Transformation Ratio not given for this question. Three identical Y-connected resistors of 1.0/0° per unit form...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Draw schematic (connection) diagrams for three-phase Y-Y and Y-Δ connected transformers using three single-phase (50 VA,...

    Draw schematic (connection) diagrams for three-phase Y-Y and Y-Δ connected transformers using three single-phase (50 VA, 120V/25V) transformers you have previously worked with in the lab. Show proper dot markings for each configuration. I. 2. Find the line-line voltage ratio (VuVa) for each configuration. For a three-phase Δ-connected resistive load (25 Ω in each leg), connected on the transformer low voltage side, calculate the line current on each side of the transformer for each configuratio Is it safe to operate...

  • 5. The line to neutral voltages of a Y-connected three phase source are given by, The...

    5. The line to neutral voltages of a Y-connected three phase source are given by, The above three phase source is directly connected to a delta connected balanced three phase resistive load. The resistance in each phase is 10 ohms. Calculate the current phasor 0. Answer- 4. Following three loads are connected in parallel across a single-phase source voltage source: Load 1 absorbs 15 kW and 6.667 kvar; Load 2 absorbs 3 kVA at 0.96PF leading; Load 3 absorbs 15...

  • solve no: 3.14 , 3.16, 3.19 please show each step and solve for beginners 120 Power...

    solve no: 3.14 , 3.16, 3.19 please show each step and solve for beginners 120 Power System Analysis 3.12. A single-phase system similar to that shown in Figure 3.11 has two transformers A-B a B-C connected by a line B feeding a load at the receiving end C. The ratings and parame ter values of the components are 500 V/1.5 kV, 9.6 kVA. leakage reactance 5 % 1.2 kV/120 V, 7.2 kVA, leakage reactance 4 % series impedance (0.5 +...

  • A 400-MVA, 200-kV/20-kV, three phase Y-Y transformer has an equivalent series impedance of ZTL = 0.012...

    A 400-MVA, 200-kV/20-kV, three phase Y-Y transformer has an equivalent series impedance of ZTL = 0.012 + 20.0162 per phase referred to the low-voltage side (secondary side). The transformer is supplying a three-phase load of 300-MVA, 0.8 power factor lagging at terminal voltage of 20 kV (line-to-line) on its low-voltage side (secondary side) as shown in Fig. 22. The primary is supplied from a transmission line with an impedance of ZL = 0.5 + j1.0 per phase. The line-to-neutral load...

  • Solvein pu sysvem 2-10. A 13,800/480 V three-phase Y-A-connected transformer bank consists of thr...

    please solve the question in pu sysyem !!!! Solvein pu sysvem 2-10. A 13,800/480 V three-phase Y-A-connected transformer bank consists of three identical 100-kVA 967/480-V transformers. I is supplied with power directly from a large constant-voltage bus. In the short-circuit test, the recorded values on the high-voltage side for one of these transformers are Isc 12.6 A Pc3300 w (a) If this bank delivers a rated load at 0.85 PF lagging and rated voltage, what is the line-to-line voltage on...

  • Fig Qshows the one-line diagram of a three-phase power system. As shown in Fig. Q3. the...

    Fig Qshows the one-line diagram of a three-phase power system. As shown in Fig. Q3. the two zones are connected by a 400 MVA, 240-kV/24-kV, Ý-A three phase transformer. The Y-A three phase transfonmer has an equivalent series impedance of ZTH - 1.2 + j1.6n per phase referred to the high voltage side (primary side). The three-phase power system can be studied with per unit quantities using base values of S-500 MVA and 240 kV in zone 1. By using...

  • A three-phase generator connected in a star generates a phase voltage of Vθ = 24 KVrms and supplies a three-phase transformer connected in star. The transformation ratio is 115: 1. Each of the three c...

    A three-phase generator connected in a star generates a phase voltage of Vθ = 24 KVrms and supplies a three-phase transformer connected in star. The transformation ratio is 115: 1. Each of the three coils of the secondary transformer feed 3 equal charges each composed of them by R = 18Ω, XC = 2Ω and XL = 20Ω. a) Calculate the phase, line and charge currents after the b) Calculate the phase, line and load voltages c) Calculate the Apparent...

  • ‏Please I need an answer to all questions 46) 46) In a Y-connected source feeding a...

    ‏Please I need an answer to all questions 46) 46) In a Y-connected source feeding a A-connected load: A) each phase of the load has one-third of the full line voltage across it. b) each phase of the load has a voltage across it equal to V times the line voltage C) each phase of the load has the full line voltage across it. D) each phase of the load has two-thirds of the full line voltage across it. 47)...

  • 8.25 A three-phase balanced Y-connected load with series impedances of

    8.25 A three-phase balanced \(Y\) -connected load with series impedances of \((8+j 24) \Omega\) per phase and mutual impedance between any two phases of \(j 4 \Omega\) is supplied by a three-phase unbalanced source with line-to-neutral voltages of \(V_{a n}=200 \angle 25^{\circ}, V_{b n}=100 \angle-155^{\circ}\), \(V_{c n}=80 \angle 100^{\circ} \mathrm{V}\). The load and source neutrals are both solidly grounded. Determine: (a) the load sequence impedance matrix, (b) the symmetrical components of the line-toneutral voltages, (c) the symmetrical components of the...

  • QUESTION 3 A 200 - MVA, 15/200 kV single-phase power transformer has a per – unit...

    QUESTION 3 A 200 - MVA, 15/200 kV single-phase power transformer has a per – unit resistance of 1.2 percent and a per-unit reactance of 5 percent (data taken from the transformer's nameplate). The magnetizing impedance is impedance is j80 per unit. a. Find the equivalent circuit referred to the low-voltage side of this transformer. b. Calculate the voltage regulation of this transformer for a full-load current at power factor of 0.8 lagging. c. Assume that the primary voltage of...