Question

A 60 Hz 20kVA 8000/240 Vrms transformer has the equivalent circuit parameters given in the table below;

Primary resistance econdary resistance Primary leakage reactance Secondary leakage reactance Magnetizing reactance Ri R2 X1 =

a) Find the magnitude of the input voltage in (V):

0 0
Add a comment Improve this question Transcribed image text
Answer #1

Given data, in f = 60tyle S: 20 x103 VA M = 8000 V Vo240V K . . . . 0.03 - - 0.43 ) 2000 R = 152, R₂ = 0.022 x, awly = 120 1To get MA we need to find 0.02 10.03)? 0.02 0.0009 = 22.222 TERASE 22,2223 0.1 . : 0.15 0.0009 .. .... . ..166.66 6 exåz 16P1 = Da = stos 54 Pa = 20x103 -C04(0.8) n . 240. . Ig : 83. 3334-36.87? - ... Pog - K Da : 0.03. ® 83,333 (-36.87 Pa: 2.51VA. Talhere, - 5 P. Relixo)/e.+jxo) Po 8299.867 (2.02 20(200130)/(2001) 20) T. 0.2292 L_39. go!A7 9,68 +P to Subesti turtingvp = [68299.867 (2009)+ (2.7127-40-86). (15+; 120) Vp : 8553. 769 ( 3.48v

Add a comment
Know the answer?
Add Answer to:
a) Find the magnitude of the input voltage in (V): A 60 Hz 20kVA 8000/240 Vrms...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • A 60 Hz 20KVA 8000/240 Vrms transformer has the equivalent circuit parameters given in the table...

    A 60 Hz 20KVA 8000/240 Vrms transformer has the equivalent circuit parameters given in the table below, a) For the rated load having a lagging power factor of 0.8, find the magnitude of the load current in Amperes. 15 Primary resistance 0.02 econdary resistance 120 Primary leakage reactance X2wL2 0.15 Secondary leakage reactance Xm=wLm Magnetizing reactance 30 k Re 200 k Core-loss resistance Answer: Check b) Find the phase of he load current in degrees (note: sign is important). Answer:...

  • Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Prima...

    Please show full working Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Primary resistance-1562, secondary resistance-0.02 Ω Primary leakage reactance-140Q, Secondary leakage reactance-0.15Q, Magnetising reactance 30 k2, Core loss resistance 200 k2 (a) The transformer is connected to two loads in parallel. The first load is 10 kW at 0.866 power factor lagging and the second load is 15kVA with a power factor of 0.8 lagging. Find the percentage regulation and power efficiency...

  • Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Prima...

    Help me answer c and d Q6. A 50 Hz, 25 kVA 7200/240 V transformer has the following equivalent circuit parameters: Primary resistance-1562, secondary resistance-0.02 Ω Primary leakage reactance-140Q, Secondary leakage reactance-0.15Q, Magnetising reactance 30 k2, Core loss resistance 200 k2 (a) The transformer is connected to two loads in parallel. The first load is 10 kW at 0.866 power factor lagging and the second load is 15kVA with a power factor of 0.8 lagging. Find the percentage regulation and...

  • A single-phase 50-kVA, 2400/240-volt, 60-Hz distribution transformer has a 1-ohm equivalent leakage reactance and a 5000-ohm...

    A single-phase 50-kVA, 2400/240-volt, 60-Hz distribution transformer has a 1-ohm equivalent leakage reactance and a 5000-ohm magnetizing reactance referred to the high-voltage side. If rated voltage is applied to the high-voltage winding, calculate the open-circuit secondary voltage. Neglect 'R and G^V losses. Assume equal series leakage reactances for the primary and the referred secondary

  • three-phase transformer is rated at 12 kV/135 kV, 100 MVA. It has the following equivalent circuit...

    three-phase transformer is rated at 12 kV/135 kV, 100 MVA. It has the following equivalent circuit parameters (referred to the primary winding where appropriate) : • primary resistance R1 = 0.03 ohms, secondary resistance R2’ = 0.04 ohms • primary leakage reactance X1 = 0.1 ohms, secondary leakage reactance X2’ = 0.1 ohms • magnetising reactance XM = 16 ohms, core-loss resistance RC = 200 ohms. In your calculations, you should use the simplified equivalent circuit. i) The transformer is...

  • 4. The figure below shows the equivalent circuit of a 2400/240-V, 60-Hz transformer. The high-side leakage...

    4. The figure below shows the equivalent circuit of a 2400/240-V, 60-Hz transformer. The high-side leakage impedance is (1.2+j 2.0) 2. the low-side leakage impedance is (0.012 ti 0.02) S2, and Xm at the high-side is 1800 2. Neglect the Hysteresis and Eddy current loss resistance Rhe Calculate the input voltage if the output voltage is 240 V (rms). Given the load resistance is 1.5 12 and the power factor is 0.8 (lagging). ཉིས་པ་དེ། དེ་ | ༼ ། ༼། །

  • Al. A 1 kVA single-phase step-down transformer is connected to a 220 V, 50 Hz A.C....

    Al. A 1 kVA single-phase step-down transformer is connected to a 220 V, 50 Hz A.C. source and delivers power to a load. The winding resistance and reactance at secondary side are 0.02 2 and 0.1 12 respectively. The maximum value of core flux is 0.248 mWb and the secondary winding contains 1000 turns. Evaluate a. b. the voltage induced on the secondary side; the turn ratio of primary side to secondary side; the rated current on both sides; and...

  • 3c) Induction Machine Analysis [ 8 marks ] A 415 V, 50 Hz, 1450 rpm, three-phase,...

    3c) Induction Machine Analysis [ 8 marks ] A 415 V, 50 Hz, 1450 rpm, three-phase, star-connected induction machine has the following equivalent circuit parameters (referred to the stator winding where appropriate) stator resistance R 0.3 ohms, rotor resistance R2 0.2 ohms stator leakage reactance X 2 ohms, rotor leakage reactance X2' 2 ohms magnetising reactance XM 50 ohms, core loss resistance Rc 200 ohms In your calculations, you should use = the simplified equivalent circuit i) Find the number...

  • Problem (1): A 15-KVA, 2400:240-V, 60 Hz transformer has the following equivalent circuit parameters: R =...

    Problem (1): A 15-KVA, 2400:240-V, 60 Hz transformer has the following equivalent circuit parameters: R = 2.522 R2 = 0.02522 Xi = 722 X = 0.0712 Re = 32 kl Xm = 11.5 k12 If the transformer is supplying a 10-kW, 0.8 PF lagging load at rated voltage, assuming the output voltage is the reference, draw the transformer's exact equivalent circuit referred to the primary (H.V) side and use it to calculate: 1. The input current 2. The input voltage...

  • 6.12 A three-phase, Y-connected, 460-V (line-line), 37-kW, 60-Hz, four-pole induction motor has the following equivalent-circuit parameters...

    6.12 A three-phase, Y-connected, 460-V (line-line), 37-kW, 60-Hz, four-pole induction motor has the following equivalent-circuit parameters in ohms-per-phase referred to the statr: R10.070 R2 0.152 X 0.743 X2 0.764 Xm 40.1 The total friction and windage losses may be assumed constant at 390 W, and the core loss may be assumed to be equal to 325 W. With the motor connected directly to a 460-V source, compute the speed, output shaft torque and power, input power, and power factor and...