Question

Fig Qshows the one-line diagram of a three-phase power system. As shown in Fig. Q3. the two zones are connected by a 400 MVA, 240-kV/24-kV, Ý-A three phase transformer. The Y-A three phase transfonmer has an equivalent series impedance of ZTH - 1.2 + j1.6n per phase referred to the high voltage side (primary side). The three-phase power system can be studied with per unit quantities using base values of S-500 MVA and 240 kV in zone 1.

By using the common base of 500 MVA and 240 kV in zone 1. calculate a. The base value of the voltage in zone 2. [1 Mark] b. The base value of the inpedance in zone 1. [1 Mark] c. The base value of the impedance in zone 2. [1 Mark] d. All impedances including the load impedance in per-unit. [3 Marks]. By neglecting the American standard phase shift, and assuming that the line-to-line load voltage Vioad is equal to 22 kV: a. Draw the per-unit equivalent circuit. [2 Marks] b. Determine the per unit value of the current supplied by the generator; give your answer in polar form. [1 Mark]. c. By choosing the line-to-neutral load voltage as a reference, find the phasor voltage

in Time 1hour. 29 minutes 10 seconds Question completos A 400-MVA, 200-V 20-5V, three phase Y-Y transformer has an equivalent

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Greetings of the day

20 kV k Zone I R Zone 2 20 - 115.22 2 Base = 2.083 KA Zg: 0.8+51.0 Iload 20020 300 MVA 400 MVA 0.8 pf 0.012, toolbe Noad = 20pu © I lood = 15 2-36.87 °KA (Iload) pu = 0.12 23627/ (6 (IP), (I Load pu = 0.7 2 2 -36.8t pu Road = 0.7698 236.87° (d) Zin (

Add a comment
Know the answer?
Add Answer to:
Fig Qshows the one-line diagram of a three-phase power system. As shown in Fig. Q3. the...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • Fig. Q3 shows the one-line diagram of a three-phase power system. As shown in Fig. 23,...

    Fig. Q3 shows the one-line diagram of a three-phase power system. As shown in Fig. 23, the two zones are connected by a 400 MVA, 240-kV/24-kV, Y-A three phase transformer. The Y-three phase transformer has an equivalent series impedance of 2T - 1.2 + |1.6 per phase referred to the high-voltage side (primary side). The three-phase power system can be studied with per unit quantities using base values of So=500 MVA and 240 kV in zone 1. 2 -1.61253.15" Line...

  • A 400-MVA, 200-kV/20-kV, three phase Y-Y transformer has an equivalent series impedance of ZTL = 0.012...

    A 400-MVA, 200-kV/20-kV, three phase Y-Y transformer has an equivalent series impedance of ZTL = 0.012 + 20.0162 per phase referred to the low-voltage side (secondary side). The transformer is supplying a three-phase load of 300-MVA, 0.8 power factor lagging at terminal voltage of 20 kV (line-to-line) on its low-voltage side (secondary side) as shown in Fig. 22. The primary is supplied from a transmission line with an impedance of ZL = 0.5 + j1.0 per phase. The line-to-neutral load...

  • INTRODUCTION TO POWER SYSTEM

    1. The one-line diagram of a three-pha  se power system is shown in Figure 3.29. Select a common base of 100 MVA and 15 kV on the motor side. Draw an impedance diagram with all impedances including the load impedance marked in per-unit. The manufacturer's data for each device is given as follow:The three-phase load at bus 4 absorbs 57 MVA, 0.6 power factor lagging at 10.45 kV. Line 1 and line 2 have reactances of 48.4 Ω and 65.43...

  • 3) The single-line diagram of a three-phase power system is shown in Fig. 1. Equipment ratings...

    3) The single-line diagram of a three-phase power system is shown in Fig. 1. Equipment ratings are given as follows: G1 1,000 MVA, 15.0 kV, 20.18, o 0.07 pu G2 : 1,000 MVA. 15.0 kV, 攻=エ1 =エ2 = 0.20, ro = 0.10 pu G3 : 500 MVA, 13.8 kV. 1" = 띠 z2 = 0.15, zo 0.05 pu G4 : 750 MVA, 13.8 kV. ェd =ェ1 = 0.30, T2 = 0.40 ro = 0.10 pu Ti : 1,000 MVA. 15.0Δ/765Y...

  • The diagram shows one phase of a 3-phase generation and distribution system. We would like to...

    The diagram shows one phase of a 3-phase generation and distribution system. We would like to determine the 12 kV short circuit (maximum) current at the indicated location attributed to the generation, in the event of a fault. For this question, we work in the per unit pu system. a. We pick S(base)=100 MVA, and V(base) = 12 kV. Then I(base) and Z(base) are fixed. The 12 kV of the transformer secondary is line-neutral voltage since this is a grounded...

  • The three-phase power and line-line ratings of the electric power system shown in Figure 2 are...

    The three-phase power and line-line ratings of the electric power system shown in Figure 2 are given below. T1 T2 V. 1 2 vm 9 Line G M Figure 2 One-line diagram for problem 2 G: T1: 60 MVA 50 MVA 50 MVA T2: Line: M: 20 kV 20/200 kV 200/20 kV 200 kV 18 kV X=9% X=10% X=10% Z=120+j200 12 X=8% 43.2 MVA (a) Draw an impedance diagram showing all impedances in per unit on a 100-MVA base. Choose...

  • solve no: 3.14 , 3.16, 3.19 please show each step and solve for beginners 120 Power...

    solve no: 3.14 , 3.16, 3.19 please show each step and solve for beginners 120 Power System Analysis 3.12. A single-phase system similar to that shown in Figure 3.11 has two transformers A-B a B-C connected by a line B feeding a load at the receiving end C. The ratings and parame ter values of the components are 500 V/1.5 kV, 9.6 kVA. leakage reactance 5 % 1.2 kV/120 V, 7.2 kVA, leakage reactance 4 % series impedance (0.5 +...

  • The three-phase power and line-line ratings of the electric power system shown in Figure 2 are...

    The three-phase power and line-line ratings of the electric power system shown in Figure 2 are given below T2 2 Line Vm G M 1 BA Figure 2 One-line diagram for problem 2 G: Ti: T2: Line: M: 60 MVA 50 MVA 50 MVA 20 kV 20/200 kV 200/20 kV 200 kV 18 kV X=9% X=10% X=10% Z=120+j2002 X=8% 43.2 MVA (a) Draw an impedance diagram showing all impedances in per unit on a 100-MVA base. Choose 20 kV as...

  • 2 - The three-phase power and line-line ratings of the electric power system shown in Figure...

    2 - The three-phase power and line-line ratings of the electric power system shown in Figure 2 are given below. Ti T2 VA Line 2 G M Vm BE BE Figure 2 One-line diagram for problem 2 G: T: T2: Line: M: 60 MVA 50 MVA 50 MVA 20 kV 20/200 kV 200/20 kV 200 kV 18 kV X=9% X=10% X=10% Z=120+j2002 X=8% 43.2 MVA (a) Draw an impedance diagram showing all impedances in per unit on a 100-MVA base....

  • the single-line diagram of a three-phase power system is shown in figure 9.17. equipment ratings are...

    the single-line diagram of a three-phase power system is shown in figure 9.17. equipment ratings are given as follows: The inductor connected to Generator 3 neutral has a reactance of 0.05 per unit using generator 3 ratings as a base. Draw the zero-, positive-, and negative-sequence reactance diagrams using a 1000-MVA, 765-kV base in the zone of line 1-2. Neglect the Δ—Y. transformer phase shifts.