An overhead lighting system is being assessed during the energy audit of a school. In a classroom with floor area = 85 m^2 , the overhead luminaires are all on a single electrical circuit (with no other loads on the circuit).
The room has 12 identical luminaires, each with three “F32T8” lamps and with electronic ballasts. The system-efficacy of the lamp-ballast combination is approximately 95 lm/W.
From the manufacturer’s specification sheet, the “luminaire efficiency” is estimated to be 78%. The lights are powered on for approximately 1,200 hours per year.
With the lights turned on, an electrician obtains the following measurements for the single-phase lighting circuit: V(rms) = 220 volts, I(rms) = 5.17 amps, and power factor = 0.95.
a) Calculate the power demand [W] of the lighting circuit.
b) Calculate the lighting power density [W/m2 ] of the classroom.
c) Estimate the annual cost [$/year] of electricity used by the lights if electricity costs $0.13/kWh
An overhead lighting system is being assessed during the energy audit of a school. In a...
The "lumen method" is to be applied to design an overhead lighting system for a room, with basic illuminance equation: total = Ewp · Awp/(Cu · LLF) The room has floor area = 60 m². The target illuminance at the work-plane is 400 lux. It is intended the lighting power density for the room should be 7.5 W/m2 or less. The design will be fluorescent lamps with electronic ballasts that together achieve "system-efficacy" = 85 lm/W. A light-loss-factor Ly =...