Question

A 60 Hz, balanced three-phase source is connected to a balanced load of 2815 kVA at 0.95 pf lagging through a short transmiss

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Corø=0.95 lag ::$ = 18.1948 al s = √3 V, IL I = 2815.k i 33 x 25k IL = 65.0096 Al c b) Zis 65.00962-18.19 1134 la Uspn = Vepu

If you have any doubt please make a comment. Thank you

Add a comment
Know the answer?
Add Answer to:
A 60 Hz, balanced three-phase source is connected to a balanced load of 2815 kVA at...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • The following three-phase, balanced loads are connected across a three-phase, Y-connected 60 Hz source with a...

    The following three-phase, balanced loads are connected across a three-phase, Y-connected 60 Hz source with a line-to-line voltage of 480 V. The loads are described below: • Load 1: ∆-connected, total three-phase apparent power is 30 kVA at 0.95 power factor lagging. • Load 2: ∆-connected, total three-phase active power is 20 kW at 0.7 power factor lagging. • Load 3: Y-connected, phase current is 30 A, and power factor is 0.9 pf leading. (a) Calculate the total complex power...

  • 1. A three-phase, 5 kVA, 208 V, four-pole, 60 Hz, wye-connected synchronous machine has...

    A three-phase, 5 kVA, 208 V, four-pole, 60 Hz, wye-connected synchronous machine has negligible stator winding resistance and a synchronous reactance of 8 Wper phase. It is operated in parallel with a three-phase, 208 V, 60 Hz power supply.Determine the excitation voltage and the power angle when the machine is delivering rated kVA at 0.8 pf lagging. Draw the phasor diagram

  • A three-phase load of 15 kVA with a PF of 0.8 lagging is connected in parallel...

    A three-phase load of 15 kVA with a PF of 0.8 lagging is connected in parallel with a three-phase load of 36 kW at 0.6 PF leading. The line-line voltage is 2000V. a) Find the total complex power and power factor. Is it inductive or capacitive? b) How much kVAR is needed to make the PF unity? c) What is the magnitude of the current going into the total load?

  • 1, Two balanced three-phase loads are in parallel. Load 1 draws 10 kW at 0.8 PF...

    1, Two balanced three-phase loads are in parallel. Load 1 draws 10 kW at 0.8 PF lagging Load 2 draws 20 kVA at 0.6 PF leading a. b. The loads are supplied by a balanced three-phase 480 Vu source. (a) Draw the power triangle for the combined load. (b) Determine PF of the combined load. (c) Determine the magnitude of the line current from the source. (d) Y-connected inductors are now installed in parallel with the combined load. What value...

  • QUESTION 6 (MULTI-PHASE SYSTEMS) A 400 v, 50 Hz, three-phase distribution system supplies a 20 kVA, three-phase induction motor load at a power factor of 0 8 lagging, and a star-connected set of...

    QUESTION 6 (MULTI-PHASE SYSTEMS) A 400 v, 50 Hz, three-phase distribution system supplies a 20 kVA, three-phase induction motor load at a power factor of 0 8 lagging, and a star-connected set of impedances, each having a resistance of 10 Ω and an inductive reactance of 8 Ω Calculate the capacitance of delta-connected capacitors required to improve the overalil power factor to 0 95 lagging [14] TOTAL 1001 QUESTION 6 (MULTI-PHASE SYSTEMS) A 400 v, 50 Hz, three-phase distribution system...

  • A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.5Q/phase and a...

    A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.5Q/phase and a synchronous reactance of 5Q/phase. The generator is supplying its rated power at its rated voltage and at a power factor lagging. The rotational loss is 2 kW. Calculate: (a) the power developed, (b) the power angle, (c) the voltage regulation, and (d) the shaft torque. A 1500-kVA, 6.6 kV, 50 Hz, 6-pole, three-phase, star-connected synchronous generator has a resistance 0.50/phase and a synchronous...

  • A balanced positive-sequence wye-connected 60-Hz three-phase source has line-to-line voltages of VL = 440 V rms....

    A balanced positive-sequence wye-connected 60-Hz three-phase source has line-to-line voltages of VL = 440 V rms. This source is connected to a balanced wye-connected load. Each phase of the load consists of a 0.5-H inductance in series with a 50-Ω resistance. Assume that the phase of Van is zero. home / study / engineering / electrical engineering / electrical engineering questions and answers / A Balanced Positive-sequence Wye-connected 60-Hz Three-phase Source Has Line-to-line Voltages ... Question: A balanced positive-sequence wye-connected...

  • of shagah Name 120 96] Proble m 1: A balanced Y. connected, 50-Hz abc source is...

    of shagah Name 120 96] Proble m 1: A balanced Y. connected, 50-Hz abc source is connected to the following loads via 0.5+0.25 j 0/phase line. A Y-connected 900 kVA at 0.7 pf lagging load. · A ?-connected 500 kw at 0.6 pf lagging load. A Y-connected 350 kVAR at 0.7 pf lagging load. · 4-connected 600 kW at 0.6 pf lagging load. A Part 1: If the load voltage is always kept at 11 kV a) what is the...

  • Problem 3ph [10 pts]: Y-connected source: A Y-connected balanced three-phase source is feeding a ...

    Please show how this transformers problem is done. Thanks! Problem 3ph [10 pts]: Y-connected source: A Y-connected balanced three-phase source is feeding a balanced three-phase load (it doesn't matter whether the load is Y or Delta connected). The voltage and current of the source are: van (t) - 340 sin (377t + 0.5236) ia(t) 100sin (377t 0.87266) Calculate the following: (a) The rms phase voltage (Van, magnitude and phase). (b) The rms line-to-line voltage (Vab, magnitude and phase) (c) The...

  • A balanced Y-connected voltage source is applied to a balanced A-connected load with Zad (45-j30) ohm/phase...

    A balanced Y-connected voltage source is applied to a balanced A-connected load with Zad (45-j30) ohm/phase connected, 150 kVA transformer. According to the rating of the transformer, which is on a reactance of the transformer is j0.8 per unit (ignore the magnetizing branch impedances) LOAD 13.2kV 480V Z j0.8 pu a) Utilizing a three-phase Stue of 100 kVA and transformer voltages as bases, draw the single phase b) What does the voltage (V) at the source to need to be...

ADVERTISEMENT
Free Homework Help App
Download From Google Play
Scan Your Homework
to Get Instant Free Answers
Need Online Homework Help?
Ask a Question
Get Answers For Free
Most questions answered within 3 hours.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT