Question

Figure 1 of 2 VO) L1 L2Consider the two loads in the circuit in (Figure 1). Load #1 (L1) absorbs S = 56 VA at a lagging power factor of pf = 0.61. Load #2 (L2) absorbs P2 = 56 W and Q2 = 1 VAR of power. If these loads are powered by a V = 425 V−rms , 60-Hz source, what impedance needs to be added to the circuit in order to raise the source's power factor to unity? Express your answer in rectangular complex form to three significant figures.

0 0
Add a comment Improve this question Transcribed image text
Answer #1

load-1 5, = 56 VA, COSø, = 0.61 lag 4,- 52.4105° S, = 56252.4105° Š = (34.16 + j 44, 3744) VA Si Pt;Q, = 44.3744 load-2 PL =

If you have any doubt please make a comment. Thank you

Add a comment
Know the answer?
Add Answer to:
Consider the two loads in the circuit in (Figure 1). Load #1 (L1) absorbs S =...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • VO) L1 L2 Line VO LI Power Calculations Learning Goal: In this tutorial, you will practice...

    VO) L1 L2 Line VO LI Power Calculations Learning Goal: In this tutorial, you will practice the calculation of power in circuits containing loads, including the effects of non-ideal transmission lines, and practice how to improve the power factor for an entire system. Many appliances (eg., hair dryers, coffee makers, and refrigerators) and industrial loads are powered by AC sources. The ability to be able to calculate their power needs is important in a number of situations. Before completing this...

  • Power Calculations 4 of 4 Review Learning Goal In this trial, you will practice the callation...

    Power Calculations 4 of 4 Review Learning Goal In this trial, you will practice the callation of power in circuts cortaring loads, including the effects of non-ideal transmission Ines, and practice how to improve the power factor for an entire system. Many appliancese.. hair dryers, coffee makers, and refrigerators) and indoads are powered by AC sources The folly to be able to calculate the power needs is important ma number of towns. Before completing the Moral make sure you are...

  • OLoad #1 : absorbs-7.5kW,2500TAR load # 3," 12.5a resistor in arallel with an induc tor that...

    OLoad #1 : absorbs-7.5kW,2500TAR load # 3," 12.5a resistor in arallel with an induc tor that has a reactance of So2. Calculate the averg e and 3 reactive power delvered bY L2 Source 2 rMS 2 Loadabsorbs lGkw and 8k VAR Load#2 : alosorbS lOkVA at o.cpf lead Load 3 absorks gKw at unity a) Cal culate ejui valeut impedance of the ircut 2 What is the pf, of the enuivalent load se the Lne's ut Jerminal s

  • Please show all work and concepts 5.2 (15 pts) In the following circuit, voltage source V...

    Please show all work and concepts 5.2 (15 pts) In the following circuit, voltage source V 10020° V, 60 Hz supplies power to three load circuits with impedances Z1, Z2, and Z3. The following information was deduced from measurements performed on the three load circuits Load Z1: 45 W at pf 0.95 lagging Load Z2: 70 VA at pf 0.75 leading Load Z3: 100 VA at pf = 0.6 lagging (a) Are Z1, Z2, and Z3 inductive or capacitive? (b)...

  • Problem 1 A single-phase source is supplying passive loads through two wires. The impedance of each...

    Problem 1 A single-phase source is supplying passive loads through two wires. The impedance of each wire is (0.05 + 30.05) 2. The load is connected between the two wires at the far end. The load current is 75 A (rms). a. What is the source voltage that you need in order to have 120 V (rms) across the load when the power factor of the load is unity? b. Repeat for the case where the load power factor is...

  • Q5: The circuit show below has two loads connected to 120 V (rms), 60Hz, house-hold supply....

    Q5: The circuit show below has two loads connected to 120 V (rms), 60Hz, house-hold supply. The load-1 is a resistive load (lamp) with a total power of 5 kW. The load-2 is a motor drawing 10 kVA at 0.6 power factor, lagging. The capacitor is initially not connected a) Calculate the load currents (phasor) I and 12 14] b) Calculate the supply current I c) What is the power factor of the source when it supplies to both loads?...

  • 1002 Figure 2: For Questions 8, 9, 10 For the circuit shown in Figure 2, Pi...

    1002 Figure 2: For Questions 8, 9, 10 For the circuit shown in Figure 2, Pi = 80 W with pf = 0.8 lagging, |S2| = 60 VA with pf = 0.7 leading, S3 = 40 VA with pf = 0.6 leading, I = 0.4237ºArms). Note that subscripts specify the load, so P1 is the real power for Load 1, which has impedance 21. 8. Determine P. (a) 57 W (b) 42 W (c) 36.63 W (d) 84.14 W (e)...

  • (15 pts.) A voltage source with 115 V rms value, is feeding three loads, which are...

    (15 pts.) A voltage source with 115 V rms value, is feeding three loads, which are in parallel to one another. The information about the loads is as follows L1: 200 W, at pf .92 lagging L2: 250 VA, at pf= .81 leading L3: 200 VARs at pf .85 lagging a. (1 point) Show the diagram depicting the given system 5 ะ Jr 2 + b. (6 points) Calculate S, P, Q, and 6 for each of the loads c....

  • Problem 3: (20 points) ase serves two balanced parallel loads. The line- A three-phase transmission line...

    Problem 3: (20 points) ase serves two balanced parallel loads. The line- A three-phase transmission line with an impedance (0.2 +j1.0) 12/phase serves two balan to-line voltage at the load end of the line is 480 V (rms). Load 1: Wye-connected and absorbs a total of 200 kW with a lagging p.f. of 0.87. Load 2: Delta-connected with an impedance of (20+30) 2/phase. a. Draw the single phase representation of the circuit b. How much current flows through phase A...

  • A generator is supplying two loads at 2800V and 60 Hz. The loads are: Load 1:...

    A generator is supplying two loads at 2800V and 60 Hz. The loads are: Load 1: 10 kVA, at 0.6 pf lagging. Load 2: 12 kW and 10 KVAR inductive a. Calculate the total active and reactive power, and the power factor of the load. S- S, - ST- Pr- PF-