Fresh air at 3200 cfm, 41oC and 30% rh is mixed with recirculated air at 24oC and 50% rh. The mixed air stream temperature is 32oC. The mixed air stream is then cooled, dehumidified and reheated to 16oC and 40% rh.
The cooling is provided with a multi-stage vapor compression refrigeration system using R717 as the working fluid. The evaporator temperature is 12oC less than the air temperature leaving the cooling coil and the condenser temperature is 12oC higher than the fresh air temperature. The intermediate pressure is selected such that the temperature in the flash tank is the average of the evaporator and condenser temperatures. Assume that the refrigeration system is ideal except for the compressor efficiencies, which are 67%.
Determine:
Fresh air at 3200 cfm, 41oC and 30% rh is mixed with recirculated air at 24oC...
An Conference Center is to be air-conditioned for a seating capacity of 3200 people for the following outdoor and comfort conditions a) Outdoor design conditions = 35 °C, db and 65% R.H b) Indoor/return design conditions-26 deg C. db and 55% RH. c) Total sensible room load = 420,000 kJ/hr d) Total latent room load = 200,000 KJ/hr e) The rise in dry bulb temperature of the air inside the conference center is limited to 9 °C (i.e. the Supply...
A two-stage compression refrigeration system with an adiabatic liquid-vapor separation unit uses refrigerant-134a as working fluid. The system operates the evaporator at 0.4 MPa, the condenser at 1.6 MPa, and the separator at 0.8 MPa. The compressors use 25 kW of power. Given that the refrigerant is saturated liquid at the inlet of each expansion valve and saturated vapor at the inlet of each compressor, and the compressors are isentropic: (0) show the process on a T-s diagram; ) calculate...
o question: An airconditioned space is to be maintained at 26 C dry bulb temperature and 50% RH. The ambient condition is 4 27.78 kW and the latent load is 11.11 kW. 60% of the return air mass is recirculated and mixed with 40% of make-up fresh air before entering the AHU. Calculate: Room SHF -Supply flow rate (m'/sec) (assume supply temperature is 10 C lower than space's) Apparatus sensible and latent load Apparatus sensible heat factor, dew point, and...
1. An industrial freezer uses a multi-stage vapor-compression cycle with R-134a as the working fluid. The evaporator operates at 140 kPa, the condenser at 1600 kPa, and the flash chamber 600 kPa. The refrigerant leaves the evaporator as a super-heated vapor at -15°C, and leaves the condenser as a sub-cooled liquid at 50°C. Both compressors used in the system have isentropic efficiencies of 85%. For a cooling load of 25 kW, (a) What is the mass flow rate of refrigerant...
System Model: Automotive Air Conditioning System Outside Air Temp: 45 oC Car Interior Air Temp: 22 oC Heat Load = 4.2 kJ/sec rate at which heat must go in to the air conditioner to be removed from the car’s interior Refrigerant: R134a HINT: Heat enters an air conditioning system where? Refrigerant 134a … - leaves the evaporator coil and enters the compressor as a saturated vapor at the evaporator pressure of 2.8 bars. - It leaves the compressor at...
A two-stage compression refrigeration system with an adiabatic liquid-vapor separation unit uses refrigerant-134a as working fluid. the system operates the evaporator at 0.4Mpa, the condenser at 1.6Mpa and the separator at 0.8 Mpa. The compressors use 25kW of power. Given that the refrigerant is saturated liquid at the inlet of each compressor, and the compressors are isentropic: i) show the process on a T-s diagram, ii) calculate the rate of cooling provided by the evaporator, the COP of the heat...
A 100-ton refrigeration system operates on the simple vapor compression refrigeration system with R-22 as the working fluid. The evaporator pressure is 2 bar and the condenser pressure is 30 bar. The refrigerant leaves the compressor at 160oC. 1 ton of refrigeration = 3.517 kW Determine the cooling load, in kW. Plot all five points (1, 2s, 2a, 3, 4) on the P-h diagram. Determine the power consumed by the refrigeration system, in kW. Determine the COP of the system. Isentropic efficiency...
b. the apparatus detw p cp Prob #7] An air conditioned auditorium with a capacity of 1 000 persons is to be maintained at 24 and 55% RH. The sensible heat gain is 115 kW and the latent heat gain is 42 kW. The co enters the auditorium at 17 C. For proper ventilation, 40% of the supply air is fresh air and the r star recirculated air. Outdoor air is at 34 C DB and 50 % RH. Determine:...
a) The coefficient of performance-of vapor-compression refrigeration cycles improves when the refrigerant is subcooled before it enters the throttling valve Can the refrigerant be subcooled indefinitely to maximize this effect, or is there a lower limit? Explain brieflyb) A two-stage compression refrigeration system with a flash chamber is used to produce chilled water for a commercial building The refrigeration system operates between a pressure limits of 1 2 MPa and 200 kPa with refrigerant-134a as the working fluid. The refrigerant leaves...
A summer air conditioning system with recirculating air stream and BPF = 0 has a room sensible heat load of 20 kW and a room latent heat load of 2.22 kW. The required inside conditions are 22°C and 50% RH, and the outdoor design conditions are 36°C and 60% RH. The mass flow rate of the outside air is 15% of the mass flow rate of the supply air. Find a) RSHF b) the point s on the chart, mass...