Question

Question 2 [20 marks] Sketch a complete (labelled) phasor diagram for an ideal single phase transformer with the following: i

0 0
Add a comment Improve this question Transcribed image text
Answer #1

galvenat Iі I YHI Nine + IO + t ta + La Telwerwe eltellrece Ve LOAD 4 - given that take flux as reference prasor. Ni > 1 Nelages flux. by secondary rostige 90° and seconday voltage by shown in phasor. secondary curent Leads angle & as

Add a comment
Know the answer?
Add Answer to:
Question 2 [20 marks] Sketch a complete (labelled) phasor diagram for an ideal single phase transformer...
Your Answer:

Post as a guest

Your Name:

What's your source?

Earn Coins

Coins can be redeemed for fabulous gifts.

Not the answer you're looking for? Ask your own homework help question. Our experts will answer your question WITHIN MINUTES for Free.
Similar Homework Help Questions
  • 1kVA ideal single phase step-up transformer

    Q1 A 1kVA ideal single phase step-up transformer is supplied by a 24 V ac power source and is delivering power to a 10 Ω resistive load connected to the secondary side. If the transformer is operated at full load (1kVA), determine, a) the secondary current IS; (3 marks) b) the secondary voltage VS; (2 marks) c) the primary current IP; (2 marks) d) the turn ratio of primary winding to secondary winding; and (2 marks) e) the number of...

  • A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting thre...

    A three phase 250 kVA 2400:415 V 50 Hz distribution transformer is constructed by connecting three single phase transformers in the Dynll vector group as shown in Fig.P1. The per phase equivalent circuit parameters on the high voltage side are: R1-0.72 Ω, Xi,-0.92 Ω, R2-0.70 Ω, Xp-0.90 Ω, R.-308.49 Ω, and X,,-44.61 Ω (a) Sketch the corresponding phasor diagram of the primary and secondary voltages for the Dynll vector group; lagging; terminal voltage is 415 V line to line, and...

  • Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60...

    Question 2 A single-phase transformer has the following nameplate ratings: 100 kVA, 7200/240 V and 60 Hz. The following results are obtained from open-circuit and short-circuit tests: Test Open-circuit Short-circuit Voltage 7200 V 250 V Current 0.65 A 13.89 A Real Power Input 425 W 1420 W a) Determine the parameters of this transformer, all referred to the primary side. b) The secondary of this transformer is connected to a load that draws 100% of the rated power at rated...

  • - The Student Name Surname Student Academic Number Exercici A single-phase transformer with a TRVA rating...

    - The Student Name Surname Student Academic Number Exercici A single-phase transformer with a TRVA rating has a 380 primary and a 220V secondary. The load scross the secondary draws acusent at a power factor of 61% leading The frequency of the power supply is son: Determine the primary and secondary full-load currents of the transformer 21 Deduce the value of turn ratio 3) Calculate the active and reactive power of the transformer Explain the result 4) Calculate the peak...

  • Question 4 (10 marks) A) A 10-kVA, 415-V, three phase, Y -connected synchronous generator has a...

    Question 4 (10 marks) A) A 10-kVA, 415-V, three phase, Y -connected synchronous generator has a winding resistance of 0.3 Q and a synchronous reactance of 0.6 on a per phase basis. Determine its voltage regulation at full load when the power factor is (a) 75% lagging and (b) 75% leading. B) (10 marks) A 220-V, Y-connected, three-phase, synchronous motor has a synchronous reactance of 4 O/phase and negligible armature winding resistance. At a certain load the motor takes 7.5...

  • QUESTION 3 A 200 - MVA, 15/200 kV single-phase power transformer has a per – unit...

    QUESTION 3 A 200 - MVA, 15/200 kV single-phase power transformer has a per – unit resistance of 1.2 percent and a per-unit reactance of 5 percent (data taken from the transformer's nameplate). The magnetizing impedance is impedance is j80 per unit. a. Find the equivalent circuit referred to the low-voltage side of this transformer. b. Calculate the voltage regulation of this transformer for a full-load current at power factor of 0.8 lagging. c. Assume that the primary voltage of...

  • Problem 4 Three ideal single-phase transformers are connected in a delta/wye configuration with the primary side of the...

    Problem 4 Three ideal single-phase transformers are connected in a delta/wye configuration with the primary side of the three-phase transformer rated at 120 kV and the secondary side rated at 13.8 kV. The rated power of the transformer bank is 20 MVA. One side of the transformer bank is connected to a 120 kV transmission line, and the other side is connected to a three-phase load of 15 MVA at 0.85 lagging power factor. Compute the following: a) The turns...

  • 4. Three ideal single-phase transformers are connected as shown below. The turns ratio of each single-phase...

    4. Three ideal single-phase transformers are connected as shown below. The turns ratio of each single-phase transformer is 2400/480. Assume a perfectly balanced three- phase system (with ABC sequence) and that the delta side is the high-voltage side. (a) If IA is 8 amperes at 20 degrees, determine the phasor current Ix. (b) If the three-phase load is 100 kW at 0.87 lagging power factor and 465 V, determine how much current is flowing in the primary winding of T3....

  • For a single-phase ac supply, and using a series RL circuit diagram, draw the phasor diagram...

    For a single-phase ac supply, and using a series RL circuit diagram, draw the phasor diagram for the RL circuit using the voltage as the reference and show the power factor angle.Also show with a phasor diagram how a capacitor connected across the series RL circuit will reduce the power factor angle and total current.

  • The S.C. test on a 1-phase transformer, with the primary winding short-circuited and 30 V applied...

    The S.C. test on a 1-phase transformer, with the primary winding short-circuited and 30 V applied to the secondary gave a wattmeter reading of 60 W and secondary current of 10 A. II the normal applied primary voltage is 200 V, the transformation ratio 1:2 and the full-load secondary current 10 A, calculate the secondary p.d. at full-load current for (a) unity power factor (b) power factor 0.8 lagging. these are the answers [ 394 V; 377.6 V ]